Secure Vent exhaust question
confusedbuilder
2
TN
Ok, need a little advice. I'm building a home that the owner wants a gas insert that uses 4.5/7.5 twist lock secure vent installed in the basement. My only vent option is to go 4 foot vertical then elbow through block then 8 foot horizontal and terminate out the side of the brick porch. My problem is the horizontal run will be under ground under a concrete porch, to keep the vent pipe away from moisture dirt I have some 8inch pvc sewer pipe I can use to run it inside, any thoughts? Will the exterior of this exhaust pipe get too hot?
First, you’re probably not installing an “insert” but a gas fireplace. What manufacturer & model are you installing?
Second, Does the manual allow for a horizontal vent run that is twice the vertical?
Third, most DV Pipe requires you to maintain a clearance to combustibles of 1” to the sides & bottom & 3” above it. You’re gonna need a 12” pipe to meet those requirements.
Reactions: stovelark
Astria Gemini DLX 35 Direct Vent. According to the spec sheet with one elbow and top vent I should be fine with the 4ft up and 8ft out, I have never installed one before and was curious about the heat generated through the exhaust. My only option is run the vent thru some 12" open core concrete block.
As long as you meet the vent manufacturer’s Clearance to Combustibles (CtC), you should be fine.