Smoke fills house
With the temperatures dropping, its time to start the stove again. Hearthstone Castleton (new March 2025) Pickens County, South Carolina. However, my partner could not get the fire going this morning (Nov 8 2026) without the stove door being wide open. This results in smoke in the house and a headache (literally) for my partner. If she closes the door the fire dies out.
Looking at Pickens, SC weather, it looks like the temperature is swinging 30º daily. Draft is created by the difference between the indoor and outdoor temperatures. If it's 55º when she starts the fire, draft may be weak, especially if the flue system is sub-optimal.
Other than a faulty stove- the two likely problems are 1) house is too air tight, or 2) stove pipe is too short (effective length).
Starting up the stove with the stove door open will eliminate a stove issue, provided you verified the flue out of the stove is open.
Starting up the stove with a window cracked will eliminate an air tight house.
I'm assuming you tried both of the above. Since you are at 10,00 ft, I'd bet on a stove pipe length issue.
ElevationAtmospheric pressureAvailable draft pressure, relative to sea level
Sea level101.3 kPa100%
5,000 ft84.3 kPaAbout 83%—17% less
10,000 ft69.7 kPaAbout 69%—31% less
In a simplified draft calculation, compensating for elevation alone requires about 20% more height at 5,000 feet and 45% more at 10,000 feet. For example, a 15-foot chimney at sea level would need roughly 22 feet at 10,000 feet to generate the same theoretical pressure at the same temperatures—not necessarily the same real-world performance.
You'll need to take the elbows into consideration too. That's going to add another 6-10 feet to the length, depending upon the horizontal run between the elbows. This will put you near or possibly over the max length recommended for the stove.
Measure your total current length and calculate where you're going to be. If you're going to be near the max, get someone in that can measure the draft with a manometer. That stove should have a 0.06-0.10 inches of water column operating draft.
Please verify my numbers with the owners manual and other references. I'm not a stove installer, just a firmware engineer with some mechanical engineering background.
I hope this helps.
Reactions: moresnow
OP says 1000 ft, not 10,000 ft.
The concepts you mention are solid though, including the elbows.
I'm not sure what the remark about max length is about.
That is to avoid over drafting, and is for straight up. Elbows and elevation similarly increase the max length because they decrease draft.
Oops, my astigmatism kicked in and I saw an extra zero in there. My bad. Thanks.
So given it's 1,000 ft, skip the additional length for elevation, but the additional 6-10 for the elbows still needs to be accounted for.
The max recommended length was from the stove manufacturer. It probably has to do with cooling of the smoke and overall resistance to the exhaust flow. The cooling would reduce lift and increase creosote build up.