Jprinter

New Member
Oct 5, 2025
7
Montana
Hi,

We’ve had a problem with our wood stove back puffing in our house, and are wondering if we ought to consider swapping it out with another stove (along with other, suggested changes). Some background first…

I’ve currently got a Lennox wood stove (model CI1000HT) in the bottom floor of a bilevel house (roughly 2,500 square feet). Our house was built in the late 1970s and, like other houses in our neighborhood, it is a tightly sealed house — too tight, in fact, with little airflow. That, combined with the stove’s location on the bottom floor, no intake ventilation for the stove, and a single-walled stove pipe (which gets quite cold during the winter, and apparently wasn’t fitted at the right angle) contributes to the back puffing.

Yes, we do heat the stove pipe and open windows and doors before starting an initial fire. It helps, but our house still gets smokey even will all of these measures. And yes, we’ve had the chimney cleaned recently.

The chimney cleaner suggested we redo the pipe — both using double walled pipe, and refitting how the stove is connected to the pipe, and is shaped at the right angle from the stove to the wall. (He also suggested installing a draw collar to the chimney pipe.) And some have suggested that after all of that we might also want to consider swapping out the Lennox with another wood stove that’s breaths better.

Anyway, I just got a free Vermont Castings Vigilant 1977 that’s in good shape. I’ve cleaned it and, as far as I can tell, nothing seems broken. I’ve done some research on the stove, and know it’s an older, well-built, sturdy stove — though it was "hi-tech" (for its time) by using the damper for secondary burns. I can see how it might “breath” better than the Lennox (i.e., through the temperature door in the back, and air valve). But I know it’s less efficient than more modern woods stoves, and that it lacks certain environmental features that found in modern stoves.

Overall, would others suggest or discourage me from replacing the Lennox and with this VC Vigilant 1977?

Our main concern is avoiding back puffing for any stove. So, I’m wondering if this VC Vigilant 1977 would be better a better fit for our house, as far as being able to “breath” better — and less inclined to smoke us out compared to the Lennox?

If I do install this stove (even as a temporary solution) I could install a double-walled (and better fitting) chimney pipe, and redo all the stove gaskets. Beyond that, we’d crack a window to prevent back-puffing — and I’d welcome any other ideas for additional mitigation. But again, I’m first trying to determine if it’s advisable to install this VC Vigilant 1977 in the first place.

Thanks!
 
The Vigilant, if in good working condition, will breath easier, but will be less efficient than the Lennox. However, backpuffing may still occur because changing the stove may be treating the symptom and not cause, which I suspect is negative pressure.

If you can tell us more about the house and include some pictures of the current stove setup (including stove pipe) and the chimney outside, we may be able to offer suggestions to address the negative pressure. There are several possible causes. Some are easier than others to address.
Here is a good site with a series on chimneys that explains causes of negative pressure:
 
  • Like
Reactions: Jprinter
I lived with, heated 100% with a 1970s vigilant for a couple of years in the early 80s. Perhaps my view isn't worth much, because I was very young and renting, and the whole group house didn't know what we were doing. And wood probably not dry enough at all. And those were cold winters in Vermont. I remember our wood was stacked outdoors in rows, and we had to dig it out of the snow. I don't remember the details of when we stacked the wood, but it certainly would not pass my standards now, I'm sure!

Compared to almost any stove I've had since, the experience was really bad. We were cold, pipes froze, chimney full of creosote. Like I say, if I did it now with my dry wood and understanding what to do, it might be better. It was really cold, sitting right in front of the stove.

Modern stoves are amazing -- more heat, less creosote, less fiddling, no (or minimal) chimney fire danger. And you'll burn half the wood with a modern stove.
 
The Vigilant, if in good working condition, will breath easier, but will be less efficient than the Lennox. However, backpuffing may still occur because changing the stove may be treating the symptom and not cause, which I suspect is negative pressure.

If you can tell us more about the house and include some pictures of the current stove setup (including stove pipe) and the chimney outside, we may be able to offer suggestions to address the negative pressure. There are several possible causes. Some are easier than others to address.
Here is a good site with a series on chimneys that explains causes of negative pressure:
Thank you so much for all of this -- it's terrific input, and I greatly appreciate all of your assistance!

