I recently discovered that our 2 yr old stove is too close to the wall according to the owners manual \ spec. We have double wall stove pipe (black) going up to ceiling with a 45 degree bend closer to the ceiling. Then it goes through ceiling to double wall stainless chimney pipe, which then is hidden in the second floor wall, then right through roof (no attic). The only bend is the 45 on the first floor where its exposed black double wall pipe.
Spec says (Regency F2400 with airmate) the stove itself, using the heat shield as a ref point to the wall, should be 5.5" using double wall pipe. Well its 4". It also says the center line of pipe coming off stove should be 12" to wall. Well its 10.5". So we are short 1.5" inches in both areas which makes sense.
I had the installers come back out to check it out and they agree that by the spec of stove its short by 1.5 and they agree they messed up, but say since the double wall pipe coming off the stove is at its 6" clearance to wall, I am fine and could leave it as is. They measure from the double wall pipe exterior (not the center line) to the wall and its 6", which they say is within spec for the pipe itself. They also said they will move it out if I want them to at no charge, including extending the floor tile out as well.
This investigation by myself with the clearances started because I have felt the wall when the stove is going good (475 - 500 deg) and the section of the wall on the low side where the stove is, is warm, however when I feel the section of the wall where the pipe is, its HOT. For about 3 secs or so, then it feels fine, meaning I don't feel like my hand is burning and I can leave it there indefinitely with no issue. Its only the initial feeling of the wall that gives me that HOT sensation and then it dies out until I move my hand to another section in that same area, then its HOT again. The wall is painted with semi gloss paint.
So my question is, should I have them move it out for the 1.5"? Although they say it will be more like a total of 5" since the 45 deg bend will be shorter in length when they bump the stove out, so it will kick the stove out more than 1.5", more like a total of 5".
Thanks in advance...
I recently discovered that our 2 yr old stove is too close to the wall according to the owners manual \ spec. We have double wall stove pipe (black) going up to ceiling with a 45 degree bend closer to the ceiling. Then it goes through ceiling to double wall stainless chimney pipe, which then is hidden in the second floor wall, then right through roof (no attic). The only bend is the 45 on the first floor where its exposed black double wall pipe.
Spec says (Regency F2400 with airmate) the stove itself, using the heat shield as a ref point to the wall, should be 5.5" using double wall pipe. Well its 4". It also says the center line of pipe coming off stove should be 12" to wall. Well its 10.5". So we are short 1.5" inches in both areas which makes sense.
I had the installers come back out to check it out and they agree that by the spec of stove its short by 1.5 and they agree they messed up, but say since the double wall pipe coming off the stove is at its 6" clearance to wall, I am fine and could leave it as is. They measure from the double wall pipe exterior (not the center line) to the wall and its 6", which they say is within spec for the pipe itself. They also said they will move it out if I want them to at no charge, including extending the floor tile out as well.
This investigation by myself with the clearances started because I have felt the wall when the stove is going good (475 - 500 deg) and the section of the wall on the low side where the stove is, is warm, however when I feel the section of the wall where the pipe is, its HOT. For about 3 secs or so, then it feels fine, meaning I don't feel like my hand is burning and I can leave it there indefinitely with no issue. Its only the initial feeling of the wall that gives me that HOT sensation and then it dies out until I move my hand to another section in that same area, then its HOT again. The wall is painted with semi gloss paint.
So my question is, should I have them move it out for the 1.5"? Although they say it will be more like a total of 5" since the 45 deg bend will be shorter in length when they bump the stove out, so it will kick the stove out more than 1.5", more like a total of 5".
Thanks in advance...