I've been running for years with the
Poor Man's Variable Speed Circulator and decided that it's time to bite the bullet and use a
real variable speed circulator, managed by my NFCS.
The control objective is to vary the boiler circulator speed to obtain the desired boiler outlet temp. Lower speed means more dwell time for the water in the boiler means higher outlet temperature - should work like a charm. With hotter fire or higher inlet temps, higher circ speeds would be possible while maintaining the desired outlet temp.
It works wonderfully, except.....
With slower flow through the boiler, you also have slower flow through the zones, which means colder inlet temps, which means you need slower flow through the boiler because you now need more rise.
Same thing happens the other way around when everything is cranking. High flow though the boiler leads to high flow through the zones and a smaller drop, meaning higher inlet temp at the boiler.
Bottom line - variable speed boiler circ doesn't solve all the world's problems.
I saw something similar on a different system, cooling towers and chillers. Within the operating conditions at that instant, the source capacity and the load are relatively constant, reducing flow around the loop increases the supply/return temp differential, delta T. Increasing loop flow reduces delta T between supply and return temps. Boiler heat production and the load may remain relatively constant as the loop flow varies and supply/return delta T varies inversely with loop flow.
Desired HW supply temp would depend on the load and the heat output firing rate, varying the load or the firing rate.
If the objective is an efficiency gain, I believe there's a big gain using "hot water reset" to vary the load supply temp. The load and the boiler have two different HW temp requirements. Boiler S/R temps have to be maintained above 140 F to avoid flue gas condensation with typically a 10 deg F S/R differential (delta T) for cast iron boilers to avoid thermal shock to the cast iron. Steel boilers generally do not have a thermal shock problem.
Varying supply temp to the load is the big ticket, even with HW baseboards and CI radiators. There's a big savings as the load is satisfied with a lower HW temp, allowing the boiler to achieve setpoint and go off earlier(for oil / gas typically). The load also runs a lot quieter as the flow is on longer at a lower temp instead of cycling on/off at 180 F. Reducing metal expansion/contraction significantly reduces the noise.
I am using outdoor reset variable speed injection pumping to set the load supply temps, independent of the boiler temps, as long as boiler water is available. It runs full speed as the boiler temp is coming up and drops down to almost nothing as the boiler temp goes up above setpoint and the load return temp goes up from a cool start. I put in a Weil Mclain Ultra gas boiler for my brother with outdoor reset built into the boiler, varying the supply temps to his baseboard convectors. It seems to me that with storage your capacity and the load are relatively independent, charge storage and take the load out slowly.
I'd like to second the comment about learning a lot from your posting. Thank You. It was reading the forums here that got me into the Froling.
One thing that is a revelation for me, I cannot understand how the human race has been burning wood for the previous 10,000+ years yet what the system should be, say a gasification boiler with HW distribution, is less than 1% of the market, with the customers completely clueless. Even clean burning stoves can be a tough sell. Keep up the good work.
I will easily be less than three cord this year (and every year after), burning sloppy, prepared wood. I am amazed the market is clueless about this. Zero oil.