Froling Add-on Install

Marshy Posted By Marshy, Oct 4, 2017 at 9:15 AM

  1. jebatty

    jebatty
    Minister of Fire 2.
    NULL
    

    Jan 1, 2008
    5,594
    830
    Loc:
    Northern MN
    For the Froling display, I had the sheet metal cover, found a box that it would fit, cut out the openings for the meters, painted the cover red to match the Froling, and then used stick-on lettering.

    Data recording can be useful, especially to spot and diagnose any anomaly. I also use DS18b20 sensors to do this. My latest foray into temperature data recording is with a Raspberry Pi computer running a Python program. I did the programming myself, using available programs in Python and then modifying them to do what I wanted. The RPi can handle multiple sensors and with the Python program can be customized and is very flexible. I am hoping this winter, when I have more spare time, to add programming for control (off-on) of devices, like circulators, valves, fans, etc.
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
  2. Chris Hoskin

    Chris Hoskin
    TarmSalesGuy 2.
    NULL
    

    Aug 29, 2008
    544
    67
    Loc:
    Lyme, NH
    One disappointment was the fit of the clean out block plate opposite of the clean out door. Must be the welded on nuts are skewed.
    View attachment 216620

    seems like the left hand mounting bolt must not be engaged properly with the nut behind it? Somethings not right here, can you take another look? As you say, the nuts are welded to the door frame / port and the frame is welded to the boiler. Try loosening the two on the right so that you can adjust the plate/insulation block square to the boiler. Once you have all three bolts started, you should be able to push the assembly against the boiler so that it is flush and then tighten all three screws. This is a gasketed seal and it is important because the exhaust gasses travel back there. Let me know.
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
    ED 3000 and brenndatomu like this.
  3. Marshy

    Marshy
    Minister of Fire 2.
    NULL
    

    Dec 29, 2016
    741
    214
    Loc:
    NY
    I will take a second look. The gasket appears to be making contact all the way around. I will attempt to rectify let you know. Thanks for your support.

    By the way, I installed the overheat aquastat in the boiler jacket with the provided well but after reading the Honeywell instructions included with the aquastat they show the bulb being held into the well with either a retainer clamp or compression fitting. Neither was provided. Is it acceptable to just push the bulb into the well?
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
  4. Chris Hoskin

    Chris Hoskin
    TarmSalesGuy 2.
    NULL
    

    Aug 29, 2008
    544
    67
    Loc:
    Lyme, NH
    just make sure the sensor is well down in the well and you be fine. Well, well, well!
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
    Marshy likes this.
  5. Marshy

    Marshy
    Minister of Fire 2.
    NULL
    

    Dec 29, 2016
    741
    214
    Loc:
    NY
    I have some general hardware questions for you guys that have plumbed your boiler. I'm ordering my tubing, fittings and valves. The plumbing layout provided by Froling say to use weighted swing check valves. While searching Grangers and supply house I cannot find any that are weighted swing check valves, only spring loaded in-line check valves...

    Is the in-line spring loaded check ok to use?


    Second question is about air removal. I was going to go with the Amtrol Expansion tank with air purged and vent. I already have this setup coming out of my oil boiler and will add this to the outlet of the wood boiler. Is this sufficient for air removal of should i use an air purge thst has a coalescing element to scrub air?

    @Chris Hoskin, thoughts?

    Screenshot_20171207-170959.png
    Screenshot_20171207-171047.png

    Amtrol with purge and vent. Screenshot_20171207-171819.png

    Air eliminator only.
    Screenshot_20171207-171736.png
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
  6. brenndatomu

    brenndatomu
    Minister of Fire 2.
    NULL
    

    Aug 21, 2013
    3,180
    938
    Loc:
    NE Ohio
    McMaster Carr has swing checks...
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
  7. Marshy

    Marshy
    Minister of Fire 2.
    NULL
    

    Dec 29, 2016
    741
    214
    Loc:
    NY
    Weighted?
    Never thought of checking them for prices. Thanks.

