We bought this old farm house 2 years ago with a now 38 year old HS Tarm OT35 combination wood and oil boiler. Previous owners used mainly wood since boiler was new but we’ve using oil since we’re not home much. Average oil consumed past 2 years is 590 gallons. I know the old steel and cast iron fittings aren’t going to last forever so wanted input into what to replace with and how to find reputable dealers in our zip code area 12020.
Currently leaning towards a new oil or pellet system. I’m thinking with a storage tank the system won’t need to be as large as our current system.
Anyone using Evoworld, Froling P4, Effecta Komplete III, EcoBoiler, or WoodMaster on this site?
======================================================================================================
You not burning a lot of oil.
Before you spend any of your hard earned money I would like you to purchase two paperbacks "Pumping Away" and Classic Hydronics.
If you buy them from (broken link removed) you buy them directly from the author or you can order them from AMAZON or Barnes & Noble.
These 2 books were written by Dan Holohan. Mr. Holohan grew up in the plumbing business being a plumbers helper, technical sales rep for B+G and Taco and a plumbing and heating trouble shooter on Long Island.
Mr. Holohan makes his reading fun and informative for the experienced plumber and the lay person and he talks about the history of plumbing and heating and the Dead Men who were responsible for the plumbing and heating systems we use today as well as the physics involved in plumbing for heating and cooling and what is needed as well as great ways to avoid crawling around on you hands and knees to bleed radiators by power purging them when you fill them with cold water by placing boiler drains in each cool water return loop before the boiler sump.
Save your money, you do not need a new boiler.
Have the oil burner serviced and then clean the boiler tubes with the brushes that came with the boiler.
If I remember your Tarm correctly you need to remove the steam chest cover to remove the lid that seals the vertical boiler tubes to brush them out to clean them.
Cleaning the boiler flue pipe to the ash door in the chimney should also be done too.
NO, NO. NO, you do not have to worry about the boiler or the steel pipe fittings until they develop a leak so no worries there at all. I have steel pipe fittings and they are very old and do not leak so no worries there.
A few simple parts will make your boiler last much, much longer and prevent needless expense.
1. back flow preventer
2. Low Water Cut Off switch wired in series as the first boiler control before the triple aquastat.
3. Boiler Bypass valve. The boiler bypass valve saves fuel by using the water in the heating loop and recirculating it and mixing it with the hot water in the steam chest.
4.
The B+G RB122-E is what I would recommend for a low water cut off. Doing it in this manner shuts the power off to the boiler in the event of a low water condition and prevents the boiler from firing if there is no water in the steam chest and also preventing an explosion from water contacting the dry boiler walls.
5. Drain the boiler off completely and flush it out and then add a can of Fernox after the backflow preventor is installed to protect the boilers wet parts.
You may want to consider replacing the triple aquastat and L6006A with a new one.
I have the Honeywell L8124L1011 horizontal triple aquastat and the RB-122-E Low Water Cut Off and a Honeywell L6006A in my coal stoker boiler and they are excellent units.
These mechanical boiler controls that are not affected by high voltage spikes and low voltage conditions which will destroy digital boiler controls.
I had 2 Hydrolevel 3250 Plus triple aquastats and they were both faulty with bad computers and the low water cut off controls did not work on either unit and I replaced them with the Honeywell L8124L1011 Triple Aquastat and the Mcdonnel & Miller Bulldog RB-122-E Low Water Cut Off.
There is no need to spend a huge amount of money to replace your current boiler when all you need is new control parts and installing the circulator above the steam chest pulling water from the large steam chest tapping to pump away from the boiler.
All you need is a little work and a few new parts and you do not have to spend a huge amount of money to do this and you can leave your oil boiler to run on summer temperatures of 160 high 140 low with a 10 degree differential on the triple aquaststat and leave the L6006A at 190 with a 15 degree differential for the dump zone temperature.
Spoil yourself and your spouse with a vacation with the money you will save by doing simple repairs with new parts or hiring a plumber to do them and you will save many thousands of dollars you can spend on a hobby or a dream vacation.
Save Your Money and do the simple upgrades and repairs.that is all you need to do.