Hi i had a log burner and wood mantel installed and the beam seems to be getting quite hot, is there a deflector or something i can get to stop this ? my measurements are
beam - just under 32” from hearth
beam - 12” above burner
beam - 4.5” from pipe

[Hearth.com] Mantel Beam hot [Hearth.com] Mantel Beam hot [Hearth.com] Mantel Beam hot
 
That does look quite close to the stove. What does the stove's manual say for clearances above it? What stove make and model is this?

A shield can be fabricated and will help, but only within reason. It would help if the mantel was mounted higher.
 
the make is newman fireplaces ltd and is a easedale 5 Se , i can’t see in the manual where it’s says about distance, it was fitted by a hetas engineer a few months ago
 
Unfortunately, I am unable to locate the manual to help. Newman's website offers little and does not appear to be up to date. The Easedale is not listed.

Was the beam in place when the stove was installed or did it come afterward? It is closer than would be permitted for any stove that I know of here in the states.

This is what a mantel shield looks like. It should extend for the full width of the fireplace opening, it should be on 1" spacers to create an air gap and can be painted.

[Hearth.com] Mantel Beam hot [Hearth.com] Mantel Beam hot
 
i’ve attached some images of manual below, thanks for the photos maybe i’ll be able to get something like that. It was all installed on one day as before was a coal fireplace which was removed

[Hearth.com] Mantel Beam hot [Hearth.com] Mantel Beam hot [Hearth.com] Mantel Beam hot [Hearth.com] Mantel Beam hot
 
I can’t recall a stove that allowed the mantle to be closer than a combustible wall. I could be wrong.

Evan
 
I see your dilemma. The manual is completely lacking in providing a meaningful specification for mantel or even ceiling clearance. Instead it vaguely refers to the huge and paywall protected British Construction Standards manual.