Best Way to stack 1000 gal propane tanks

NP ALASKA Posted By NP ALASKA, Jul 31, 2017 at 4:38 AM

  1. NP ALASKA

    NP ALASKA
    Burning Hunk 2.
    NULL
    

    Feb 3, 2008
    221
    39
    Loc:
    North Pole, ALASKA
    ok- i need to stack and connect 1000 gallon tanks:)

    Any suggestions?

    I was thinking a couple different options:

    Cutt long ways- 10" wide on both and the weld a band around them

    Next was 3 or 4 10-12" pipes

    Thoughts
    Anyone??
     
  2. sportbikerider78

    sportbikerider78
    Minister of Fire 2.
    NULL
    

    Jun 23, 2014
    1,901
    744
    Loc:
    Syracuse, NY
    If you're talking about welding on a pressure vessel and you don't have the experience for that, please don't do it. I'd hate to see it rupture during or after the weld when full. You could take out half a town with 1000 gallons of propane.
     
  3. maple1

    maple1
    Minister of Fire 2.
    NULL
    

    Sep 15, 2011
    7,491
    1,307
    Loc:
    Nova Scotia
    I'm quite sure these tanks don't have any LP in them....
     
  4. NP ALASKA

    NP ALASKA
    Burning Hunk 2.
    NULL
    

    Feb 3, 2008
    221
    39
    Loc:
    North Pole, ALASKA
    LOL
    Thanks for warning- I am sure these tAnks are
    Empty:)
    They have been venting open for about 4 years
     
  5. maple1

    maple1
    Minister of Fire 2.
    NULL
    

    Sep 15, 2011
    7,491
    1,307
    Loc:
    Nova Scotia
    I used 6x6 wood between my stacked 330's. Three of them, I think. Made a template for tank diameter and chainsawed a circular relief on each side of the 6x6 cradle-like, so there's only maybe 2-3" of actual wood between the tanks. Three more under the bottom tank, relieved only on top side for it to sit into. Then I put 4x4 across them top & bottom, along the sides of the tanks. Screwed & bolted everything together, & put strapping around all of it (the metal tie strapping stuff with holes in it for screws. Not sure that was the best way but it's what I came up with - didn't have to do any welding. I'd suggest checking out my install thread, but Photobucket messed that up.

    1000's are a lot bigger than 330's though - I'd likely try to do something with steel I could find easily, and some welding.
     
  6. DaveBP

    DaveBP
    Minister of Fire 2.
    NULL
    

    May 25, 2008
    1,153
    30
    Loc:
    SW Maine
    I put two 500s together by welding them with a skirt around where they were touching. I was aiming for minimal height to clear a steel center beam in the basement. It's been working for 4 years and I plumbed it so it can thermosiphon if the power fails.

    Don't know why you couldn't do the same with a couple 1000s.
     

    Attached Files:

  7. coaly

    coaly
    Fisher Moderator 2.
    NULL
    
    Staff Member

    Dec 22, 2007
    2,848
    387
    Loc:
    NE PA
    Unfortunately that is what compromises the tank.
    No DOT cylinders or ASME tanks are to be left open to the atmosphere.
    At night, cooling temperature of vessel allows outside moisture laden air to enter. During the day, heating expands air, increasing pressure, expelling air, leaving water that has condensed on the bottom behind. Day after day this accumulates at the bottom with no drain to remove water.
    Retired from the LP business, I inspected, certified and hydro tested cylinders.
     
  8. Dutchie84

    Dutchie84
    New Member 2.
    NULL
    

    Jun 15, 2016
    36
    1
    Loc:
    Nova Scotia, Canada
    Looking at the drawing, is there 3 large pipes connecting the two tanks, and then the skirt going around is just support to carry the tank? Meaning that the skirt isn't pressurized? This looks like the nicest set up I've seen yet, even though everything gets covered with insulation.
     
  9. NP ALASKA

    NP ALASKA
    Burning Hunk 2.
    NULL
    

    Feb 3, 2008
    221
    39
    Loc:
    North Pole, ALASKA
    Thats is the thought; spray foam once complete
     
  10. NP ALASKA

    NP ALASKA
    Burning Hunk 2.
    NULL
    

    Feb 3, 2008
    221
    39
    Loc:
    North Pole, ALASKA
    Thanks hopefully it mostly runs out the bottom hole then; made sure of this as the gas is heavy and would leave the tank in the bottom not the top- that is if I have read things correctly in my research. Thanks for the insight - experience means alot in this world:)

    Regards
     
  11. NP ALASKA

    NP ALASKA
    Burning Hunk 2.
    NULL
    

    Feb 3, 2008
    221
    39
    Loc:
    North Pole, ALASKA
    Thanks a bunch; I saw these a few years ago and was in my mind as I was working through this upgrade. Probably gonna model of your design:)
     
  12. NP ALASKA

    NP ALASKA
    Burning Hunk 2.
    NULL
    

    Feb 3, 2008
    221
    39
    Loc:
    North Pole, ALASKA
    Was curious of the same- my thought is to cutt the length of the tank 10" wide- top of bottom tank and bottom of top tank for water flow ans use the band as the final pressurized piece

    ????
     
  13. Bob Rohr

    Bob Rohr
    Minister of Fire 2.
    NULL
    

    Jan 9, 2008
    1,152
    167
    Loc:
    SW Missouri
    Any way to stand them upright, much better stratification leverage from a vertical tank.

    Three or 4 channels welded around the tank for legs.
     
