It looks like I might be finally able to add OAK's to my two BK Ashford 30's. Those who've been on this forum more than a few years already know the setup, two BK 30's pushed into walk-in fireplaces, the entry point is thru 22 inches of mud-stacked granite and red shale.

The stoves sit less than a foot off the rear wall of the fireplace, so total duct length will be very short, essentiall wall thickness plus a foot, with an elbow up into the stove's adapter. I bought a 3" OAK adapter plate, which BKVP said something like "should be fine for your short run", so it sounds like there's at least some chance I might need to up-size to 4 inch later.

The primary quesiton comes down to what size core drill to purchase for this penetration, which is obviously going to depend on the type and OD of the duct to be used, relative to a given nominal size (e.g. 3 inch or 4 inch). What type of duct is typically used in these OAK's? Given my mud-stacked stone wall construction, I'm going to want to favor something that's heavier and stainless, as we've seen too many other galvanized penetrations rot thru in the past, and the potential for shifting inside mud-stacked stone walls is higher than for modern walls with cement bedding mortars.

And then there's the connections to and exterior finishing of. Looking for some sort of rain hood that will look reasonably acceptable on exterior stone walls.

Specific duct product recommendations?
 
Sounds like 3" will work well. The duct size will largely determine on how restricted the air flow will be. Short runs with minimal 90º turns will work with 3". Longer runs with a few 90º turns will benefit from going up in size. Galvanized duct, aluminum flex duct are fine. Even PVC pipe will work as long as the connecting end transitions to metal to connect to the stove.
 
  • Like
Reactions: Ashful
I'm familiar with duct work that has standard sizes, and one end belled or crimped to fit into the next, whether that be HVAC duct or stove pipe. Is there no similar standard used for OAK piping?

I really want to avoid galvanized, as I've personally seen how fast it corrodes in our walls. Aiming for stainless, and preferably something with a heavier wall, if I can find something that will mate up with an exterior vent hood and interior plumbing.

If I can't find a workable stainless solution, aluminum might work.
 
Aluminum dryer duct would work. Given the short run, a length of 3" stainless stove pipe might also work.
 
  • Like
Reactions: Ashful
Schedule 40 pvc or stainless automotive exhaust pipe would be your best bet through the wall. If your walls shift as much as you say the flex duct could potentially crush/kink. Pvc is what gets used for 90% furnace exhaust as well. If you could find stainless spiral duct that would work as well, but working commercial hvac smallest spiral duct I’ve seen is 4”
 
  • Like
Reactions: Highbeam and Ashful
Just finishing up one of two large projects that are preceeding this one, so starting to think more about gettng the tools and materials in to make this happen. Of course, it's looking less and less like I'll get this done before running any stoves for the year, but heck... that's the way the start to most heating seasons seem to go. I also still have to clean and re-gasket the stoves, which was never done at the end of last season. ;lol

Speaking of which, didn't the prior heating season end just two weeks ago? This summer went way too fast.

PVC has a thick wall (at least sch.40), requiring a larger hole, and in the 3" size the OD is 3.5", many of the longer coring bits not even coming in that size (3.25" is more common). It's obviously also susceptible to heat, not that an OAK should be getting that hot, I guess.

The 3" stainless automotive exhaust tubing option is attactive, as I've had 3" stainless exhaust on some of my past muscle cars, and it's quite heavy and durable. But I'm wondering what elbow or flex duct might actually mate up to this cleanly? I guess I'm just used to venting systems that are designed with ID/OD and bell flare diameters that allow one pipe to mate cleanly with the next. That's obviously not going to be the case with random PVC pipe or automotive exhaust tubing.
 
PVC has a thick wall (at least sch.40), requiring a larger hole, and in the 3" size the OD is 3.5", many of the longer coring bits not even coming in that size (3.25" is more common). It's obviously also susceptible to heat, not that an OAK should be getting that hot, I guess.

