Hi
I have a 32" deep x 56" wide X 9' tall alcove where there used to be a fireplace and chimney. The chimney had issues so we had installed a lopi patriot stove and chimney liner and now for seismic upgrades have removed the chimney. We now want to reinstall the lopi to code. And at some future date, I'd like to have the flexibility of changing out the stove.
I have read and posted a few questions and think I understand what is needed but the contractors with whom I have spoken all seem to think I am going way over what is required. I would greatly appreciate answers to a few quick questions:
1) Distance to combustibles: Am I correct in that one layer of durock screwed into metal studs and then covered with ceramic tile does not reduce clearance to combustibles? That the only way to do that is with an NFPA211 clearance reducer?
2) 1" standoffs with the air gap at top and bottom for convection and then durock and tile allow for this reduction by 50%? (the contractor thinks that the standoffs, as described in the owners' manual, are only for mobile homes, which ours is not)
3) Durock or some similar material must line the entire alcove?
4) Are 2 layers of durock recommended over 1 for the hearth (floor) of the alcove? (The Lopi owners' manual only requires 1/8th or 1/4".)
Thanks
Rob
I have a 32" deep x 56" wide X 9' tall alcove where there used to be a fireplace and chimney. The chimney had issues so we had installed a lopi patriot stove and chimney liner and now for seismic upgrades have removed the chimney. We now want to reinstall the lopi to code. And at some future date, I'd like to have the flexibility of changing out the stove.
I have read and posted a few questions and think I understand what is needed but the contractors with whom I have spoken all seem to think I am going way over what is required. I would greatly appreciate answers to a few quick questions:
1) Distance to combustibles: Am I correct in that one layer of durock screwed into metal studs and then covered with ceramic tile does not reduce clearance to combustibles? That the only way to do that is with an NFPA211 clearance reducer?
2) 1" standoffs with the air gap at top and bottom for convection and then durock and tile allow for this reduction by 50%? (the contractor thinks that the standoffs, as described in the owners' manual, are only for mobile homes, which ours is not)
3) Durock or some similar material must line the entire alcove?
4) Are 2 layers of durock recommended over 1 for the hearth (floor) of the alcove? (The Lopi owners' manual only requires 1/8th or 1/4".)
Thanks
Rob