Stovepipe clearance of 18" vs. what the stove manufacturer certification plate states?

Ludlow Posted By Ludlow, Jun 22, 2018 at 12:42 AM

  1. Ludlow

    Ludlow
    New Member 2.
    NULL
    

    Jun 4, 2018
    84
    8
    Loc:
    PA
    Some people choose a certain stove based on it's close clearance claims. The instructions state that the clearances were tested with single wall. There is no directives to use any heat shielding with these clearances.
     
  2. begreen

    begreen
    Mooderator 2.
    NULL
    
    Staff Member

    Nov 18, 2005
    71,801
    10,595
    Loc:
    South Puget Sound, WA
    Seems a matter of whose margin of safety one wishes to believe then. Bring out the IR thermometer in December.
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
  3. bholler

    bholler
    Minister of Fire 2.
    NULL
    

    Jan 14, 2014
    12,731
    2,513
    Loc:
    central pa
    But the pipe has not been tested at all. The stoves clearances should be. So the only margin that is based on anything is the stoves. The pipes is based on a generic code.
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
  4. begreen

    begreen
    Mooderator 2.
    NULL
    
    Staff Member

    Nov 18, 2005
    71,801
    10,595
    Loc:
    South Puget Sound, WA
    So just ignore the pipe instructions and code?

    Screen Shot 2018-07-05 at 3.42.54 PM.png
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
  5. bholler

    bholler
    Minister of Fire 2.
    NULL
    

    Jan 14, 2014
    12,731
    2,513
    Loc:
    central pa
    Code says absolutly nothing about honoring untested clearances given for unlisted components. Because it is unlisted those instructions legally mean nothing. And the fact that they are untested means they are based on nothing. Squisher clearly showed us that code in canada says 18" no matter what so that is what it is. But code here gives generic clearances but says follow instructions for all LISTED components.
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
  6. bholler

    bholler
    Minister of Fire 2.
    NULL
    

    Jan 14, 2014
    12,731
    2,513
    Loc:
    central pa
    I am curious why you are so set on following these unlisted instructions but are fine with disregarding instructions for listed prefab fireplaces.
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
  7. begreen

    begreen
    Mooderator 2.
    NULL
    
    Staff Member

    Nov 18, 2005
    71,801
    10,595
    Loc:
    South Puget Sound, WA
    Similar issue, but that didn't answer the question. Just ignore the pipe instructions?
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
  8. bholler

    bholler
    Minister of Fire 2.
    NULL
    

    Jan 14, 2014
    12,731
    2,513
    Loc:
    central pa
    I did answer the question. Those instructions are for an unlisted product and the clearance is completly untested. So when it comes to code compliance those instructions are meaningless.
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
  9. begreen

    begreen
    Mooderator 2.
    NULL
    
    Staff Member

    Nov 18, 2005
    71,801
    10,595
    Loc:
    South Puget Sound, WA
    So you ignore Ventis's explicit instructions and install according to the stove instructions instead, correct?
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
  10. bholler

    bholler
    Minister of Fire 2.
    NULL
    

    Jan 14, 2014
    12,731
    2,513
    Loc:
    central pa
    What did i say i do here many times? I use doublewall in that case. Infact i used double wall for anything under 19" or 20" But by code those ventis instructions mean absolutly nothing because they are for an unlisted product. And that stated clearance has no basis in reality because it was not tested. The regency one was.
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
  11. begreen

    begreen
    Mooderator 2.
    NULL
    
    Staff Member

    Nov 18, 2005
    71,801
    10,595
    Loc:
    South Puget Sound, WA
    Then we are both in agreement. In spite of the stove mfg. saying a closer distance is ok for single-wall we are not comfortable with single wall pipe being that close to a combustible surface.
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
  12. Ludlow

    Ludlow
    New Member 2.
    NULL
    

    Jun 4, 2018
    84
    8
    Loc:
    PA
    The instructions clearly give tested minimums for every scenario except for horizontal run to ceiling distance, and they defer to the pipe manufacturer. That means that all others were tested and UL approved. Code is default for untested products. How close can you put an old untested stove to the wall? How about a sidewall? Aint it 3 feet absent a UL tested lesser distance?
     
  13. Ludlow

    Ludlow
    New Member 2.
    NULL
    

    Jun 4, 2018
    84
    8
    Loc:
    PA
    If a UL approved distance isnt good enough then UL testing and approval is useless.
     
  14. bholler

    bholler
    Minister of Fire 2.
    NULL
    

    Jan 14, 2014
    12,731
    2,513
    Loc:
    central pa
    No i am not comfortable opening my self up to the potential liability. I am confident the ul testing assures the clearances are safe.
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
  15. bholler

    bholler
    Minister of Fire 2.
    NULL
    

    Jan 14, 2014
    12,731
    2,513
    Loc:
    central pa
    And yes it is similar. But the big difference is in this case one product is a listed and tested unit the other is unlisted and un tested. In the case of prefab fireplace the instructions you are disregarding are for a ul listed system. Which is against code.
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...