I installed a new water heater awhile back, and thought I might also someday want another for a distant point-of-use. So I installed a sub-panel, protected with a 50-amp double-pole breaker in the main panel (and wired with 6 gauge Romex). I wired the water heater, spec'd with non-simultaneous 4500 watt elements, with 10 gauge and protected by a 30 amp breaker in the sub-panel (as per the water heater instructions).
The thought was that I might someday add a small 20 amp storage water heater for the distant sink. However, I now want to put a tankless electric water heater at that use point. To get the capacity I want, I need one that is spec'd for a 30 amp breaker (the specific one uses 5700 watts). I'm wondering if it's ok to drive that one off the same sub-panel (again with a 30 amp breaker and 10 gauge wire).
Each section of wiring is of sufficient gauge for the breaker protecting it (50amp/6ga for the feed from the main panel to the sub-panel, and 30amp/10ga for the feed from the sub-panel to each water heater). So there should be no safety issue. But 2 * 30amps is obviously more than 50 amps; seems like that's ok too, because it's normal for all the breakers in a given panel to exceed the ampacity of the breaker protecting that panel - IOW, if I add up all the breakers in my main panel, it's well over 500 amps, yet the main breakers (for the feed from the meter) are something like 150 amps.
So I think the main issue is whether or not the 50 amp breaker will trip, if I engage the tankless unit while the main storage water heater is also active. The total wattage would be 5700+4500 = 10.2kw, or 42.5 amps (at 240v). That's cutting it a bit close on a 50 amp breaker. There's also code of course (which I want to obey even though this won't be inspected); I'm probably good on that, since each wire gauge is sufficient for the corresponding breaker, but maybe not.
Appreciating any helpful thoughts (and yes, I know electricity is dangerous ).
The thought was that I might someday add a small 20 amp storage water heater for the distant sink. However, I now want to put a tankless electric water heater at that use point. To get the capacity I want, I need one that is spec'd for a 30 amp breaker (the specific one uses 5700 watts). I'm wondering if it's ok to drive that one off the same sub-panel (again with a 30 amp breaker and 10 gauge wire).
Each section of wiring is of sufficient gauge for the breaker protecting it (50amp/6ga for the feed from the main panel to the sub-panel, and 30amp/10ga for the feed from the sub-panel to each water heater). So there should be no safety issue. But 2 * 30amps is obviously more than 50 amps; seems like that's ok too, because it's normal for all the breakers in a given panel to exceed the ampacity of the breaker protecting that panel - IOW, if I add up all the breakers in my main panel, it's well over 500 amps, yet the main breakers (for the feed from the meter) are something like 150 amps.
So I think the main issue is whether or not the 50 amp breaker will trip, if I engage the tankless unit while the main storage water heater is also active. The total wattage would be 5700+4500 = 10.2kw, or 42.5 amps (at 240v). That's cutting it a bit close on a 50 amp breaker. There's also code of course (which I want to obey even though this won't be inspected); I'm probably good on that, since each wire gauge is sufficient for the corresponding breaker, but maybe not.
Appreciating any helpful thoughts (and yes, I know electricity is dangerous ).