Are you comfortable using a voltmeter? Can check that the fan is getting power.
 
Clean and oil it, even then it may not work and running with out the room fan is likely to result in high temperature shut downs.
 
Hello

The room fan turns on when the snap disc mounted on the exhaust blower reaches approx 120 Deg F. See the red arrow in the pic below. If this disc is bad and stuck open the room blower will not turn on. If the room blower does not turn on the stove will overheat and trip the Hi Limit snap disc.

Also if the room blower has ceased up and not working then it will not turn on.
 

Attachments

  • [Hearth.com] Room Fan has failed on Enviro Mini A
    EnviroMiniLowLimitSnapDisc.webp
    17.8 KB · Views: 132
Hello

The room fan turns on when the snap disc mounted on the exhaust blower reaches approx 120 Deg F. See the red arrow in the pic below. If this disc is bad and stuck open the room blower will not turn on. If the room blower does not turn on the stove will overheat and trip the Hi Limit snap disc.

Also if the room blower has ceased up and not working then it will not turn on.
How do I know if the disc is bad?
 
Jump it out!
 
Yes I can use a voltmeter. Once the stove has cooled, it was charging along at 420 degrees with Black Hills, will the power lugs be obvious?
Follow the wires to and from the fan. Look for spade connectors or connection points to probe.
 
Ok, A continuity checker of Volt-Ohm meter will only show Zero ohms when your stove is cool when testing the snap disc.

Remove the wires from the snap disc and connect them together. Turn the stove on and if the room blower comes on in 5 or 10 minutes like it normally does then the snap disc is bad. :-)
 