Yeah not my problem. They are installing.Good luck installing a baro on an insert stack.
They said it's more or less a type of screen that we would not have to access to open or close. A type of filter to cut draft down perm. Downside is it will not be able to be adjusted. Baro is the term they used.They may put a key damper in the pipe but they ain't gonna be putting a barometric damper up in the chimney. And with an insert, seeing how you access it to open and close the thing is gonna be interesting also.
Yeah I know. I was talking about the install of it. I can care less if it's hard to do. I do care about performance of insert and so does the dealer. He has said that he has done this before. He has a trouble shooting process. While they pull the insert it will be a good time to put roxul behind it. That's a plus.Yeah? It's your home!
Well that does not seem promising. I'm just trying to get what everyone else claims they get out of insert. Osburn 2200. Wood put on two hours ago. Reached 700. All ready down to three hundred. No flames just coals. What would you guys do ? Obviously that's not good operation. Wood is under 20 mc. It is mixed hard woods. Split and tested with meter. What would be next step. Or what do you think could be problemNobody on the planet with more wood burning appliance device experience than John Gulland. Here is his take on baros for regulating overdraft with EPA stoves.
"The third potential solution is to install a barometric draft control in the flue pipe. Although a barometric control could work, it would also vastly increase the amount of air consumed by the system. The higher the draft, the more the control swings open and the more room air would flow into the venting system. These effects would reach their maximum during the coldest weather when draft is highest. That would represent a considerable energy efficiency penalty and could create depressurization problems in a well-sealed new house. Also, the barometric control could be the easiest path for smoke spillage into the room in a house with negative pressure problems.
The oil and gas industries have worked to eliminate dilution devices like barometric controls from their equipment because of the energy penalty and operational problems. The wood heating industry should probably do the same. In fact, the CSA B365 technical committee has already moved in that direction. A new clause proposed for the next edition of the code reads: 'A Barometric damper shall not be installed in the flue vent of an appliance unless the appliance has been certified for use with a barometric damper.'"
this is a good read. I wished he would have explained why oil is moving away from them. definitely a good read. thanks for sharing.Nobody on the planet with more wood burning appliance device experience than John Gulland. Here is his take on baros for regulating overdraft with EPA stoves.
"The third potential solution is to install a barometric draft control in the flue pipe. Although a barometric control could work, it would also vastly increase the amount of air consumed by the system. The higher the draft, the more the control swings open and the more room air would flow into the venting system. These effects would reach their maximum during the coldest weather when draft is highest. That would represent a considerable energy efficiency penalty and could create depressurization problems in a well-sealed new house. Also, the barometric control could be the easiest path for smoke spillage into the room in a house with negative pressure problems.
The oil and gas industries have worked to eliminate dilution devices like barometric controls from their equipment because of the energy penalty and operational problems. The wood heating industry should probably do the same. In fact, the CSA B365 technical committee has already moved in that direction. A new clause proposed for the next edition of the code reads: 'A Barometric damper shall not be installed in the flue vent of an appliance unless the appliance has been certified for use with a barometric damper.'"
why can't they put a hand damper in and modify the handle?Well that does not seem promising. I'm just trying to get what everyone else claims they get out of insert. Osburn 2200. Wood put on two hours ago. Reached 700. All ready down to three hundred. No flames just coals. What would you guys do ? Obviously that's not good operation. Wood is under 20 mc. It is mixed hard woods. Split and tested with meter. What would be next step. Or what do you think could be problem
I'm not sure how they couldwhy can't they put a hand damper in and modify the handle?
So are you saying you wish you did not have one?We do, but there's a few drawbacks. One is you pull a bit of air thru the baro, so it will pull some heat from the home. It cools the stack quite a bit also, but it's very effective in reducing draft. The problem with a baro on an insert is not having access to it. If there's a strong draft, the best bet is to reduce the intake a little bit to try and control the insert.