The 3" stainless automotive exhaust tubing option is attactive, as I've had 3" stainless exhaust on some of my past muscle cars, and it's quite heavy and durable. But I'm wondering what elbow or flex duct might actually mate up to this cleanly? I guess I'm just used to venting systems that are designed with ID/OD and bell flare diameters that allow one pipe to mate cleanly with the next. That's obviously not going to be the case with random PVC pipe or automotive exhaust tubing.

So PVC, schedule 40, is sized based on OD so the wall thickness only effects the inside diameter. Same size hole.

I like the SS exhaust pipe idea the best and I would recommend the 4" because going back in to go from 3 to 4 would be difficult. I upsized my 3" OAK to 4" partly because it was so much easier to find compatible fittings, pipe, and even the termination hoods from the HVAC world.

I would plan on core drilling through such a stone wall at least 1/2" oversize so that you can correct slope issues, you want it to slope away from the stove, and if you get a weird loose stone in the hole you have some room to work. You'll need to seal the penetration anyway.

I expect you will want a piece of flex pipe between the stove and the rigid pipe anyway and the dryer vent section of a hardware store will have the parts.
 
Some insulation attached to the outside of the pipe would be preferred in our HVAC best practices. Foil backed duct insulation is made for that purpose, but any insulation would help. Engineers on commercial HVAC jobs here require it, and I believe it is in the residential building code as well. The insulation will help with the pipe degrading by electrolysis as well as helping with condensation, picture a can of cold beverage (cold air) in a warm environment.
 
So PVC, schedule 40, is sized based on OD so the wall thickness only effects the inside diameter. Same size hole.
While is true that scheduled PVC pipe (e.g. 40 and 80) are based on OD (3.5" for "3-inch"), I was referring to the PVC products folks actually face in a store, namely DWV versus S&D. Or to put it more clearly:

3 inch S&D OD = 3.25 inches
3 inch sch.40 OD = 3.50 inches
3 inch sch.80 OD = 3.50 inches

But no matter. I like their resistance to corrosion, but I don't think either is a great choice for installing in the back wall of a 300 year old fireplace, for several reasons.

I like the SS exhaust pipe idea the best and I would recommend the 4" because going back in to go from 3 to 4 would be difficult. I upsized my 3" OAK to 4" partly because it was so much easier to find compatible fittings, pipe, and even the termination hoods from the HVAC world.
Yep... that's the present debate. I'll have to un-box the 3 inch OAK adapter I bought for the Ashford 30. Does anyone have a photo of the 4 inch one, or can they get some basic dimensions?

I'm not worried that much about termination hoods, I think the difficulty of finding a suitable hood that mates up with automotive exhaust in either size is going to be a bit of a challenge, silicone will presumably be involved.

Probably looking at something like this, sandblasted and painted a suitable brown or gray:


I would plan on core drilling through such a stone wall at least 1/2" oversize so that you can correct slope issues, you want it to slope away from the stove, and if you get a weird loose stone in the hole you have some room to work. You'll need to seal the penetration anyway.
Agreed.

I expect you will want a piece of flex pipe between the stove and the rigid pipe anyway and the dryer vent section of a hardware store will have the parts.
Agreed. Although what's the common method of affixing incompatible pipe diameters, in this application? I guess air tightness is of low concern, other than leaking cold air or summer insects into the house.
 
The dryer vent/flex duct will slide right over which ever pipe you use as long as it’s the same diameter. The crimped end of an adjustable elbow will slide right into any pipe that is the same diameter, and you can crimp it tighter if necessary to make it happen. If you’re using the dryer vent I don’t see why you would even need an elbow at all.

Also make sure you don’t use dissimilar metals as they will eventually corrode due to electrolysis. If you do, use a healthy amount of silicone so the metals don’t touch. I’m partial to Solar Seal when it comes to sealing outside envelope of a building against air and water intrusion.
 
  • Like
Reactions: Ashful
I'd personally go with a 4" hole through the wall, and use stainless stovepipe...lots of adapters available down to 3" then...first thing that comes to mind is a 3-4" adapter for the old single wall gas furnace vent pipe...you'd have to decide if an increaser or decreaser works better.