  14. DaveBP

    DaveBP
    Minister of Fire 2.
    NULL
    

    May 25, 2008
    1,153
    30
    Loc:
    SW Maine
    You wouldn't want to make a long slot to connect the tanks. That would destroy the cylindrical strength of the tanks and they wouldn't be nearly as resistant to pressure. I just flame-cut three holes in each tank (8 X 8" ?) before joining them. According to my computer model, there is almost 30 gallons in the skirt around the middle. Every bit helps, eh?
     
  15. NP ALASKA

    NP ALASKA
    Burning Hunk 2.
    NULL
    

    Feb 3, 2008
    221
    39
    Loc:
    North Pole, ALASKA
    Good point; makes sense
    Ill stick with the 3 pipes approach
     
  16. nhtreehouse

    nhtreehouse
    New Member 2.
    NULL
    

    Feb 11, 2017
    14
    2
    Loc:
    New Hampshire
    Hey NP,

    I just finished welding fittings and legs onto a vertical 1000 gallon tank. Since I'm not stacking them, the only tidbits of advice I can send your way would be... I used 4" 7.5 lb/ft channel for the legs. That stuff has 5/16" web and 5/16" flanges. Worked really well. Also, I measured the thickness of the head and cylinder - on my tank, the heads are 1/4" and the cylinder is 5/16". There is a lot of metal there - about a ton.

    Best of luck, be sure to post some pics when you have these tanks together!
     
  17. BoiledOver

    BoiledOver
    Feeling the Heat 2.
    NULL
    

    Apr 14, 2013
    420
    152
    Loc:
    Right Here
    I, (who is more booger welder than boiler welder) stacked two 500 gal tanks. The attached image is a very poor compilation but does show clearly, the principal. I sacrificed and old 100 pound propane tank for the supports. It took several pattern cutting attempts to get a good fit. Used corrugated cardboard for the pattern to cut the 100 pounder into three supports. If a person had a source (from scrapyard or whatever) for steel pipe, it would be heavier gauge than the 100 pound propane cylinder which is 1/8" at best. I passed on some offered by the nearby pipeline crew, way too thick. Read too heavy, one inch wall by two feet diameter.

    Going this way requires consideration in cutting your inlet and outlets in your main tanks. Wouldn't want to have air pockets. So top center in lower tank and near the highest edge of the support in the upper tank. The welds on first test were pretty good but did have two pinholes in one and one pinhole in another. Second test was a winner.

    Keep in mind when pressure testing, that is a considerable volume. I loaded water from the drain on the lower tank until I guessed at where the level was. Was shooting for just below the lowest weld. Then finished the test with air, sure wish it coulda been more water but what ya gunna do. The air takes a long time to come up to 75 psi, and a long time to drain too (and loud coming out).

    All has been well for the few years it has been up and running.

    Image1.jpg
     
  18. Herm

    Herm
    New Member 2.
    NULL
    

    Jul 18, 2017
    2
    0
    Loc:
    Western Ny
    If you PM me with your e-mail I will send you a complete drawing, Mine has been in operation for 7 years and all is fine. I also have also have some tips on insulation.
     
  19. warno

    warno
    Minister of Fire 2.
    NULL
    

    Jan 3, 2015
    860
    232
    Loc:
    illinois
    I built 3 saddles between each of my 250s i stacked up. Worked out great. there's basically an air gap between each tank. I was trying to save height in my stack like everyone else, you can see why.


    20160827_112707.jpg
     
  20. NP ALASKA

    NP ALASKA
    Burning Hunk 2.
    NULL
    

    Feb 3, 2008
    221
    39
    Loc:
    North Pole, ALASKA
    Very cool; great way to save on space
    Ill probably end up with something similar and 3-4" pipes between them
     
  21. JohnDolz

    JohnDolz
    Feeling the Heat 2.
    NULL
    

    Dec 29, 2015
    365
    41
    Loc:
    Burlington, CT
    Glad to see that you are back in business and that your project is happening!
     
    NP ALASKA likes this.
  22. warno

    warno
    Minister of Fire 2.
    NULL
    

    Jan 3, 2015
    860
    232
    Loc:
    illinois
    Thank you.

    With yours being 1000 gallon tanks i would most defiantly build it STOUT. Hate to have a 1000 gallon tank of water fall on your foot. Bad day right there.
     
  23. maple1

    maple1
    Minister of Fire 2.
    NULL
    

    Sep 15, 2011
    7,491
    1,307
    Loc:
    Nova Scotia
    Did you mean 4" diameter pipes? I don't see any reason to go that big - or any bigger than the supply fittings on your boiler. I connected my tanks in a similar way to Warno - just used 1-1/4" black iron fittings. IMO the less you cut into an LP tank, the better. Even if only from the perspective of having that much less new weld to worry about not leaking. Are there any existing ports on them you can use? That's what I planned my stacking layout around.
     
  24. NP ALASKA

    NP ALASKA
    Burning Hunk 2.
    NULL
    

    Feb 3, 2008
    221
    39
    Loc:
    North Pole, ALASKA
    I was sizing up to help with stratification- my current stacked 500's have 1 1/4" - 3 of them. Should Instick with this?
     
  25. maple1

    maple1
    Minister of Fire 2.
    NULL
    

    Sep 15, 2011
    7,491
    1,307
    Loc:
    Nova Scotia
    I'm just not seeing any reason to go with bigger holes than your boiler ins & outs, especially with tanks that big. Mine stratify fine, being the same size holes. Maybe someone else can shed some light.
     