Robvidusa

New Member
Nov 18, 2015
5
NY
Hi guys, I'm looking for ideas of how to install a Lopi Answer wood burning stove in my basement. The chimney is already in place and all the installation requirements were met but one: Ceiling clearance. On the alcove installation manual which I'm using, the minimum height for combustible alcove is 84". My beams are already 82" high and this entire room has drop ceiling that I'd like to keep it, but I'm already planing to remove the part around the stove. So this brings me to create a non-combustible ceiling around the stove to work as a heat shield, that as per installation requirements, needs to be 1" from the combustibles (beams and insulation), 3 1/2" thick and made of brick, stone or concrete. Does anyone here has any ideas, pics, materials that I should use or anything that could help me on this project? I'm stuck!
 

Attachments

Last edited:
You might be misunderstanding the heat shield requirements for a ceiling. I've never heard of requiring three and a half inches of brick or concrete for a ceiling heat shield! Most of the ceiling heat shields I've heard about consist of just a piece of sheet metal with the one inch air space behind it. Since you are just two inches shy of the required 84" height I would be confident a metal heat shield would provide adequate safety.

Welcome to the forum and good luck.
 
  • Like
Reactions: Robvidusa
A ventilated heat shield is what you want here. It can be made with any non-combustible material, on 1" non-combustible spacers attached to the floor joists. A 3' x 5' sheet of cement board works well for this or a sheet of sheetmetal. They sell ceramic spacers or you could cut some 1" spacers up from a length of 1/2" copper pipe.
 
  • Like
Reactions: Robvidusa
  • Like
Reactions: Robvidusa
A ventilated heat shield is what you want here. It can be made with any non-combustible material, on 1" non-combustible spacers attached to the floor joists. A 3' x 5' sheet of cement board works well for this or a sheet of sheetmetal. They sell ceramic spacers or you could cut some 1" spacers up from a length of 1/2" copper pipe.

Cool! Do you have any ideas for the material I could use on the cement board to fill up the other 2 1/2" I need?
 
What 2 1/2"? Do you have a picture?
 
You might be misunderstanding the heat shield requirements for a ceiling. I've never heard of requiring three and a half inches of brick or concrete for a ceiling heat shield! Most of the ceiling heat shields I've heard about consist of just a piece of sheet metal with the one inch air space behind it. Since you are just two inches shy of the required 84" height I would be confident a metal heat shield would provide adequate safety.

Welcome to the forum and good luck.

Nick,
Thanks for the reply and the big welcoming!
I just hope I didn't understand this right, my life would be so much easier! I'm uploading the page that I got it from, so you guys can help me think. But this is what it says there:

"Alcoves are classified as combustible and non-combustible. Non-combustible alcoves must have walls and ceiling that are 3 1/2 thick of a non-combustible material (brick, stone or concrete)..."

Again, thanks for your help and let me know what you think.
 
The cement board or metal can be left raw or painted with high-temp paint.
 
  • Like
Reactions: Robvidusa