The GARN controller supplied by Dectra does not incorporate a specific means to prevent over-firing of the unit. It seems to me that all that is needed to prevent an over-fire situation is to have a temperature controlled draft fan cut-out. As the unit approaches 200 or so degrees, the fan would be shut off, combustion would slow and temperature rise would be halted before reaching the boiling point.
I intend to implement this via a high-limit aquastat (like the Honeywell L4006E-1067) mounted to the front upper bung of the GARN, and wired in series with the low water cut out that is provided with the GARN. This is a break on rise, manual reset aquastat. I already have the temp well in the GARN for it.
Does this sound reasonable? Has anyone else incorporated an over-fire protection in their GARN controls?
I intend to implement this via a high-limit aquastat (like the Honeywell L4006E-1067) mounted to the front upper bung of the GARN, and wired in series with the low water cut out that is provided with the GARN. This is a break on rise, manual reset aquastat. I already have the temp well in the GARN for it.
Does this sound reasonable? Has anyone else incorporated an over-fire protection in their GARN controls?