I don't envy you going through a 22" wall...we just had to bore a 10" hole through concrete at work...it was a new and an old wall poured against each other...took 2 trips in with a 16" deep core bit on a vacuum mounted rig, 6' off the floor...fun.

Then I just finished a 10" hole through the basement wall at home, that was just block, but it was 5' off the floor, and had to hold the 44lb rig by hand...I could only go a couple minutes between breaks, and less at the end...but it went fine and was done in an hour ish...still gotta finish putting things back together on that one.
 
Last edited:
I'd like to avoid boring 4" if I can, esp. since there are a lot of options for 3.25" coring bits, it's a real common size.

3" x 16 gauge stainless automotive exhaust tubing looks ideal for the wall thimble. It's 3" OD, so it'd slide right into any hole left by a 3.25" coring bit, and the flex duct will slip right over the indoor end of it. I suppose I might need to ask an exhaust shop to expand the outdoor end a bit to fit a standard 3" wall vent, depending on how far down I can crimp those.

Found some nice ones here, that I could probably make slide into 3" exhaust tube:


Chimney pipe and any stove venting product is usually very thin wall, .016" type thicknesses. Not interested in going there. I don't need schedule 40, but I don't want cardstock thin, either.
 
Last edited:
Question. Are you going to be able to drill a 3.25” hole through the wall? Your description of the wall “22 inches of mud-stacked granite and red shale” makes me think the boring bit is going to want to drift into the softer parts of the wall potentially leaving you with an out of round hole of varying diameter.
 
Question. Are you going to be able to drill a 3.25” hole through the wall? Your description of the wall “22 inches of mud-stacked granite and red shale” makes me think the boring bit is going to want to drift into the softer parts of the wall potentially leaving you with an out of round hole of varying diameter.
We will find out, I guess! I've done coring thru walls of similar thickness and construction, the only difference being those walls were all 1800's and so likely contained Portland bedding mortar. This will be my first time doing a hole this large thru a pre-Portland (1700's) wall, but I expect the length of the coring bit itself will help keep everything straight as I go. I will definitely not be using a hammer drill, my only real concerns are water flow (not eroding out too much bedding mortar below), and getting the whole job done in time for the wall to dry before first deep freeze.

I learned something interesting about stainless exhaust tubing last night. The majority of it is a 400-series stainless, which is great at handling higher temperatures, but not very corrosion resistant, especially if placed in a stone wall where constant moisture and exposure to salts and lime is expected. There are plenty of makers of 304 stainless exhaust, but a lot of them are 18-gauge or thinner.

Individual tubes of 304 or 316 can be bought, but I didn't find any with an expanded end, so I might still have to buy or find an expander to make it compatible with a rain hood. But funny enough, I happend to find a whole universal dual exhaust kit on Amazon, which is reported to be 16-gauge 304 stainless and contains two 4 foot straight sections will an expanded bell on one end... all for like $120.

So that's on order now, we'll see if what arrives actually matches the description. Obviously I can check thickness / gauge pretty easily, but determining whether it's actually 304 vs. 400-series stainless might be a game of guessing with magnets. I might be able to get a QA guy at my prior employer to shoot it with a spectrometer gun, and see what it reads, if anything useful.

Also ordered some rain hood options, just to see what fits / works / looks good. Lots of "stainless" options on Amazon for like $10, but I suspect they'll be a stainless outer hood on zinc/steel shell, at that price. Also got some black aluminum foil flexible duct for indoor connection. Only thing I'm waiting on is determination of bell end OD of exhaust tube, if we even need a bell end, before making final decision on coring bit diameter.
 
  • Like
Reactions: GG Woody
Just a thought......

Is your house.
Given its age/construction etc.
Even remotely tight enough to require outside air delivery?

Not trying to ruffle feathers here but?
 