I'm attaching some pics of the current set up of the Lennox stove, include the placard for that stove. (I didn't install it; it came with the house.) I didn't manage to take pics of the chimney outside because it was too overcast to get a decent photo. However, I've had several people look at the chimney (chimney sweeps, a few local experts on wood stoves), and they've all said it's the right height. No one believes the chimney height and build have contributed to the back puffing issue. (BTW, the plat covering in my pic is where I had to replace the glass for the door.)

Here are the the chimney pipe dimensions, in case that's helpful:

-The first chimney pipe measures 40" from the stove to where the 45 degree bend joint begins;

-The next section of chimney pipe measures 25" to where the next 45 degree bend joint begins;

-Then there's a 6" section of chimney pipe;

-Finally, there's a 3" cap that connects the last section of chimney pipe to the ceiling -- or where the internal chimney piping begins;

I take your point when you said:
backpuffing may still occur because changing the stove may be treating the symptom and not cause, which I suspect is negative pressure.
I'm sure you're right; I think the problems we face are mostly because of the tightness of the house and negative pressure. Our neighbors (whose home are similar to ours) keep a window by their stove open whenever they've got a fire burning. They also warm their chimney pipe with a torch or heat gun.

I confess I dislike the Lennox (which I find fussy and unpleasant to use for various reasons), and I do like the look and feel of a VC stove. But I do understand it is less efficient than a modern stove though, again, I'm wondering if it might work (even as a stop gap) as a stove that might at least breathe better and help cut down on the back puffing. Or if it's just not worth it.

Thanks so much, again.
 

Attachments

  • [Hearth.com] Whether to install a VC Vigilant, and how else to reduce puffing
    IMG_7709 2.webp
    26.8 KB · Views: 16
  • [Hearth.com] Whether to install a VC Vigilant, and how else to reduce puffing
    IMG_7707.webp
    29.8 KB · Views: 20
  • [Hearth.com] Whether to install a VC Vigilant, and how else to reduce puffing
    IMG_7708.webp
    9.9 KB · Views: 16
Basement install introduce more complexity. Im guessing there is a bit of a low pressure zone down there. How does the stove light on a cold start? Air sealing the upper floors can help. I’m guessing the house is not as tight as you think it is. (I could be wrong)
 
The house design, chimney location and height can affect draft. There are other chimney links on the WoodHeat website that are worth reading. At 5,000 ft, the chimney will need additional height. What is the current flue system height from stove top to the chimney cap? Is the chimney chased (enclosed) through the upper level? Is the offset in the room the only offset or does the chimney pipe also have an offset?

Negative pressure can be caused by leakage on the upper floor. This leakage can be through bath and kitchen fan vents and exacerbated when these fans are in operation. Sometimes leaky attic doors, windows, etc. can also cause a pressure drop on the lower floor.

The issue with any stove that has weak or failing draft is draft reversal as the fire dies down in the later coaling stage. At that point, carbon monoxide can enter the room from the coals. That's a very bad thing and may still happen with the Vigilant. A draw collar will help, but what if it fails or there is a power outage? In the least, the room needs a good, CO monitor in addition to a smoke detector.

Hopefully it's light enough now to take a picture of the outside chimney and post it.
 
Can you give us more information about the chimney that we can’t see? Length and diameter.
 
Basement install introduce more complexity. Im guessing there is a bit of a low pressure zone down there. How does the stove light on a cold start? Air sealing the upper floors can help. I’m guessing the house is not as tight as you think it is. (I could be wrong)
It does not light well on a cold start. Our neighbors often heat their chimney pipes with a torch or heat gun to help start things up, and ensure the smoke flows through the chimney properly (as well as have a downstair window and/or door open when starting up).

As for the house being tight, our contractor and neighbors have all remarked at how unusually tight our houses are -- all of which were constructed during the late 1970s/early 1980s, mostly be the same builder. FWIW...
 
The house design, chimney location and height can affect draft. There are other chimney links on the WoodHeat website that are worth reading. At 5,000 ft, the chimney will need additional height. What is the current flue system height from stove top to the chimney cap? Is the chimney chased (enclosed) through the upper level? Is the offset in the room the only offset or does the chimney pipe also have an offset?

Negative pressure can be caused by leakage on the upper floor. This leakage can be through bath and kitchen fan vents and exacerbated when these fans are in operation. Sometimes leaky attic doors, windows, etc. can also cause a pressure drop on the lower floor.

