Stainless Steel liner questions

Post in 'The Hearth Room - Wood Stoves and Fireplaces' started by Trickle, Mar 6, 2013.

  1. Trickle

    Trickle New Member

    Joined:
    Jan 20, 2013
    Messages:
    47
    Loc:
    East Central Missouri
    So it looks like I'll need to buy a stainless steel liner and "T" since my chimney is masonry with clay flues. I know there are a lot of kits out there, but anyone have a preference or know of a good one?

    I'm guessing I need the smooth line instead of grooved to keep creosote from building up on the grooves. Also need the insulation.

    Finally, if I install a T where the stove exhaust enters the masonry chimney, how do I clean out the bottom of the "T"? I'm picturing running the rods and brushes from the top of the chimney, and anything it knocks down would end up in the bottom of the "T". Do I then have to pull the stove exhaust and clean by hand through the thimble or is there an easier way?

    Thanks,
    Trickle

    Helpful Sponsor Ads!





  2. webby3650

    webby3650 Master of Fire

    Joined:
    Sep 2, 2008
    Messages:
    4,371
    Loc:
    southern Indiana
    Don't worry about getting a smooth wall liner, it's not necessary. Theres not wrong with them, you just don't need to spend the extra money. I've cleaned lots of liners, and I see no difference in the way creosote builds up, it's very minimal in either one as long as it's insulated. So, make sure you get the insulation.

    You will need to pull the stove pipe to get to the bottom of the Tee. It's no sweat, you need to pull the pipe off to clean it anyway.

    Is there something wrong with your masonry flue?
  3. Trickle

    Trickle New Member

    Joined:
    Jan 20, 2013
    Messages:
    47
    Loc:
    East Central Missouri
    Masonry is cracked in a few places, as is the clay flue. I'll post pictures in a few weeks as I can. The sweep that cleaned it out said he would do a SS liner if he was burning 24x7, and from what I've read the SS liner is preferred.
  4. WoodpileOCD

    WoodpileOCD Minister of Fire

    Joined:
    Jan 19, 2011
    Messages:
    659
    Loc:
    Central NC
    I bought mine from Rockford Chimney Supply and found them to be most helpful in the selection process and getting all the pieces I needed. Prices were competitive and outstanding customer service. They screwed up on the cap they sent. Called them and the told me to keep the one they sent and then sent me another one in 2 days.
  5. webby3650

    webby3650 Master of Fire

    Joined:
    Sep 2, 2008
    Messages:
    4,371
    Loc:
    southern Indiana
    Just don't be fooled by a super internet "deal", make sure that it comes with all the components that you will need.
  6. chimneylinerjames

    chimneylinerjames Feeling the Heat

    Joined:
    Nov 26, 2012
    Messages:
    381
    The smooth wall liner in my opinion is worth it for wood. It will clean easier and give you better draft. But if you are tight on money and deciding on insulation or the smooth wall liner, definitely go with the insulation. The insulation is a must for any liner. But if you want the best draft and best setup, get a smooth wall liner and the insulation.
  7. Nick Mystic

    Nick Mystic Minister of Fire

    Joined:
    Feb 12, 2013
    Messages:
    672
    Loc:
    Western North Carolina
    Regarding cleaning out the T - connector inside the fireplace behind your stove: The T - connectors come with a cap on the bottom of them a few inches below the horizontal pipe that connects to the flue collar on your stove. You attach the cap with a couple of sheet metal screws and then remove the cap when you clean your pipe. When I recently did my installation I positioned my end cap so that two of the three screw holes angled out at a 45 degree angle toward the front of my fireplace opening. I have about five inches on either side of my stove and my fireplace opening and I can reach the screws pretty easy by reaching in with a screw driver. I didn't put a screw in the hole in the back of the pipe since I wouldn't be able to reach it and two screws can hold the cap on securely. Some people remove the cap before they clean from above and attach a bag over the bottom of the T so all the creosote, ash, and soot go directly into the bag for easy cleanup. IMG_0179.JPG

    You can't see the cap in this photo, but it about three inches below the bottom of the picture.
  8. Trickle

    Trickle New Member

    Joined:
    Jan 20, 2013
    Messages:
    47
    Loc:
    East Central Missouri
    Gotcha Nick, but my T would be inside of a masonry and clay flue with no access from the sides or below. You converted a fireplace so you can get underneath, the only way to access mine would be from inside the house through the thimble or from the chimney top.

