Hi there.
I have an old(60s?) zero clearance Selkirk Metalbestos model 832 that recently failed WETT inspection. It has an 8" chimney that exits through the foundation(block) wall(above grade) and enters a wooden chase with cedar siding.
The inspector seemed to imply the setup was not fixable and wanted me to install their new gas insert. I wanted to get some other opinions. The following were the findings:
- "Due to width of chase we assume there is not adequate clearance "
- "The junction at the T comes to a 90. Can't see past that"
- "Rain cap not the type for this chimney"
- "Glass doors not meant for this model"
1. How wide does the chase have to be? My math would be 8" pipe + 2x2" gap + 2x0.75" ply + 2*0.75" cedar = 15" wide. The outside wall is brick so 11.5" deep. Or am I missing something? To confirm I'm assuming we have to open it up to to see?
2. Is a 90 not allowed? Are there any grandfather clauses accepted. Can't we just cut the old 90, widen the hole in the foundation and install some 30s. The top front of the fire place is enclosed behind some panel wood and would not be a big deal to open. Regardless of replace or repair we would have to open the chase.
3. Is there only one special rain cap that can fit the old chimney or are they fairly generic? I would think we could find a proper replacement?
4. The glass doors can be lifted off thus simple.
Don't get me wrong if there is something wrong I want to make sure it gets fixed correctly. A lot more has happened, that I won't bore people with, that has made me not believe this company is reliable.
I have an old(60s?) zero clearance Selkirk Metalbestos model 832 that recently failed WETT inspection. It has an 8" chimney that exits through the foundation(block) wall(above grade) and enters a wooden chase with cedar siding.
The inspector seemed to imply the setup was not fixable and wanted me to install their new gas insert. I wanted to get some other opinions. The following were the findings:
- "Due to width of chase we assume there is not adequate clearance "
- "The junction at the T comes to a 90. Can't see past that"
- "Rain cap not the type for this chimney"
- "Glass doors not meant for this model"
1. How wide does the chase have to be? My math would be 8" pipe + 2x2" gap + 2x0.75" ply + 2*0.75" cedar = 15" wide. The outside wall is brick so 11.5" deep. Or am I missing something? To confirm I'm assuming we have to open it up to to see?
2. Is a 90 not allowed? Are there any grandfather clauses accepted. Can't we just cut the old 90, widen the hole in the foundation and install some 30s. The top front of the fire place is enclosed behind some panel wood and would not be a big deal to open. Regardless of replace or repair we would have to open the chase.
3. Is there only one special rain cap that can fit the old chimney or are they fairly generic? I would think we could find a proper replacement?
4. The glass doors can be lifted off thus simple.
Don't get me wrong if there is something wrong I want to make sure it gets fixed correctly. A lot more has happened, that I won't bore people with, that has made me not believe this company is reliable.