It is that is why it is rarley done right. But that is the only way you will get a fireplace that doesnt suck air you already paid to heat out of the houseThanks. That seems like a gob of passive air to be bringing directly in to the firebox? And then the issue of where to bring it in? Vents along the front edges?
So, 800 CFM up the chimney means we'll need 800 CFM of combustion/MUA. Right? You can do two 6" passive intakes directly in to the fire box (unheated). I believe a 6" passive is good for 75 CFM (@5pa differential to outside)? So two is 150 CFM leaving us needing at least 650 CFM MUA in to the house?
In MN make up air is nearly always brought in to the return air duct. Outside air could be as low as -30°f. HVAC installers here consistently say that the heat exchangers in residential gas furnaces should never have air below +40°f. Theoretically this is due to the potential for creating extreme condensation. I have never seen anything from a manufacturer saying anything similar though.
So, the air being brought in from outside is filtered, pre-heated to between 38-50°f before being introduced in to the return air duct from where it will enter the furnace, be heated to room temp and then distributed throughout the house.
I'm not an engineer of HVAC person so mostly just spitting out what I've read and been told by HVAC folks and builders.
I still can't get my head around this. If fresh make up air is getting fed right to a return duct, that would mean an equivalent volume of heated air is not getting into the return. So where is it going? Outdoors?
Up the chimney.
Right. Which again makes no sense to me. Make up air should be going right to the combustion source, then up the chimney. That seems like a lot of wasted heated interior air.
At least that's my take - and I have been off base before.
It is not impractical at all. In fact it is the most practical solution.Ideally, yes. But as the OP already noted, the CFM requirement makes meeting that need entirely at the source a little impractical.
Fuel economy is always a partial consideration, but not everyone’s end goal.
How best to accomplish this with the Isokern?It is not impractical at all. In fact it is the most practical solution.
If you want an open fireplace you will need lots of makeup air. So yes they are big holes to put in the house from an efficency syand point. But an open fireplace is horrible as far as efficiency .How best to accomplish this with the Isokern?
A 12" flue is 452 sq inches which would require 2 8-9" intakes to be equal in sq inches. A flue is effectively 'powered' though so will exhaust much more air than the equiv passive intakes so I'd estimate that you'd need at least 2 10" (314" ea) fresh air intakes to have equal air flow? That's a lot to try to integrate in to the firebox somehow (and I'm not sure that'd be enough) and these are some pretty big holes to put in the house envelope from an energy standpoint.
These also need to be done in a way that when not used that they do not introduce excessive energy loss and dew point problems?
How do u get your sq in? 12" round is 6*6*3.14= 113.04sqin. 12 square is 12*12=144sqin. I apologize if i missed somthin.How best to accomplish this with the Isokern?
Good catch i didnt notice thatHow do u get your sq in? 12" round is 6*6*3.14= 113.04sqin. 12 square is 12*12=144sqin. I apologize if i missed somthin.
Around here, pie are round.Yes, sir. pi r squared
I reminded her of that on Facebook recently. She said she failed it too but that we had fun.Interesting fact, the Pythagoreans never knew the Pythagorean theorem. It was named after them, because they were well-known to have enormous (and pretty accurate) tables of right triangle ratiometric dimensions. But their tables were developed by literally drawing accurate triangles on the ground, and measuring them, not by the theorem that was later given their name.And so, thirty years later, I was building a log cabin, needed to figure the length of the rafters, I used the Pythagorean theorem, a squared plus b squared equals c squared. The wisdom of brilliant Greek intellectuals from 2,500 years ago, and, thirty years after I studied it in high school I used it to figure rafter length.