Rather than waiting for our 20 yr. old heat pump to give out the ghost, I gave our old system to a friend in need and put in a modern, commercial, Mitsubishi hyperheat system. This is for a ducted system. It's a nice improvement. Most of the time it's so quiet that you don't know it's running. I added a whole house surge protector while at it. Currently the system is loafing with mild temperatures. I am curious how it does when old man winter blows in. We'll still keep burning, but it will have to get colder before we do.

[Hearth.com] New heat pump for the season
 
Theoretically, the 3 ton system is rated to put out 40k BTUs at 17º. I will put it to the test when/if we drop into the low 20s to see how well it carries the load. The old 3T system was good down to about 30ºF.
 
  • Like
Reactions: EbS-P
I put in 3t Madia G3Evox (16k with Install) in April. So far this fall with Temps as low as 24f we are using about 9kw daily on heating. Four 5k Shop Heaters are using 40-50k daily. How it will do at -10f is to be seen. Very quiet outside and inside. Old unit dated from 2002 (Trane XP13i). Noisy to say the least. Could hear it with bathroom right behind the unit. New one have to open the Window and Strain my hearing.


What I dislike is you can't set the Furnace Fan to run 100% of the time in Winter. Designed not to blow cold air. Madia makes Carrier and others (Same exact Unit). We get some snow, up to 4ft at most on the ground. Old unit I had to keep clear of snow.

Thermostat has setting to run the fan 100%, but it does not take effect in heating mode. Carrier unit will override it I was told. Had them out for service call.

I put in Humidifier and Remy Halo LED. Dust is non existent. Also got 4 washable 4" Filters. About $300 but those throw away ones are 40 bucks each.

Also put in Surge Protector.

Not White Nasty Stuff is from years earlier. This fall zero snow. All Rain.

We have Harmon XXV and would typically use about 1-2 bags of pellets. This warm (50's high soon) about half a bag to 1 bag. 9kw is about $.54 cents. Pellets closer to $6 bucks with delivery (Newport WA)
 

Attachments

  • [Hearth.com] New heat pump for the season
    IMG_20220108_093117169.webp
    202.3 KB · Views: 121
  • [Hearth.com] New heat pump for the season
    20250503_145042.webp
    86.5 KB · Views: 104
  • [Hearth.com] New heat pump for the season
    20250503_143553.webp
    308.7 KB · Views: 109
  • [Hearth.com] New heat pump for the season
    20250421_165239.webp
    164.2 KB · Views: 109
  • [Hearth.com] New heat pump for the season
    20250421_094325.webp
    334.1 KB · Views: 114
Last edited:
Theoretically, the 3 ton system is rated to put out 40k BTUs at 17º. I will put it to the test when/if we drop into the low 20s to see how well it carries the load. The old 3T system was good down to about 30ºF.
Our family owns a summer home, one story ranch on Cape Cod, Massachusetts. We installed Mitsubishi splits for three bedrooms, the living room and three season porch which is now a 3.75 season porch as it's not insulated. They have been flawless for the last 6 years, other than routine cleaning etc. Good Choice!
 
  • Like
Reactions: Whitenuckler
Rather than waiting for our 20 yr. old heat pump to give out the ghost, I gave our old system to a friend and put in a modern, commercial, Mitsubishi hyperheat system. This is for a ducted system. It's a nice improvement. Most of the time it's so quiet that you don't know it's running. I added a whole house surge protector while at it. Currently the system is loafing with mild temperatures. I am curious how it does when old man winter blows in. We'll still keep burning, but it will have to get colder before we do.

View attachment 341566
That’s a nice system. I’m going to keep my Trane 3T 16 seer system as long as I can. It’s 16 years old. Blower was replaced 5 years ago. It will probably be rep with a 4T unit. It would be really nice to get rated capacity at 17F. I just looked I get rated capacity at 50F and 55% at 17 F. Gotta have those heat strips.
 
  • Like
Reactions: Whitenuckler
I was considering the 4 ton version. This Mitsy is a 3 ton system, but combined with this particular air handler the capacity is raised a bit to 40K BTUS. The combo provides a better COP for heating which is the goal. There is a notable improvement in heat output at the registers already over our Am Std/Trane Heritage 16, 2-stage system.
 
  • Like
Reactions: EbS-P
Nice. My 4 ton system is 17 years old (the compressor was replaced 11 years ago)... so I am watching things closely.

I was really hoping that the variable speed Infinity systems would come down in price... hasn't happened.

There is a refrigerant switchover in process, giving me another reason to wait. What refrigerant does your new system use?
 
The new system is using R454B refrigerant. Looking at the AHRI certificate, it's rated at SEER2: 21.20, EER2: 12.10, HSPF2 (zone IV) 9.20.
 
I read about R454B. It sounds like a pretty functional replacement.
 
Theoretically, the 3 ton system is rated to put out 40k BTUs at 17º. I will put it to the test when/if we drop into the low 20s to see how well it carries the load. The old 3T system was good down to about 30ºF.
I have the same system, but ductless,on R410A
 
That sounds like it mght be an older version?
 
Yes, I think the changeover happened this year.
 
Rather than waiting for our 20 yr. old heat pump to give out the ghost, I gave our old system to a friend in need and put in a modern, commercial, Mitsubishi hyperheat system. This is for a ducted system. It's a nice improvement. Most of the time it's so quiet that you don't know it's running. I added a whole house surge protector while at it. Currently the system is loafing with mild temperatures. I am curious how it does when old man winter blows in. We'll still keep burning, but it will have to get colder before we do.

