Extending Hearth and the R Value Blues

  • Active since 1995, Hearth.com is THE place on the internet for free information and advice about wood stoves, pellet stoves and other energy saving equipment.

    We strive to provide opinions, articles, discussions and history related to Hearth Products and in a more general sense, energy issues.

    We promote the EFFICIENT, RESPONSIBLE, CLEAN and SAFE use of all fuels, whether renewable or fossil.
  • Hope everyone has a wonderful and warm Thanksgiving!
  • Super Cedar firestarters 30% discount Use code Hearth2024 Click here
Status
Not open for further replies.

mskif

Member
Hearth Supporter
Nov 22, 2008
76
Hudson Valley NY
I need to extend my hearth 9" to meet the requirement of 18" from the glass. 1/4 inch Durock has already been laid down and I have another 1 1/4" inch to work with to reach the required R value of 0.6.

From Regency Manual
* Hearth thickness of 0.5" with k value = 0.84",
r value = 0.6 or greater.

I have been to several hardware and masonry stores and no on has heard of Micore 300. One stove and stone materials shop sold me Permabase today which I found out that I can not use in several threads.

Even if I went with:
- Durock 1/4 inch .10
- Durock 1/2 inch .20
- Durock 1/2 inch .20
- Slate 1/4 inch .025
0.525 K Value

This would not give me the required 0.6 or greater. I am not sure what other options I have to get to the required 0.6 R.
 

Attachments

  • [Hearth.com] Extending Hearth and the R Value Blues
    hearth-2.webp
    29.3 KB · Views: 612
Have you tried calling any stove stores in your area? They might have a sheet of Micore they will sell you, or tell you where you can get some.
 
The stove store is the one that sold me the Permabase. But I could try some other stove stores.
 
Just thinking. Maybe you can use an air space instead. I know you only have 1 1/2 inches total to work with, but 1" of air space has an R value of 1.43. So, 1/2" would have an R value of .715. I know others here have used metal wall studs to create an air space for hearths. I know conventional metal wall studs are too large for your needs, but maybe you could find something like 1/2" square metal tubing. You could cut it to the length you need and have it on the bottom of your hearth or sandwiched between two sheets of Durock or whatever. The Lowe's down here has all types, lengths, as well as aluminum and steel.

BTW, I have also seen angle iron type metal pieces at Lowe's. It has holes along both sides and is thin steel, probably for shelves. You could cut those to length and have them sitting on the floor like a triangle. Side by side, they should be pretty strong.

I think you have a few options.
 
It would seem that the area in front of the ash lip would only need ember protection, since it is not getting direct radiant heat from the bottom of the stove.
 
Originally I thought I only needed ember protection up front, but the blower seems to blow hot air right in that spot. I am afraid I would be heating up the subflooring too much.

I may investigate using air space as Nic36 recommended. It looks like I need another trip to Lowes.
 
If you want to go with air space you can buy Z furring. Any sheet metal shop can make them. You can have it bent to any dimension and space it however you like. I would recomend having them bent out of 20 guage galvanised. For instance if you needed to bring your hearth up 1/2" you would ask for 1 1/2" x 1/2" x 1 1 1/2' Zs. This would give you a nice inch and a half to fasten to to the floor and a inch and a half to screw your tile backer to. Be sure to buy self drilling screws for your tile backer. I hope this makes sence. BTW I am a steel stud framer by trade.
 
Air space is a great idea, but with 1 1/4" to work with, you are really made for building it up with Micore and never worrying about it again. Keep trying to find a Micore supplier - assuming you can afford the time, it's worth the drive or the shipping to just get the right stuff, and do it the right way. Thinset over your 1/4" Durock layer, set in the 1/2" Micore, then thinset and set in the 1/2" Durock, screw that all down, and then mortar your slate down.

Good luck and keep us posted!
 
Edthedawg said:
Air space is a great idea, but with 1 1/4" to work with, you are really made for building it up with Micore and never worrying about it again. Keep trying to find a Micore supplier - assuming you can afford the time, it's worth the drive or the shipping to just get the right stuff, and do it the right way. Thinset over your 1/4" Durock layer, set in the 1/2" Micore, then thinset and set in the 1/2" Durock, screw that all down, and then mortar your slate down.

Good luck and keep us posted!

Thanks for the tip. This is really the route I want to go, but finding Micore has proved to be very difficult. All the stone places, stove shops and big box stores have never heard of it. They all seem to think that I am over thinking this and should just lay down the cement board. One Masonry store and stove shop even sold me Permabase.

I am off today so I my quest for Micore continues. If anyone knows of a source in the Northern NJ or Hudson Valley area of NY please let me know.
 
I'm not sure if this will help at this point but I'll share what I learned. I just had my Hampton HI300 inspected and passed this morning. I was concerned with my extension but it passed. My manual stated "Thermal floor protection not required if unit is raised 3.5" min. measured from bottom of stove. At this point the standard ember floor protection will be required."

In my case the fireplace floor and hearth height is greater than 3.5" so I only need standard ember protection for the hearth extension. I am 8" short from the 18" extension mark so I bought a piece of brownstone to lay directly on the floor. I plan to have a wool rug on the hardwood floor and then lay the stone on top of that. I currently have the stone resting on 1/2" wood boards so the stone is not in contact with finished wood floor. The LLBEAN wool hearth rug is due in any day now.

I think the key difference here is the 3.5" of hearth thickness. Your picture suggests less than 3.5" but I can't be sure. If that is the case, you will need to meet the R value stated in the manual.

I hope this helps.

Good luck!
 

Attachments

  • [Hearth.com] Extending Hearth and the R Value Blues
    hearth extend.webp
    104.4 KB · Views: 473
  • [Hearth.com] Extending Hearth and the R Value Blues
    hearth extend stone.webp
    56.4 KB · Views: 494
I Finally found someone who knows what Micore is at a stove shop today! They can get it within a week. She said it was refreshing to see someone taking R Values into account. She said that they find bad installations with singed wood subfloors. They even had someone who complained about smells because they used Permabase and the poly was off gassing.

The Micore product I ordered is actually resold by Majestic Fireplace and not under the Micore name. They call it Majestic Equious, part #EH2416. It is listed as .458 K and 1.09 R for .50". It comes in 16" x 24" sheets.

Thanks for everyone's help. It is much appreciated. I will be cutting the slate to size tomorrow.
 
After a 2 month wait my micore finally arrived. I picked it up from the stove shop today and can finally finish my hearth extension. I can do it right with an Rvalue of 1.46 (.60 minimum).
 
organic said:
Originally I thought I only needed ember protection up front, but the blower seems to blow hot air right in that spot. I am afraid I would be heating up the subflooring too much.

I may investigate using air space as Nic36 recommended. It looks like I need another trip to Lowes.

Isn't that blower on the bottom blowing air out the top?? I would have thought ember protection would be fine. Anyway, glad you are on your way to what you want...
 