I want to re-locate our electrical vehicle charger (EVSE) which is now on the side of the house and located pretty inconveniently. I want to move it to the edge of the gravel parking area. To do that, I will need to bury about 20ft of conduit across an area of lawn and a gravel path. Unfortunately I'll be crossing the main power feed to the house, theoretically buried 24" deep, but I don't completely trust that and the penalty for failure is high; so I don't want to attempt the 18" burial depth for PVC conduit (never mind the grunt work).
So I'm looking to use intermediate metal conduit (IMC) or possibly rigid metal conduit (RMC). I am thinking I can get away with only burying it 6", although I'll probably do more like 12". I am basing this on NEC Table 300.5 (Screenshot here).
Using column 2, it looks like the top row ("All locations not specified below") would apply, allowing 6" burial. It seems like the only thing that could get me would be the next to bottom row ("One- and two-family dwelling driveways and outdoor parking areas, and used only for dwelling-related purposes"). But as long as the IMC/RMC only comes up the edge of my parking area (and never crosses the driveway itself), I should be ok with 6" per the top column. Make sense ?
I'm also thinking the vertical runs coming up at each end, to the house and to the EVSE, can be done in PVC. Simply to save having to buy all those expensive IMC fiittings. So hopefully two 10-ft sections of IMC is all I need, the remainder can be PVC (assuming the transition can be gracefully done, with the threaded PVC fittings mating up with the threaded fittings at the ends of the IMC).
So I'm looking to use intermediate metal conduit (IMC) or possibly rigid metal conduit (RMC). I am thinking I can get away with only burying it 6", although I'll probably do more like 12". I am basing this on NEC Table 300.5 (Screenshot here).
Using column 2, it looks like the top row ("All locations not specified below") would apply, allowing 6" burial. It seems like the only thing that could get me would be the next to bottom row ("One- and two-family dwelling driveways and outdoor parking areas, and used only for dwelling-related purposes"). But as long as the IMC/RMC only comes up the edge of my parking area (and never crosses the driveway itself), I should be ok with 6" per the top column. Make sense ?
I'm also thinking the vertical runs coming up at each end, to the house and to the EVSE, can be done in PVC. Simply to save having to buy all those expensive IMC fiittings. So hopefully two 10-ft sections of IMC is all I need, the remainder can be PVC (assuming the transition can be gracefully done, with the threaded PVC fittings mating up with the threaded fittings at the ends of the IMC).