    Attached Files:

  9. Nick Mystic

    Nick Mystic Minister of Fire

    Joined:
    Feb 12, 2013
    Messages:
    672
    Loc:
    Western North Carolina
    I'm with you now. I have a similar set up with my Woodstock Classic stove in the lower level of my house. When I clean my chimney for that stove I have to pull the pipe off the back of the stove and pull the other end out of the thimble. I take that three foot long pipe assembly outside to clean with a brush. Inside I use a cup to scoop out any creosote that fell through to the bottom of my T, which is actually just a continuation of the clay flue liner. It continues down inside the brickwork of the chimney (a huge 8' x 4' brick chimney) as far as I can reach my arm! I just scoop out down about a foot or so. Until recently I did not have any sort of cap on the flue at the top of the chimney and there would be leaves mixed in with the creosote, cinders, etc.
  10. mellow

    mellow Resident Stove Connoisseur

    Joined:
    Jan 19, 2008
    Messages:
    3,142
    Loc:
    Salisbury, MD
    How tall is that chimney measuring from the bottom of the stove to the top cap?
  11. Joful

    Joful Minister of Fire

    Joined:
    Mar 7, 2012
    Messages:
    6,249
    Loc:
    Philadelphia
    Maybe I missed it, but what is your clay flue ID and height? Smooth wall flex with a blanket wrap will provide maximum draft, and better safety in an old and questionable flue, if that is what you're looking for. As others stated, not often necessary, but I like doing things the best way every time.
  12. Woody Stover

    Woody Stover Minister of Fire

    Joined:
    Dec 25, 2010
    Messages:
    5,505
    Loc:
    Southern IN
    I like my HomeSaver Heavy Duty Roundflex. When they say HD, they ain't kiddin'! MIL's sweep put it in her chimney a few years back, as well. There are cheaper liners out there, though...

  13. Jackfre

    Jackfre Member

    Joined:
    Oct 3, 2011
    Messages:
    79
    Loc:
    N CA
    I have a Dura-Vent Dura-liner system on my place and like it. Mine is the oval system and the flex piece at the bottom was simple to feed thru the smoke shelf...once I blasted enough of it out. Worth a look!
  14. Trickle

    Trickle New Member

    Joined:
    Jan 20, 2013
    Messages:
    47
    Loc:
    East Central Missouri
    Measured it today, just a few inches over 13 foot tall from floor to bottom of top cap.

    I'm not sure how to ID the flue, can you give me more info on what you are looking for? By height I hope you mean overall height as in the previous question?

    Affirmative, that is the objective.


    As do I, so when the sweep mentioned it was ok, but if burning 24/7 he'd do a liner I automatically go to I need a liner.
  15. chimneylinerjames

    chimneylinerjames Feeling the Heat

    Joined:
    Nov 26, 2012
    Messages:
    381
    ID= Inside dimensions
    Measure the inside of the flue to make sure you have enough room for the liner with insulation. If not, you would be best of taking out the existing flues.
  16. mellow

    mellow Resident Stove Connoisseur

    Joined:
    Jan 19, 2008
    Messages:
    3,142
    Loc:
    Salisbury, MD
    Most stoves work best with at least 15 feet of pipe measured from the bottom of the stove to the top cap.
  17. Joful