  • Like
Reactions: Tron
my only real concerns are water flow (not eroding out too much bedding mortar below), and getting the whole job done in time for the wall to dry before first deep freeze.
Core it dry...it works fine as long as you aren't drilling concrete/rebar. I just did a 10" diam hole in a CMU wall dry, no issues at all (other than its a lil more dusty, but that can be controlled with a drywall filter in a shopvac, and a helper) and the bit didn't even get hot (warm yes, hot no)
Take your time, go slow, pull the bit back regularly, it'll work fine.
Individual tubes of 304 or 316 can be bought, but I didn't find any with an expanded end, so I might still have to buy or find an expander to make it compatible with a rain hood. But funny enough, I happend to find a whole universal dual exhaust kit on Amazon, which is reported to be 16-gauge 304 stainless and contains two 4 foot straight sections will an expanded bell on one end... all for like $120.
If you need something modified, find a custom exhaust shop nearby, they can make little adjustments like that in seconds...often for free (at least our local guy will) if its just one or two quick things like that
 
You can wrap the stainless to keep it from wall contact as well, think like roofing ice and water barrier or something similar.
 
Just a thought......

Is your house.
Given its age/construction etc.
Even remotely tight enough to require outside air delivery?

Not trying to ruffle feathers here but?

There are more reasons than just tightness of home to implement an OAK. I can't think of a situation where it wouldn't be better to be burning outside air.
 
  • Like
Reactions: Ashful
I can't think of a situation where it wouldn't be better to be burning outside air.
Maybe if you have a basement stove and low level/borderline high radon...::-)
 
Maybe if you have a basement stove and low level/borderline high radon...::-)

We don't have radon in my area, but are you saying that the stove acts suck out the bad air from the basement and pull in fresh air to replace it?
 
We don't have radon in my area, but are you saying that the stove acts suck out the bad air from the basement and pull in fresh air to replace it?
Yeah
 
Is your house.
Given its age/construction etc.
Even remotely tight enough to require outside air delivery?
Definitely not! ;lol But by drawing house air to feed the stove, I am having enormous trouble keeping our indoor humidity up into a reasonable range, and I'm also constantly drawing cold air into the house which makes rooms distant from the stoves much colder than they'd likely be without stove demand creating that constant fresh air draw on those rooms.

I'm really looking forward to NOT filling two or three large humidifiers every day for 6 months at a stretch.

Core it dry...it works fine as long as you aren't drilling concrete/rebar.
Really? That would be ideal, if it could work. I had read that the combination of red shale (lots of clay) and granite would make this very difficult or impossible, but have to admit I'm not an expert.

I've only core drilled three times that I can recall, and two of those were block and concrete, only once thru stone similar to this. In that case, I used water, but it was a newer wall and not at the bottom of 4 stories of stone above.

Do you use a different bit for dry coring stone? I was looking at classic segmented diamond bits, for a good mix of clearing slurry from the clay-heavy red shale, and diamond for getting thru the granite. No hammer action, just turning it on my low-speed gear drill, and with minium water flow.

Take your time, go slow, pull the bit back regularly, it'll work fine.
Only concern for me would be cooking the bit part way thru the job, and leaving things in a half-drilled state. My gut tells me I want to get the hole done and get the stainless tube in there before letting it sit days half-drilled. I've never had issues with stone shifting before, but leaving it days while waiting to order up a new bit, thru possible freeze/thaw cycles, gives me the willies.

If you need something modified, find a custom exhaust shop nearby, they can make little adjustments like that in seconds...often for free (at least our local guy will) if its just one or two quick things like that
Yep. Used to do that back when I built hotrods and race cars in the 1990's. But haven't maintained any of those contacts, and not sure where I'd go for that work around here today. I'll do what needs doing, but hopefull I can avoid that by just using the pre-expanded tube end I ordered, if even needed.

You can wrap the stainless to keep it from wall contact as well, think like roofing ice and water barrier or something similar.
Yeah, I'm definitely thinking of doing this. My gas company did the same with the 3/4" stainless 304 pipe I put thru the wall to feed one of my gas stoves. They just used PVC tape, basically electrical tape, several layers thick.
 
  • Like
Reactions: GG Woody
FYI I run an oak, 2009 pretty tight construction, 3ksqft heating area and still run a console humidifier to keep it over 30% humidity. Without it, it is static city. Oak may help but not much imho.
 
  • Like
Reactions: GG Woody