View attachment 341566
What size of breakers are required ?
 
What size of breakers are required ?
That depends on the system requirements based on its size and technology. Our system is essentially a 3.5ton system on a 30amp/240v breaker. If heat strips are added, they will require a separate breaker sized to their requirement. This could be 40-60amps/240v.
 
I have a Mitsibushi too - not hyper heat though. (22k BTU at 17 F - but that's enough for my place unless it's also very windy).
I do get antsy when I hear defrost cycles going on (I can hear some turbulence (?) in coolant flow in the units inside the home when the flow direction changes for this). So below 35 I burn wood.

I remember when they installed, and said "it's working (cooling)", I opened a window right next to the outside unit and I told them "nope, you're wrong". I could not hear it.
The inside unit I do hear a whisper from the air flow, but that's it.
 
My panel has 30a and 50a and 60a for 3Ton Heat Pump with 15kw ER heat. Replacement of xr13i Trane (13.8 Sere) this Spring with Midea EvoxG3 (19 Sere). (Midea makes other Brands like Carrier). Unit has 3-stage auxiliary heat kit. I am guessing 15kw or such. Manual says 10kw - 25kw can be installed. Old unit had 15kw.

So far it slow like all Heat Pumps if you drop the temps at night to pick back up to 72f. I have seen Aux Heat symbol on couple of times on Thermostat. We are having 20f nights here. Last night 101kw used for Whole House. Four 5k Garage/Shop Heaters, 2 Refrigerators, Two 20qf Upright Freezers. Plus we have Deep Well for Water (Pump is 30ah, 240v).

Last Month was $284 or about 461kw more than last year at this time. Some cold days (9f nighttime's), but most of the month as been warmer than normal. Last year it was $244 for this Bill.

Going to try running Pellet Stove for 9f Mornings. Have done that few times. Pellet with Delivery is $6.00 vs .006kw for Electric. So math says Electric can be cheaper than burning pellets. When it will break even burning pellets Jury still out. (Elec is .006kw)

So far burned less than 1/3 of bag of pellets. Old Heat Pump was from 2002. Worked, but we only used it above 30f. Included pics of Old and New. Took 2 days to swap out. Learning Curve on Thermostat. Had it figured out and they updated it. Gives Weather Forecast on it now. Outside Temp and Indicator of Aux Heat. Downside you cannot tell the fan to run 100% on Heat. Just AC Mode.
 

Attachments

  • [Hearth.com] New heat pump for the season
    20250421_094325.webp
    334.1 KB · Views: 68
  • [Hearth.com] New heat pump for the season
    20250421_113138.webp
    529 KB · Views: 68
  • [Hearth.com] New heat pump for the season
    20250421_165239.webp
    164.2 KB · Views: 65
  • [Hearth.com] New heat pump for the season
    20250503_143553.webp
    308.7 KB · Views: 74
  • [Hearth.com] New heat pump for the season
    20250503_145042.webp
    86.5 KB · Views: 56
  • Like
Reactions: stoveliker
I wish my electric was that cheap. I pay $0.30/kwh. I’d use the hyper heat more often if that were the case
 
We have ours set to 68º at night, 72º during the day. It heats up the house quickly at 34º outside. It takes about 30 minutes to start cycling. It hasn't any colder outdoors so far. This may be the warmest December on record here.

Dataman, who is your elect co? PSE raised the rates almost 40% this year for our area. Haven't seen $.06/kW since we lived in Seattle years ago.
 
  • Like
Reactions: Burnin Since 1991
I wish my electric was that cheap. I pay $0.30/kwh. I’d use the hyper heat more often if that were the case
You must be subsidizing the data centers. Mine was something like $CAD 0.18/kwh. I set the heat pumps at 16C below about -2C.
 
  • Like
Reactions: Burnin Since 1991
We have ours set to 68º at night, 72º during the day. It heats up the house quickly at 34º outside. It takes about 30 minutes to start cycling. It hasn't any colder outdoors so far. This may be the warmest December on record here.

Dataman, who is your elect co? PSE raised the rates almost 40% this year for our area. Haven't seen $.06/kW since we lived in Seattle years ago.
"$6.00 vs .006kw for Electric." This does not make sense. Energy is charged per kwh used. $0.006 would be 0.6 Cents . Dataman must have another math he is using
 
  • Like
Reactions: Burnin Since 1991
We have ours set to 68º at night, 72º during the day. It heats up the house quickly at 34º outside. It takes about 30 minutes to start cycling. It hasn't any colder outdoors so far. This may be the warmest December on record here.

Dataman, who is your elect co? PSE raised the rates almost 40% this year for our area. Haven't seen $.06/kW since we lived in Seattle years ago.
PUD. https://popud.org/ They are great. Put in Fiber Optics about 2013. Well the South Part of County where most live.
We get power from Boundry Dam (The Postman Dam)
and Box Canyon Dam
 
  • Like
Reactions: Burnin Since 1991
PUD. https://popud.org/ They are great. Put in Fiber Optics about 2013. Well the South Part of County where most live.
We get power from Boundry Dam (The Postman Dam)
and Box Canyon Dam
Lucky you. Gotta love that $0.0660 per kilowatt-hour rate.