TACO controller calling for heat, thermostat isn't

  • Active since 1995, Hearth.com is THE place on the internet for free information and advice about wood stoves, pellet stoves and other energy saving equipment.

    We strive to provide opinions, articles, discussions and history related to Hearth Products and in a more general sense, energy issues.

    We promote the EFFICIENT, RESPONSIBLE, CLEAN and SAFE use of all fuels, whether renewable or fossil.
Nov 28, 2023
3
nh
Hey all looking for some help with my boiler's TACO controller. I have an oil fired hot water baseboard system with 4 zones. Came home yesterday and the bedroom (zone 2) was HOT! Touch the baseboard and it's cranking hot, thermostat is turned off. Checked the controller and indeed zone 2 is calling for heat. This continues even with the thermostat pulled off of its mounting base. Is my controller failing in some way? What could cause this, any ideas?
I manually disconnected the red wire thermostat feed from the terminal inside the controller for now but would like to sort this out without having to call in a service. No work has been done to the house and this all worked perfectly during the winter.
Thanks in advance, been lurking on these forums for awhile and have learned much!
 
Hey all looking for some help with my boiler's TACO controller. I have an oil fired hot water baseboard system with 4 zones. Came home yesterday and the bedroom (zone 2) was HOT! Touch the baseboard and it's cranking hot, thermostat is turned off. Checked the controller and indeed zone 2 is calling for heat. This continues even with the thermostat pulled off of its mounting base. Is my controller failing in some way? What could cause this, any ideas?
I manually disconnected the red wire thermostat feed from the terminal inside the controller for now but would like to sort this out without having to call in a service. No work has been done to the house and this all worked perfectly during the winter.
Thanks in advance, been lurking on these forums for awhile and have learned much!
It is sounding like a problem with the thermostat if you can disconnect it and make the TACO happy.
Maybe bad wiring too. Check the wiring and swap thermostats with one that works.
 
Last edited:
Or wire going to the thermostat shorted. I had this happen last year. I swapped the thermostat with no fix. Called a company and explained the issue as I ran through everything I’d done to troubleshoot. He said, it’s the wire. I’m like really?

I snaked a new wire and he was right.
 
Hey all looking for some help with my boiler's TACO controller. I have an oil fired hot water baseboard system with 4 zones. Came home yesterday and the bedroom (zone 2) was HOT! Touch the baseboard and it's cranking hot, thermostat is turned off. Checked the controller and indeed zone 2 is calling for heat. This continues even with the thermostat pulled off of its mounting base. Is my controller failing in some way? What could cause this, any ideas?
I manually disconnected the red wire thermostat feed from the terminal inside the controller for now but would like to sort this out without having to call in a service. No work has been done to the house and this all worked perfectly during the winter.
Thanks in advance, been lurking on these forums for awhile and have learned much!
Grab a meter and check on ohms wire to wire and wire to ground if there is one. Then short the wires on one ends
and measure on the other end (assuming they are not already shorted together)
 
After following your recommendations I found this. How did this wire get between that beam and the outside foundation wall? Did dryer winter air create a gap? Humid air now swelled it shut? Bypassed that small section and all is good.
 

Attachments

  • [Hearth.com] TACO controller calling for heat, thermostat isn't
    thermostat_wire.webp
    268.2 KB · Views: 4
After following your recommendations I found this. How did this wire get between that beam and the outside foundation wall? Did dryer winter air create a gap? Humid air now swelled it shut? Bypassed that small section and all is good.
Sometimes the wires are placed after walls and ceiling are finished so they are "fished" in. This can be a blind process as as long as you can pull between point A and Point B you are done, however you can't see what you have done. That wire would normally be secured. Also the person could have gave it a tug to get some extra length. I guess if you could see it there is no excuse as it could have been secured somehow. Glad you found it and were able to get at it.