Over heating issues...

warno Posted By warno, Jun 5, 2018 at 6:59 PM

  1. warno

    warno
    Minister of Fire 2.
    NULL
    

    Jan 3, 2015
    1,122
    295
    Loc:
    illinois
    I had a thread during the winter on my issues with caviation and over heating.

    https://hearth.com/talk/threads/cavitation-issues.166597/

    I've finally started tearing into my system to see if I can find the flow issue on my boiler side. I was seeing huge delta Ts on the boiler side of the FPHX. First thought was my pump was damaged from cavitating. The impeller looks good. So next thought was my FPHX scaled up. I pulled it out of the plumbing today and from looking in the ports i couldn't see anything. Looks like the day I installed it. My only other restriction could possibly be the themomix valve being stuck semi closed and allowing bypass of boiler flow. I didn't get a chance to pull the valve ti look at it but other then that what could be my loss of flow?

    I went from delta Ts of 10-15°F at the beginning of the season to 40-45°F towards the end.
     
  2. maple1

    maple1
    Minister of Fire 2.
    NULL
    

    Sep 15, 2011
    8,724
    1,654
    Loc:
    Nova Scotia
    Ah yes, that was an epic thread.

    Are those dTs across the HX or across the boiler?

    Was there any change in dTs on the system side?

    I don't have experience from inspecting a cavitation damaged circ, but wonder if there could be an issue without it being obvious to the eye? I think I remember about there being a lot of noises then. Maybe something in the wear surfaces where the impeller shaft spins that would increase resistance to spinning?
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
  3. Chris Hoskin

    Chris Hoskin
    TarmSalesGuy 2.
    NULL
    

    Aug 29, 2008
    548
    68
    Loc:
    Lyme, NH
    higher delta T means you are moving MORE water, not less.
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
  4. brenndatomu

    brenndatomu
    Minister of Fire 2.
    NULL
    

    Aug 21, 2013
    3,323
    1,009
    Loc:
    NE Ohio
    Unless the cavitation was very mild and did not happen much, there would be very visible damage. Do a little reading up on cavitation, is is quite destructive to a pump.
    I was in a class a couple years back that had a pump with a clear case, you could see what was happening when they throttled various valve to make it cavitate...it can actually be quite violent
    pump-cavitation-10-638.jpg
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
  5. maple1

    maple1
    Minister of Fire 2.
    NULL
    

    Sep 15, 2011
    8,724
    1,654
    Loc:
    Nova Scotia
    If you move more water thru the boiler & that side of the HX, wouldn't that narrow the dT on that side?
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
    Chris Hoskin likes this.
  6. E Yoder

    E Yoder
    Member 2.
    NULL
    

    Jan 27, 2017
    191
    26
    Loc:
    Floyd, VA
    I think I would agree with maple1, but maybe we're not all talking about the same thing.
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
  7. Chris Hoskin

    Chris Hoskin
    TarmSalesGuy 2.
    NULL
    

    Aug 29, 2008
    548
    68
    Loc:
    Lyme, NH
    Correct! (sorry, brain fart) More flow means narrower delta T across the heat exchanger (transfering more energy).
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
  8. Chris Hoskin

    Chris Hoskin
    TarmSalesGuy 2.
    NULL
    

    Aug 29, 2008
    548
    68
    Loc:
    Lyme, NH
    yep, sorry, I got that backwards
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
  9. E Yoder

    E Yoder
    Member 2.
    NULL
    

    Jan 27, 2017
    191
    26
    Loc:
    Floyd, VA
    Lol, I have more of those the older I get..
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
    Chris Hoskin likes this.
  10. warno

    warno
    Minister of Fire 2.
    NULL
    

    Jan 3, 2015
    1,122
    295
    Loc:
    illinois
    @maple1 The delta Ts were higher on the boiler side of the HX vs the storage side. When they used to ride also identical.

    And the delta Ts didn't change any in the system.

    The circ I'm running has a plastic impeller. It's probably composite of some kind but either way it showed no signs of wear. And it had caviation going on for about 2 seasons on and off. When the boiler would reach anything mid 170s it would be very faint but closer to 180 and over it sounds like the circ was eating gravel.
     
  11. BoiledOver

    BoiledOver
    Minister of Fire 2.
    NULL
    

    Apr 14, 2013
    586
    210
    Loc:
    43°58'55 N - 85°20' W
    @warno Do you have good news to report concerning your system modifications?
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
    warno likes this.
  12. warno

    warno
    Minister of Fire 2.
    NULL
    

    Jan 3, 2015
    1,122
    295
    Loc:
    illinois
    I've completely changed things up. I'm going to start a thread here in the next few weeks about my changes. I've eliminated probably half or more of my head loss on both sides of the FPHX and I've also step up my FPHX size by more than 10 fold.
     
  13. BoiledOver

    BoiledOver
    Minister of Fire 2.
    NULL
    

    Apr 14, 2013
    586
    210
    Loc:
    43°58'55 N - 85°20' W
    Sure are hoping for dramatic improvements, seems like that beautiful boiler should easily handle your needs.
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
    warno likes this.