Hello,
so I had found a technical bulletin..... for Durock.... Sept.... 2004
The technical bulletin says this...:
__________________________________________________________
DESCRIPTION
Space-saving DUROCK®Cement Boards are listed byUnderwriters Laboratories, Inc., for use with UL-listed solid-fuel room heaters and fireplace stoves. Used as a wall shield, DUROCKCement Board reduces by one-half themanufacturer-specified clearance (minimum 12") between the room heater or stove and a combustible wall surface.DUROCKCement board may also be used as a floor protector in place of one layer of 3/8" thick millboard.*
**Having a thermal conductivity of k ≤0.84 Btu in./(ft.2? °F) in the minimum dimensions specified by the room heater/stove manufacturer
So................... on the front of this bulletin........ they had a drawing....(picture)
of a wall behind a stove...... showing Durock behind a brick venneer......
Taking all this in........
with the idea of bringing stove closer to the wall.......(A jotul f118)
moving from 36" to no closer than 18".........
What is necessary to accomplish this with the use of Durrock........
I can fabricate anything and assemble... what needs to be done...
I have all the tools.......
I want to do the requirement...... and not go overboard......
It is more of a sense of piece of mind....... I am trying to achieve... by my actions......(safety yes.... but, in knowing that it is the right thing)
The blurb says "USED AS A WALL SHIELD"
can anyone elaborate....
Thanks, Soup
so I had found a technical bulletin..... for Durock.... Sept.... 2004
The technical bulletin says this...:
__________________________________________________________
DESCRIPTION
Space-saving DUROCK®Cement Boards are listed byUnderwriters Laboratories, Inc., for use with UL-listed solid-fuel room heaters and fireplace stoves. Used as a wall shield, DUROCKCement Board reduces by one-half themanufacturer-specified clearance (minimum 12") between the room heater or stove and a combustible wall surface.DUROCKCement board may also be used as a floor protector in place of one layer of 3/8" thick millboard.*
**Having a thermal conductivity of k ≤0.84 Btu in./(ft.2? °F) in the minimum dimensions specified by the room heater/stove manufacturer
So................... on the front of this bulletin........ they had a drawing....(picture)
of a wall behind a stove...... showing Durock behind a brick venneer......
Taking all this in........
with the idea of bringing stove closer to the wall.......(A jotul f118)
moving from 36" to no closer than 18".........
What is necessary to accomplish this with the use of Durrock........
I can fabricate anything and assemble... what needs to be done...
I have all the tools.......
I want to do the requirement...... and not go overboard......
It is more of a sense of piece of mind....... I am trying to achieve... by my actions......(safety yes.... but, in knowing that it is the right thing)
The blurb says "USED AS A WALL SHIELD"
can anyone elaborate....
Thanks, Soup