I'm trying to understand the lower bound for the storage tank temperature. I'm getting an air source heat pump installed now so I also know the duct system design specs.
giving me:
first floor:
45k BTU/hr design temp 5F
1250 CFM from duct system
second floor:
49k BTU/hr design temp 5F
1600 CFM from duct system
I figure there should be a way to see what the minimum temperature that I can run with these known values right? From that I can calculate how much storage I would need so that I can have 12hours between burns, for example.
I took delta t = BTU/CFM * 1.08 and came up with a 109F lower temp based on a 70F indoor temp. Then 180F-109F = 71F plugged that into 8 * 71 * 2000 = 1.1million / (49k+45K) = 12hours.
Is this right? I thought it looked right, but now that I type it out, I'm wondering.
thanks
dave