Sorry about polluting this thread with the blower door idea -- should have started a new thread.
So, thinking out loud about a simple way to get the blower flow out of the house at the standard blower door test depressurization of 50 Pascal...
The specs below are for a Fasco blower sold by Grainger -- I think the blower I have is quite similar.
When you look at the flow rates vs pressure drop for each speed, the flow rate drops very slowly as pressure drop is added. So with no load on high speed, the blower door does 2400 cfm, and with 0.3 inches of water (75 Pa) pressure drop, the flow is only down by 20 cfm to 2380 cfm. So, for the range of pressure for a blower door test (0 to 50 Pa), the blower flow rate is essentially constant (I think).
So, to determine the flow rate at 50 Pa (as is used in a standard blower door test), could I run the blower at high speed and note the house depressurization on by Dwyer gage (say its 75 Pa), then go down to low speed and note the new Dwyer gage reading (say its 20 Pa) -- then I could interpolate between the two readings to estimate the flow at 50 Pa?
So, in this example, with 2400 cfm at high speed and 1200 cfm at low speed, the flow at 50 Pa would be 1200 + ((50-20)/(75-20))(2400-1200) = 1855 cfm. Knowing the volume of the house, I could then calculate the Air Changes per Hour (ACH) at 50 Pa and be able to compare it to other standard blower door tests.
This assumes that all 1/2hp furnace blowers put out the same flow rates, and I'm sure this is not strictly true, but this Fasco is close to the 2500 cfm that I measured on my used 1/2 hp blower.
Gary
Edit: the blower data is easier to read at the Grainger catalog page at the link below.
Item
Blower
Type
Double Inlet Forward Curve, Direct Drive, With Motor
Speed
4
Wheel Dia. (In.)
10-5/8
Wheel Width (In.)
10-5/8
CFM Range
2400 to 230 @ 0.000-In SP to 1.700-In SP
CFM @ 0.000-In. SP
2400, 1800, 1450, 1220
CFM @ 0.300-In. SP
2380, 1760, 1420, 1185
CFM @ 0.400-In. SP
2350, 1750, 1410, 1180
CFM @ 0.500-In. SP
2335, 1720, 1395, 1170
CFM @ 0.600-In. SP
2300, 1675, 1365, 1150
CFM @ 0.700-In. SP
2210, 1650, 1300, 1080
CFM @ 0.800-In. SP
2130, 1550, 1220, 1010
CFM @ 0.900-In. SP
1900, 1390, 1125, 925
CFM @ 1.000-In. SP
1720, 1225, 1010, 790
CFM @ 1.10-In. SP
1440, 1030, 845, 620
CFM @ 1.200-In. SP
1160, 840, 650, 465
CFM @ 1.250-In. SP
955, 735, 570, 380
CFM @ 1.30-In. SP
750, 635, 490, 300
CFM @ 1.40-In. SP
540, 435, 340, 245
CFM @ 1.500-In. SP
430, 325, 240, 120
CFM @ 1.600-In. SP
320, 215, 150, -
CFM @ 1.70-In. SP
230, 100, -, -
CFM @ 1.80-In. SP
-, -, -, -
Max. Inlet Temp. (Deg. F)
104
Max. Ambient Temp. (F)
104