Possible thermostat problems

  • Active since 1995, Hearth.com is THE place on the internet for free information and advice about wood stoves, pellet stoves and other energy saving equipment.

    We strive to provide opinions, articles, discussions and history related to Hearth Products and in a more general sense, energy issues.

    We promote the EFFICIENT, RESPONSIBLE, CLEAN and SAFE use of all fuels, whether renewable or fossil.
  • Hope everyone has a wonderful and warm Thanksgiving!

Lord Whorfin

New Member
Nov 2, 2026
13
Vermont
Greetings, all. New problem: Furnace in Manual light, Auto mode. Last year, when I turned the thermostat down, furnace would note that heat was not being called for and only feed enough pellets to keep small fire going, and the main blower would stop running but exhaust fan would keep running.
This year I had trouble lighting, but traced to bad exhaust temp probe, but also replaced board before finding it was the probe. Dip switchsd were set according to instructions with the new board.
Now, furnace maintains the same level of operation, no matter where thermostat is set- set at minimum, and temp control on board set to #1-
Furnace never cools down enough for blower fan to stop.

Thanks in advance for any help you all can provide.

Harman PF 100
Use about 9 tons per year
 
Greetings, all. New problem: Furnace in Manual light, Auto mode. Last year, when I turned the thermostat down, furnace would note that heat was not being called for and only feed enough pellets to keep small fire going, and the main blower would stop running but exhaust fan would keep running.
This year I had trouble lighting, but traced to bad exhaust temp probe, but also replaced board before finding it was the probe. Dip switchsd were set according to instructions with the new board.
Now, furnace maintains the same level of operation, no matter where thermostat is set- set at minimum, and temp control on board set to #1-
Furnace never cools down enough for blower fan to stop.

Thanks in advance for any help you all can provide.

Harman PF 100
Use about 9 tons per year
I have a P43, but it sounds like the same operation. I don't use a thermostat. I extended the probe. I do know that people use thermostats but they need to wire them in series with the probe. I have don't use that mode. I imagine you need to keep the temp dial all the way up to use an external thermostat. Then when the thermostat opens up the room temp probe you get xxx blinks and it either shuts off, or maintains the flame. I'd check all the wiring and make sure the thermostat works with a meter. Can you go back to the old board? Is the color of ESP probe wires the same as before?
 
  • Like
Reactions: silverfox103
Hello, Whitenuckler- thanks for the reply. The thermostat is a Harman-specific item, that adjust the size of the fire based on difference between room temp and thermostat settings. I have it turned all the way down, so the temp difference is about 10 degrees between them setting and room temp. I have a new thermostat from Harman, but I'm paranoid about changing another thing without knowing it is the problem. I guess the only way to find out is to do it, but hoping someone will have a better idea. Thanks again for your help.
 
Hello, Whitenuckler- thanks for the reply. The thermostat is a Harman-specific item, that adjust the size of the fire based on difference between room temp and thermostat settings. I have it turned all the way down, so the temp difference is about 10 degrees between them setting and room temp. I have a new thermostat from Harman, but I'm paranoid about changing another thing without knowing it is the problem. I guess the only way to find out is to do it, but hoping someone will have a better idea. Thanks again for your help.
That does not make sense to me. I would crank the stove temp dial to max if using a thermostat on my stove. That assumes its mounted in the same room. I'm not sure about how yours works, but that is the way it would work for a pellet stove like mine.
 
4 blinks: Can occur only in the Automatic Mode and indicates the Wall Control has failed or is not installed. If a Wall control is then installed the status light will automatically reset.

I took a quick look. I am not familiar with this at all. It appears they put a thermistor in the remote thermostat, as well as millivolt thermostat (contacts).
 
I guess I should just bite the bullet and change out a new thermostat- at least then I can eliminate that, and then check the dip switches again if new thermostat doesn't fix my issue. Thanks for your help.
 
I guess I should just bite the bullet and change out a new thermostat- at least then I can eliminate that, and then check the dip switches again if new thermostat doesn't fix my issue. Thanks for your help.
Check the wire connections. Try manual mode. Try and check everything you can before guessing. If you have a multimeter, we could probably figure out how to test the thermostat. There are only 4 wires. 2 appear to just be used for the Low Hopper LED so that is just an indication. The other T wires would be the ones to disconnect at the furnace and measure.
 
I have two Harman's: a P68 and a P38. Both have Honeywell thermostats; the 68 has four set backs. Has worked perfectly for about 15 years on automatic mode. The thermostat is two rooms away. The 38 is a simple basic thermostat, no set backs as it will not run on one of those, it is a manual start and shut off.

The 38 had an issue where the exhaust fan stayed on for @2.5 hours after you shut it off. I changed the exhaust probe and it took care of that problem.

I don't think you have much of a problem, just got to figure it out: thermostat, dip switch, or probe. As Whiteknuckler said red or black wires on the probe makes a difference. Don't be quick to throw parts at it. Now to eat my own words where you have an older unit and a new board: if your probe was red wires, get a probe with black wires and swap, or vicesa versa. There cheap online maybe $10 to $15. Stranger things have happened.

Tom