Highbeam

Minister of Fire
Hearth Supporter
Dec 28, 2006
21,152
Mt. Rainier Foothills, WA
So the owner's manual for the NC30 repeatedly calls out 16" as the distance from the single wall pipe to the combustible wall. Isn't it supposed to be 18"? Does the manual trump the standard 18" requirement or is the requirement now 16"?

http://www.englanderstoves.com/manuals/30-NC.pdf

Double wall on this stove doesn't save you much. Such odd installation requirements.
 
18" from combustible ceiling (in the case of a horizontal run), 16" from wall/ with single wall pipe no shields
Double wall black pipe 12", unit comes with rear heat shield on stove.
 
So the owner's manual for the NC30 repeatedly calls out 16" as the distance from the single wall pipe to the combustible wall. Isn't it supposed to be 18"? Does the manual trump the standard 18" requirement or is the requirement now 16"?

http://www.englanderstoves.com/manuals/30-NC.pdf

Double wall on this stove doesn't save you much. Such odd installation requirements.
Yes, this would trump the standard 18" requirement. Since they tested it this way it's ok. I've ran into this a few times and still don't mind sticking with the 18"s.
We called Englander and asked about the strange clearance with the double wall. They said that double wall pipe allowed the stove to get hotter therefore it didn't allow much of a reduction by using double wall.
 
Thanks guys. I believe that I'll follow the advice and stick to 18" anyway which should give an extra margin of safety plus will allow a future stove to be installed. Looking at 10 feet of vertical single wall and then 8 feet of vertical class A duratech.
 
i always recommend DVL pipe if there is 8' or more of exposed pipe in the room
(some makers now require it)

The NC30 manual allows 10' max of single wall. This is a pole barn stove so it will be run hard and hot every so often and not simmered like a home stove. Hope to save some cash by sticking with single wall and also I just want to try it. I've only ever used double wall DVL.

Does the NC30 stove collar take single wall straight in without an adapter?
 