I was having a problem with our Integra II when we first started it up for this season. The unit would start normally and then immediately alternately display "Er0" (error 0) and "CL" (cleaning mode) after the end of the 21 minute starting cycle. An extensive cleaning did not help. After some snooping I found that the low level limit temp sensor located on the exhaust outlet was bad. Its a normally-open switch that is supposed to close once the exhaust temp reaches 45C (113F). I ran the start cycle and monitored the continuity at the two switch terminals. It registered very high (m-ohms) and never changed even when the stove was hot after 21 minutes of start-up. I inserted a jumper wire across the switch connections and the stove works normally.
The switch is a standard therm-o-disc style snap unit. Once I locate a replacement I'll follow-up on that.