Does adding plaster to drywall count?

  • Active since 1995, Hearth.com is THE place on the internet for free information and advice about wood stoves, pellet stoves and other energy saving equipment.

    We strive to provide opinions, articles, discussions and history related to Hearth Products and in a more general sense, energy issues.

    We promote the EFFICIENT, RESPONSIBLE, CLEAN and SAFE use of all fuels, whether renewable or fossil.

JRP3

Feeling the Heat
Hearth Supporter
Sep 17, 2007
334
NYS
For the wall near the wood stove in my garage I put up 1/2 inch drywall but it seems code is for 5/8, can I add 1/8 of plaster on top, or another layer of 1/2, or should I just add a layer of 5/8 over existing 1/2?
 
For the wall near the wood stove in my garage I put up 1/2 inch drywall but it seems code is for 5/8, can I add 1/8 of plaster on top, or another layer of 1/2, or should I just add a layer of 5/8 over existing 1/2?
A woodstove can never meet code in a garage in the USA regardless
 
not if there is anytime gas or gasoline etc. in there, whether in a car, lawnmower, or jerrycans.

IF you do it (you'd not be the only one), I suggest you look up Canadian code that does allow it - as long as the stove is set a certain height above the floor (1ft?).

What is the code for that specifies drywall thickness? (it's not clearances, as the paper on the drywall already is flammable...)
 
  • Like
Reactions: Whitenuckler
The only car I regularly keep in it is electric. I don't store gas cans in there.

Google AI said 5/8 Type X drywall.
For a wood stove installation, you need Type X 5/8-inch fire-rated drywall, often used in multiple layers or with a heat shield (like metal/cement board with an air gap) to meet safety codes,
I also added a metal shield with spacers to the side of the stove. I think the firebox is more than 12 inches off the floor, the stove feet are on 8 inch cinder blocks.
 
The only thing that matters is how far the combustibles are from the stove - and that depends on the stove model (see its manual; for unlisted stoves its 3 ft ! - that can be cut to 1 ft using an approved heat shield spaced 1" of the wall and with a 1" gap at the bottom and open at the top to allow for convection to carry away the heat).

The paper on the drywall is the first combustible the heat sees, and the clearance distance is therefore the distance to the paper facing.
Add more drywall means your combustibles end up 1/2" closer to the stove each time. So that's not advisable.

Methinks Google AI is hallucinating.
 
  • Like
Reactions: Whitenuckler
The clearance to combustibles is the determining factor. Adding plaster doesn't change this. What stove is this for, a UL listed stove or an unlisted old stove.

The electric car question is interesting one. Rules will be changing I think.
 
  • Like
Reactions: Whitenuckler
A proper, ventilated, NFPA 211 wall shield will allow the stove to be within 12" of the combustibles behind that shield.
 
  • Like
Reactions: JRP3
I'd still add that 5/8 over the existing. Yes, the face is combustible, so you'd need something like begreen mentions, but when it comes to actually spreading a fire, the 5/8 drywall is going to slow it down much better than a half inch. 5/8 over 1/2 is even better.

That doesn't affect code clearance, just actual fire spread.
 
that can be cut to 1 ft using an approved heat shield spaced 1" of the wall and with a 1" gap at the bottom and open at the top
Can those gaps be larger than 1 inch? Since the stove is 14 inches off the floor and is only about 2 ft tall does the shield need to go from floor to ceiling, minus the 1 inch gaps, or can it be less?
 
Yes they can. Minimum of 1".

The shield does not need to go to the ceiling. I'm not sure what the exact requirement is, but I would put it 1 ft taller than the top of the stove. That is aesthetically acceptable imo.
 
  • Like
Reactions: JRP3
Thinking of something like this, stove is in a corner, angle top of the shield on the left to help reflect some heat into the room, back wall shield would be straight since it's further away. Green circle is a wood stove powered fan, pointed at the stove pipe in reality.

[Hearth.com] Does adding plaster to drywall count?
 
The angled shield won't make an appreciable difference imo.

I would not point the fan to the pipe unless you don't have a baffle in the stove (i.e. you're pushing too much heat up the pipe).

Then, your insurance may not pay out of something happens with the garage if you have a stove there. Just be aware ..
 
  • Like