    Refresh for edited post and second question above.
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
  8. brenndatomu

    brenndatomu
    Minister of Fire 2.
    NULL
    

    Aug 21, 2013
    3,180
    938
    Loc:
    NE Ohio
    I personally have never seen a small weighted check...3-4" and up is my experience...maybe they exist though, IDK...
    This is what I'm familiar with as a weighted check valve...
    upload_2017-12-7_17-37-54.jpeg
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
  9. Marshy

    Marshy
    Minister of Fire 2.
    NULL
    

    Dec 29, 2016
    741
    214
    Loc:
    NY
    Me too. I worked on a 42" anchor darling tilted seat swinging disk check before. I have little residential experience beyond hooking up a water heater. That's why I was asking about the in-line spring check.
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
  10. peakbagger

    peakbagger
    Minister of Fire 2.
    NULL
    

    Jul 11, 2008
    3,760
    959
    Loc:
    Northern NH
    I think they mean one of these

    https://www.pexuniverse.com/taco-219-4-flo-check-valve
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
    Marshy likes this.
  11. Fred61

    Fred61
    Minister of Fire 2.
    NULL
    

    Nov 26, 2008
    2,347
    457
    Loc:
    Southeastern Vt.
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
  12. maple1

    maple1
    Minister of Fire 2.
    NULL
    

    Sep 15, 2011
    8,408
    1,579
    Loc:
    Nova Scotia
    I just used ordinary swing check valves like in the pic above the expansion tank above. No issues 5+ years later. I think I was warned about possible chattering but haven't heard any of that. I actually took the flapper out of one and drilled a small hole in it to let a bit of water past when heating from backup. Just to maintain my storage temps a bit and also cut down on short cycling of my backup boiler. And I also used just an ordinary air vent like it sounds like what you say you already have. Not much fancy stuff on the supplier shelves here.
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
  13. Marshy

    Marshy
    Minister of Fire 2.
    NULL
    

    Dec 29, 2016
    741
    214
    Loc:
    NY
    Thanks guys. @Fred61, I'll probably avoid the watts check valve because it will cost about twice as much as the one I posted above after I buy the NPT to C adapter to sweat it in line.

    @maple1, I do already have an Amtrol like in the picture above. It's at the outlet of my oil boiler but I need one at the outlet of the wood boiler as well. Maybe not with fill capability because the other one will fill when water is circulated to the heating zones but I do need expansion capability in the wood boiler loop.
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
  14. nhtreehouse

    nhtreehouse
    New Member 2.
    NULL
    

    Feb 11, 2017
    49
    9
    Loc:
    New Hampshire
    All the literature suggests a minimum of 12 pipe diameters straight run before the swing check. I'm working on piping right now and things are a bit tight, space wise. Any idea how long your straight run is before the swing check? I might be able to get 12D, but I'll likely have a full port ball valve in there. Piping seems like a huge compromise every way one looks at it.
     
  15. Marshy

    Marshy
    Minister of Fire 2.
    NULL
    

    Dec 29, 2016
    741
    214
    Loc:
    NY
    Since @maple1 didn't reply I'll give you my opinion. A full port ball valve wind make much turbulence and if you can get 10 pipe diameters instead of 12 you'll still be fine.
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
  16. maple1

    maple1
    Minister of Fire 2.
    NULL
    

    Sep 15, 2011
    8,408
    1,579
    Loc:
    Nova Scotia

    Missed your question. I just looked. I only have 3" in front of one and 5" in front of the other. Had no idea about the 12x talk when I put this stuff together, but haven't seen any ill effects.
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
  17. Marshy

    Marshy
    Minister of Fire 2.
    NULL
    

    Dec 29, 2016
    741
    214
    Loc:
    NY
    Ok, I've been dragging my feet long enough. I searched high and low looking for the best deals on copper and fittings and trying to figure out how this all gets plumbed together. It was a close tie but I chose to go with SupplyHouse.com over coppertubingsales.com

    When it came down to it, it was within $20 for the common parts at each store. The cavet was supply house doesn't sell copper tubing and the other site did so I use my local hardware store prices to supliment the tubing in my cost comparison. Even though supply house was only about $20 higher, I still needed some more things from supply house so I went with one stop shopping.