The issue with any stove that has weak or failing draft is draft reversal as the fire dies down in the later coaling stage. At that point, carbon monoxide can enter the room from the coals. That's a very bad thing and may still happen with the Vigilant. A draw collar will help, but what if it fails or there is a power outage? In the least, the room needs a good, CO monitor in addition to a smoke detector.

Hopefully it's light enough now to take a picture of the outside chimney and post it.
Here a the pics you requested of the chimney. I'm just relaying what several people have said after inspecting the chimney (contractors, those who install and repair wood stove, and our chimney sweeP: they feel it's at an appropriate height, it's has the right cap, and is in good condition.

BTW, our bathroom fans are very far from the stove, and aren't very strong at all. We don't have an attic doors, and the windows are in good shape.

I hear you about CO monitors. We have them installed, but need to get additional monitors set lower down. Some people in our town suggested we get the energy company to come by to do a CO2 inspection and air flow analysis. So, all of these considerations are definitely top of mind. Thanks so much!
 

Attachments

  • [Hearth.com] Whether to install a VC Vigilant, and how else to reduce puffing
    tempImage8Zye9D.webp
    57.7 KB · Views: 6
  • [Hearth.com] Whether to install a VC Vigilant, and how else to reduce puffing
    tempImageszFk7o.webp
    191.4 KB · Views: 7
  • [Hearth.com] Whether to install a VC Vigilant, and how else to reduce puffing
    tempImageC2YP5x.webp
    52.3 KB · Views: 7
  • [Hearth.com] Whether to install a VC Vigilant, and how else to reduce puffing
    tempImageSzbG2e.webp
    72.2 KB · Views: 7
  • [Hearth.com] Whether to install a VC Vigilant, and how else to reduce puffing
    tempImage4Qp1KS.webp
    39 KB · Views: 4
You have a mostly interior chimney. Cold starts shouldn’t be an issue. Do you crack a window by the stove when lighting? How long has your wood been drying?
 
  • Like
Reactions: Jprinter
I see about 5' exterior chimney and about 6" with an offset, interior stovepipe. How much chimney pipe length do we not see?

If the total is 14', it's not enough for this altitude unless the stove is a very easy breather. At 5,000 ft. here is what's needed for the average stove.

[Hearth.com] Whether to install a VC Vigilant, and how else to reduce puffing
 
You have a mostly interior chimney. Cold starts shouldn’t be an issue. Do you crack a window by the stove when lighting? How long has your wood been drying?

Yes, we crack a nearby window, and sometimes even a door, when lighting. We get our wood from a local dealer who provides the best wood in the valley. It’s as seasoned as we can get.
 
I see about 5' exterior chimney and about 6" with an offset, interior stovepipe. How much chimney pipe length do we not see?

If the total is 14', it's not enough for this altitude unless the stove is a very easy breather. At 5,000 ft. here is what's needed for the average stove.

View attachment 340768
Thanks for this. So, we’re just trying under 5K ‘ elevation, FWIW. Your analysis might be correct, but the chimney is certainly taller than what our neighbors have, and we’ve had several people here inspect the chimney— and all of them have said its height is more than adequate. Again, I’m just relaying what they’ve told me. I’m happy to get yet another opinion, however. Thanks you!
 
How dry is the wood though? Wet wood can make starting and running a fire very frustrating. Pick up a moisture meter at Home Depot, split a regular sized split in half, and test with the grain in the center.
 
  • Like
Reactions: kborndale and EbS-P
Yes, we crack a nearby window, and sometimes even a door, when lighting. We get our wood from a local dealer who provides the best wood in the valley. It’s as seasoned as we can get.

Buying wood from a dealer means there is a very small chance it is actually seasoned and ready to burn. You have to get a year ahead on your wood and you will have much better results.
 
I think the wood is probably the issue here, but OP may be burning a quick seasoning species.

A cheapie meter will either confirm or tell us we have to keep looking for the answer. $30 to help solve an issue vs the cost of a new stove or chimney seems like a no brainer.
 
