That's a bummer. It sounds like you may be the best inspector of this system. Post pictures and feel free to ask any questions here if there are additional concerns.
I’ll see if I can get a picture of the attic penetration tomorrow. Here’s my mental checklist of honest to god safety things that need to be checked, and where we’re at on this install.

Stove clearances to combustibles and hearth protection: from hearthstone operators manual, double and triple checked. Good to go.

Stove pipe below ceiling clearances to combustibles: from Selkirk DSP manual/label on stove pipe, also good to go.

Chimney pipe in attic mounting: not how I would have done it, or 100% per the Selkirk manual (they used a roof support but put it inside on the penetration through the old roof deck before our addition put another 3-4’ of attic over that), but I see no practical or safety issue with it. Will grab a picture of this too for the brain trust.

Chimney pipe in ceiling clearance to combustibles: 2” per Selkirk chimney manual and labels. Was bad, but now good to go after adjusting stove position and mounting brackets plus trimming some more drywall and plywood to give a little bonus clearance.

Chimney pipe insulation shield: appears to be required per Selkirk installation manual and possibly standard building codes, though I haven’t looked at codes. Completely absent. There’s no insulation in that bay of the attic because it all fell out when I took the drywall down during the making of the stove nook, so I feel comfortable that it’s not going to burn anything down right away, but my interpretation is it definitely needs it long term.

Chimney stack 2/3/10 rule: I haven’t hopped up on the roof to check this out. I probably should given everything else I’ve seen so far.

Any other major code/safety things to look for on a stove/chimney install? I have to read and understand technical manuals for a living so I feel pretty comfortable reading and interpreting them for things like stoves, pipes, etc as long as I can find the correct applicable documentation. Im just slow as hell when it comes to doing the work especially if I haven’t done it before.
 
Some basic stuff like making sure the stove pipe and chimney are installed in the correct direction.
Examine the chimney flashing and storm collar now before the weather makes it harder to inspect.
 