So here's a quick synopsis of how the controls on the Froling react on a typical burn.
Lets assume the boiler has finished a load of fuel the day before, and is currently cold and in the "Off" mode. Both primary and secondary air ports will be closed. First of all, the boiler needs lit. (of course) To do this you open the outer insulating door which covers the loading door, the lighting door, and the combustion chamber door. As soon as this door opens, the draft fan turns on at 100%, and the primary air shutter moves to fully open. Wood is placed in the upper chamber, and some newspaper is placed just inside the lighting door. I generally leave the lighting door cracked for just a couple of minutes (really, just a couple... 2, maybe 3) to get a good roaring fire going. Close the lighting door, and close the outer insulating door.
Once the outer door is closed, the boiler goes into the "Heating up" phase. The draft inducer goes to 85%, and the air shutters begin metering primary and secondary air individually to tune the residual O2 content in the exhaust stream. If the boiler does not reach it's minimum stack temperature within a set time frame of closing the insulating door, it assumes there is no fire present in the boiler, and goes back into "Off" mode. Once the minimum stack temperature is reached, the boiler enters the "Heating" phase.
During the initial part of the "Heating phase," the boiler does not turn on it's thermal storage circulator. Once the temperature of the boiler reaches 65° C it will then release the storage circ and begin sending heat to your tanks or your zones. After the circulator circuit has been energized, the boiler then adjusts the burn conditions to maintain the user selected "Boiler Setpoint." The default boiler setpoint setting is 85°C. As long as the boiler temperature remains under this setpoint, the draft fan will operate at 85%. Once the boiler reaches and begins to pass the "boiler setpoint," the draft fan will begin reducing speed in an attempt to match the boilers output with the load. The Froling can modulate down to 50% of it's rated output while maintaining it's efficiency. I believe the draft fan will run at around 30% or so at it's slowest speed.
I don't have to tell you how fantastic it is to be able to match output with demand. As the storage tanks start to return warmer water to the boiler, and the delta T between the tanks and the boiler diminishes, the boiler automatically adjusts it's output to compensate. No need to increase flow rate with a dimished Delta T... just let the control on the Froling lower the output to match flow. Ingenious.
Towards the end of the burn, the residual O2 content in the exhaust stream will begin to rise regardless of air settings. Once the O2 content rises above the setpoint, the boiler shuts down the draft inducer, closes both the primary and secondary air ports, and goes back into "off" mode. At this point, the boiler still has quite a few coals inside the upper chamber and is quite certainly still warmer than the storage tanks. To deal with this, the boiler is monitoring storage tank temperatures at top and bottom, and will compare the temperature of the bottom tank sensor with the boiler temperature. Once the difference between the boiler termperature and the tank bottom temperature falls below a user defined amount, the boiler considers the tanks to be fully charged, and will turn off the circulator. This process does a couple of things... A) it ensures that the residual coal bed will have ample chance to cool once the draft fan shuts off, which will prevent the production of steam inside the vessel. B) it extracts every last btu from the boiler before shutting down. Of course, if the boiler should for some reason go over it's maximum setpoint, the circulator will come on and stay on regardless of the differential between the tank bottom and the boiler.
Overheat due to power out is obviously handled with the standard gravity loop with a normally open zone valve. Overheat with power on is simply a mechanical aquastat wired in parallel to the thermostat on your largest heating zone.
All in all, this control is pretty amazing. I'm not an engineer, so I can't speak to the requirements for developing such a unit, but the time and research invested in plotting curves for the primary and secondary air flows must have been intense of an by itself. One of the biggest benefits of this boiler is that while the controls are quite sophisticated, the actual operation of the boiler couldn't be any simpler. It's actually much simpler to operate than the typical forced draft gassers... which we all know require a little expiramentation in order to glean the best results.
I suppose that's all for now. I don't think I missed anything regarding how the controls work... if I did I'll have to catch up on it later.
cheers