Hi,

We’ve had a problem with our wood stove back puffing in our house, and are wondering if we ought to consider swapping it out with another stove (along with other, suggested changes). Some background first…

I’ve currently got a Lennox wood stove (model CI1000HT) in the bottom floor of a bilevel house (roughly 2,500 square feet). Our house was built in the late 1970s and, like other houses in our neighborhood, it is a tightly sealed house — too tight, in fact, with little airflow. That, combined with the stove’s location on the bottom floor, no intake ventilation for the stove, and a single-walled stove pipe (which gets quite cold during the winter, and apparently wasn’t fitted at the right angle) contributes to the back puffing.

Yes, we do heat the stove pipe and open windows and doors before starting an initial fire. It helps, but our house still gets smokey even will all of these measures. And yes, we’ve had the chimney cleaned recently.

The chimney cleaner suggested we redo the pipe — both using double walled pipe, and refitting how the stove is connected to the pipe, and is shaped at the right angle from the stove to the wall. (He also suggested installing a draw collar to the chimney pipe.) And some have suggested that after all of that we might also want to consider swapping out the Lennox with another wood stove that’s breaths better.

Anyway, I just got a free Vermont Castings Vigilant 1977 that’s in good shape. I’ve cleaned it and, as far as I can tell, nothing seems broken. I’ve done some research on the stove, and know it’s an older, well-built, sturdy stove — though it was "hi-tech" (for its time) by using the damper for secondary burns. I can see how it might “breath” better than the Lennox (i.e., through the temperature door in the back, and air valve). But I know it’s less efficient than more modern woods stoves, and that it lacks certain environmental features that found in modern stoves.

Overall, would others suggest or discourage me from replacing the Lennox and with this VC Vigilant 1977?

Our main concern is avoiding back puffing for any stove. So, I’m wondering if this VC Vigilant 1977 would be better a better fit for our house, as far as being able to “breath” better — and less inclined to smoke us out compared to the Lennox?

If I do install this stove (even as a temporary solution) I could install a double-walled (and better fitting) chimney pipe, and redo all the stove gaskets. Beyond that, we’d crack a window to prevent back-puffing — and I’d welcome any other ideas for additional mitigation. But again, I’m first trying to determine if it’s advisable to install this VC Vigilant 1977 in the first place.

Thanks!
Hi!


Thanks for sharing all the details—it really helps to understand your situation. Back puffing can definitely be frustrating and even hazardous, so it’s smart you’re looking into all the possible solutions.


From what you describe, a few things stand out:


  1. Tightly sealed house & no dedicated stove intake: Modern, airtight homes often don’t provide enough fresh air for wood stoves to draft properly. Without a dedicated fresh air intake for your stove, it can create negative pressure that pulls smoke back inside. Installing an outside air kit or a dedicated fresh air vent directly to the stove can help a lot with this.
  2. Single-wall stove pipe and incorrect angles: These can cause cooling of the flue gases, reducing draft and encouraging back puffing. Switching to double-walled insulated stove pipe and ensuring the stove pipe runs at proper angles (ideally short, straight, and with gentle bends) will help maintain hotter gases and improve draft.
  3. Draw collar suggestion: Adding a draw collar can improve draft by helping regulate airflow and stabilizing the burn, so it’s a good idea.
Regarding swapping the Lennox for the Vermont Castings Vigilant 1977:

  • The Vigilant is indeed a solid, well-built stove. Older stoves like that can “breathe” differently, with some manual control via dampers which can help you fine-tune airflow. However, they tend to be less efficient and produce more emissions than modern EPA-certified stoves.
  • Whether it will solve your back puffing issue depends more on the installation and airflow conditions than just the stove model itself. If the root cause is lack of proper ventilation or a poorly configured chimney system, the back puffing might persist with either stove.
So, if you do decide to use the VC Vigilant, definitely:
  • Replace the single-wall pipe with double-walled insulated stove pipe.
  • Fix all gaskets to ensure airtight connections.
  • Consider adding an outside air kit for the stove.
  • Keep a window slightly cracked to balance air pressure if needed.

Also, check the chimney height and clearance to ensure proper draft, and verify there are no nearby obstructions causing downdrafts.


In summary, the VC Vigilant could work if properly installed and vented, but solving back puffing mostly hinges on improving air supply and chimney setup rather than just swapping stoves. If you plan to stay with the Lennox, these same improvements still apply.


Hope this helps you make the best choice for your home and stay safe and warm this winter!
 
AI much?
Lots of generic suggestions repeating what has already been posted. Some comments like outside air for the Vigilant, don't apply.