    Thst being said, I bought everything I think I needed minus the tubing and it was $500. EEK.
    Plus someone gave me about $60 in fittings for free. Also, I still need about 40' of 1-1/4" type M tubing which is $42/10' locally.

    More to follow. While I'm waiting for the copper to come in I'll start tallying up all the other expenses made thus far. So begins the sulking also. Let there be bourbon I say.
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
    Highbeam likes this.
  18. maple1

    maple1
    Minister of Fire 2.
    NULL
    

    Sep 15, 2011
    8,408
    1,579
    Loc:
    Nova Scotia
    I would maybe suggest not tallying anything until perhaps 2 years from now - it won't sting QUITE as bad.

    Also, there were at least 10 times through my build when I said 'there, I have everything I need now'. Only to find myself running back to the supplier the next day.
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
    huffdawg, Highbeam and Marshy like this.
  19. peakbagger

    peakbagger
    Minister of Fire 2.
    NULL
    

    Jul 11, 2008
    3,760
    959
    Loc:
    Northern NH
    I must admit, if I am doing a big piping project, I visit home depot and buy more fittings than I need then return the ones I dont use. I make sure they are kept in good condition and they do end with a pretty good net sale.
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
    Highbeam likes this.
  20. Marshy

    Marshy
    Minister of Fire 2.
    NULL
    

    Dec 29, 2016
    741
    214
    Loc:
    NY
    They don't have crap for 1-1/4" fittings beyond an elbow. What they did have is twice as much as you can buy them for online. Lowes 1-1/4" elbow CxC is $7.04, supply house has them for $2.90. When you need 10 or 12 fittings that kind of mark up gets ridiculous. I mapped every thing out on paper and bought what I unlink I need. If I'm one or two short I'm run to town and get a few fittings but that's it. Normal retail is outrageous.
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
  21. hiker88

    hiker88
    Burning Hunk 2.
    NULL
    

    Aug 3, 2011
    239
    42
    Loc:
    Central Maine
    Hi Marshy,

    I haven't logged on in a long time; did it today out of a whim. Looks like you and I will have about the same setup. I have the Solar Technics 820 gallon system, and the BLT controller from Tarm as well.

    Yesterday it was about a high of 17f. Spent the day at 70f indoors with the main door open, and just the glass storm door between us and the elements (we like to let the light in). The system is still going strong and I don't worry about heat anymore.

    Let me know if you have any questions; I'll try and check back in more regularly.
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
  22. Marshy

    Marshy
    Minister of Fire 2.
    NULL
    

    Dec 29, 2016
    741
    214
    Loc:
    NY
    Thanks for tuning in Hiker88. I put up some sheetrock in the boiler room over the weekend. Still have a lot of rock to put up but need to get the insulation done. All the funky surfaces in the celing need insulating and I have no nailer in the corners so some are just floating. Other area are getting getting ridgid foam board for insulation before rock. Should look a lot different next time I show pics. Motivation is high right now because I'm sick of bringing in arm loads of firewood. That and my shenandoah stove is quite inefficient.
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
  23. hiker88

    hiker88
    Burning Hunk 2.
    NULL
    

    Aug 3, 2011
    239
    42
    Loc:
    Central Maine
    Marshy, how goes the battle?

    I have made one concession and we have closed the front door! -15 tonight, and a wicked cold streak ahead. Might be pushing 120 lbs a day in burns the last week.
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
  24. Marshy

    Marshy
    Minister of Fire 2.
    NULL
    

    Dec 29, 2016
    741
    214
    Loc:
    NY
    Current status...
    20171228_214315.jpg

    Edit: if anyone is reading this and about to sweat their own plumbing system, always put the union in line with the threaded adapter it will make your life easier! Either that or sweat the elbow on after the threaded adapter is installed.
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
    huffdawg likes this.
  25. huffdawg

    huffdawg
    Minister of Fire 2.
    NULL
    

    Oct 3, 2009
    1,435
    112
    Loc:
    British Columbia Canada
    Some nice clean sweating there. Is that your near boiler piping?
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
    Marshy likes this.