    Joful Minister of Fire

    Joined:
    Mar 7, 2012
    Messages:
    6,249
    Loc:
    Philadelphia
    Wow... if you only have 13 feet from the floor to the cap, then you indeed have a challenge. Best bet is to find a way to get a few more feet (even 2 - 3 feet will help) on top of that chimney. Short of that, smooth-wall stainless with a blanket wrap. No matter what you do, with a short flue, you may find yourself limited to burning only when outside temps fall below 40F. I have similar (but much less drastic) issues on the shorter of my two flues, although I have about 18 feet from the top of the stove to the cap.
  18. Michael6268

    Michael6268 Feeling the Heat

    Joined:
    Nov 19, 2005
    Messages:
    423
    Loc:
    Grafton NH/Upper Valley
    I beleive if the area from the T to the the bottom of your chimney/cleanout door is "sound" then most installers would not install a cap on the bottom of the T allowing for debris to fall down to the cleanout door/area.
  19. Woody Stover

    Woody Stover Minister of Fire

    Joined:
    Dec 25, 2010
    Messages:
    5,505
    Loc:
    Southern IN
    Manual says "This product was designed for and tested on a 6"chimney, 14-16'."
    Might get away with it with a smooth-wall liner and insulation, I don't know...
  20. Ablaze Tech

    Ablaze Tech New Member

    Joined:
    Nov 24, 2012
    Messages:
    21
    Loc:
    Neenah, WI
    Masonry chimneys that run up the side of the house suck. They are always affected by the cold. If the chimney is in rough shape tear that baby down and put an insulated class a chimney with a support box(dura-tech or similar brand) in directly above the stove. This will give you the best performance out of your stove and you will never have to worry about the chimney deteriorating in the future.
    jeff_t likes this.
  21. Ablaze Tech

    Ablaze Tech New Member

    Joined:
    Nov 24, 2012
    Messages:
    21
    Loc:
    Neenah, WI
    O yeah then you wont have to worry about a T section. When you sweep it everything will fall on top of the baffles in the stove. Just make sure you clean it off the baffles.
  22. Woody Stover

    Woody Stover Minister of Fire

    Joined:
    Dec 25, 2010
    Messages:
    5,505
    Loc:
    Southern IN
    Manual sez "designed for and tested on a 6" chimney, 14-16'." Might get away with it with an insulated, smooth-wall liner. I wonder if two 45* elbows to get into the masonry chimney would help (or even be possible with the thimble?) Or would more rise help before the stove pipe enters the chimney (entering the chimney higher?)
  23. Trickle

    Trickle New Member

    Joined:
    Jan 20, 2013
    Messages:
    47
    Loc:
    East Central Missouri
    Finally got up on the roof the other weekend to take care of some other projects and wouldn't you know it I forgot my measuring tape. I happened to have a dollar in my wallet though, so here are some pics to estimate the ID of the clay flue. Best guess maybe 7" or just over?

    Attached Files:

    • c1.jpg
      c1.jpg
      File size:
      394 KB
      Views:
      46
    • c3.jpg
      c3.jpg
      File size:
      94 KB
      Views:
      45
    • c2.jpg
      c2.jpg
      File size:
      208.6 KB
      Views:
      45
    • c4.jpg
      c4.jpg
      File size:
      237.3 KB
      Views:
      53
  24. Hogwildz

    Hogwildz Minister of Fire

    Joined:
    Nov 3, 2006
    Messages:
    6,788
    Loc:
    Next to nuke plant Berwick, PA.


    Not a real good idea to leave the bottom cap off the T. Enough on here have learned how that sucks cool air up through the bottom end of the T effecting both draft( causing poor draft from the stove), which also allows for a crapload of creo to build up in the stack.
  25. jeff_t

    jeff_t Minister of Fire

    Joined:
    Sep 14, 2008
    Messages:
    3,516
    Loc:
    SE MI
    That's gonna be tough to work with. Unless the mortar joints are perfect, it will be a struggle. Busting out the tiles will help.

    Figure in two 90s, coupled with the already short flue, and I agree that going with a new class A would work the best. It just might not be aesthetically pleasing.