Froling Add-on Install

Marshy Posted By Marshy, Oct 4, 2017 at 9:15 AM

  1. Marshy

    Marshy
    Minister of Fire 2.
    NULL
    

    Dec 29, 2016
    812
    245
    Loc:
    NY
    Thanks for the compliment. I'm learning as I go. The real test will be under pressure lol.

    Yes, that will thread into the hot outlet of the boiler jacket. There are a few galvanised fittings provided by Tarm for the pressure relief valve. I'll have a few more pics as I go. Should be able to get the boilers circulator, heat exchanger and emergency dump zone plumbed. Gotta run to get more copper pipe right now and run a few errands.
    20171229_144737.jpg
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
  2. huffdawg

    huffdawg
    Minister of Fire 2.
    NULL
    

    Oct 3, 2009
    1,447
    114
    Loc:
    British Columbia Canada
    That looks excellent. Is that 1-1/4" or 1-1/2"? I used die-electric unions at the boiler inlet and outlet , it was recommended by the froling dealer. Not actually sure if they were a must have , but would have been a little easier to plumb without, with the tight clearance to the wall.
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
  3. huffdawg

    huffdawg
    Minister of Fire 2.
    NULL
    

    Oct 3, 2009
    1,447
    114
    Loc:
    British Columbia Canada
    Lol.. I felt the pain also . I never did tally it up.
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
  4. Marshy

    Marshy
    Minister of Fire 2.
    NULL
    

    Dec 29, 2016
    812
    245
    Loc:
    NY
    I knew nothing about them. Would have used them if I had known. What's another few $ at this point! It's all 1-1/4" type M.

    Yeah, so I've only sweat some small copper and never very much. Watched a few YouTube videos and now I'm an expert. Well, better wait until after the pressure test to claim that lol.

    Air purger and expansion tank will go about here and I'll get tee's plumbed for the dump zone. To the left you can see plywood pained white. That's where the pump and diverter valve will go.

    No liner installed yet. Figured I'd wait until I was done playing with fire and molten metal.
    20171229_153551.jpg

    BTW, I used permatex liquid tread sealant with PTFE at threaded connections. Stuff works well. It's like liquid pipe tape.
    15145801153041288213107.jpg
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
  5. huffdawg

    huffdawg
    Minister of Fire 2.
    NULL
    

    Oct 3, 2009
    1,447
    114
    Loc:
    British Columbia Canada
    Dielectric Unions Stop Galvanic Corrosion. To avoid this plumbers use a special coupling called a dielectric union. It's a coupling that acts as an electrical barrier between the two metals. One side is made of copper; the other, steel.
    You would need to put them at the black iron nipples coming out of the boiler.

    Then again what you have might be totally fine , be a bunch more work to install at this point .

    Also I dont know what quality unions you have available there , I had to put that thread sealant on the mating surfaces of the unions to make them watertight , you might want to dab some on before you get it all together.. could save you some time .
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
  6. hiker88

    hiker88
    Burning Hunk 2.
    NULL
    

    Aug 3, 2011
    239
    43
    Loc:
    Central Maine
    Looking good! Don't you love climbing in and out of the storage tank when your filling your voids and taping etc? ;)
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
  7. brenndatomu

    brenndatomu
    Minister of Fire 2.
    NULL
    

    Aug 21, 2013
    3,980
    1,457
    Loc:
    NE Ohio
    Pretty much a requirement...but a standard union will work...for a while... ;hm
    As much as it sucks to redo it now...it will be a lot worse later...
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
  8. Marshy

    Marshy
    Minister of Fire 2.
    NULL
    

    Dec 29, 2016
    812
    245
    Loc:
    NY
    Doubt Im going to change it now. I have other copper threaded connections into iron within my existing hydronic system that doesn't have dielectric connections. I might look beck on this and curse myself but it will be in 20 years or more lol. My pumps have dielectric flange kits because they have a steel flange and a bronze valve.
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
  9. maple1

    maple1
    Minister of Fire 2.
    NULL
    

    Sep 15, 2011
    9,851
    2,077
    Loc:
    Nova Scotia
    I didn't use any dielectrics in mine - have copper connected directly to black iron in a few places. Actually the old boiler system didn't have any either, and it was 17 years in when I redid the boiler, with no issues. Maybe not as pertinent with a closed system? One thing I did do was use a tiny dab of MotoSeal on the union mating faces, which I had on hand and decided to try on a whim - I have had issues with getting unions to not drip a little bit, in the past. Didn't have one union drip issue. So that's SOP for me & unions from now on.

    Anybody else find it odd that galvanized parts would be supplied? That is one thing I avoided all together.

    Looks good!!
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
  10. Marshy

    Marshy
    Minister of Fire 2.
    NULL
    

    Dec 29, 2016
    812
    245
    Loc:
    NY
    It's black iron, I misspoke when I called it galvanized.
    20171230_142317.jpg
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
  11. huffdawg

    huffdawg
    Minister of Fire 2.
    NULL
    

    Oct 3, 2009
    1,447
    114
    Loc:
    British Columbia Canada
    looks like those tees are galvanized.
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
  12. Marshy

    Marshy
    Minister of Fire 2.
    NULL
    

    Dec 29, 2016
    812
    245
    Loc:
    NY
    Looks like my take sensor wires will be too short. I'll have to add wire. What are you guys using, 20 gauge thermostat wire? Solder the joints?
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
  13. maple1

    maple1
    Minister of Fire 2.
    NULL
    

    Sep 15, 2011
    9,851
    2,077
    Loc:
    Nova Scotia
    I'm calling BI. :)
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
  14. Marshy

    Marshy
    Minister of Fire 2.
    NULL
    

    Dec 29, 2016
    812
    245
    Loc:
    NY
    LoL you guys crack me up. Don't care! :p LoL

    Next question for you guys that are using the American Solartechnics tanks... My heat exchanger had some zip ties on the small tubing to the main manifold. Mine no longer have any, should I put ties back on it? Also, the one manifols doesn't want to sit flat on the edge of the tank... is this common or cannot be resolved if the tire were on it?
    20171230_153752.jpg
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
  15. huffdawg

    huffdawg
    Minister of Fire 2.
    NULL
    

    Oct 3, 2009
    1,447
    114
    Loc:
    British Columbia Canada
    Just the colour of them
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
  16. Marshy

    Marshy
    Minister of Fire 2.
    NULL
    

    Dec 29, 2016
    812
    245
    Loc:
    NY
    You guys are fine, I was joking. See my questions above. Thanks!!
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
  17. peakbagger

    peakbagger
    Minister of Fire 2.
    NULL
    

    Jul 11, 2008
    4,568
    1,375
    Loc:
    Northern NH
    You might want to get in touch with "Tom in Maine". If I remember correctly when I had to pull my coil all the zip ties were brittle or sitting at the bottom of the tank. I believe they were there to make it easier to get the coil into the tank. I ended putting some back on when I pulled the coil as otherwise it was a "bundle of snakes". Tom now supplies a Stainless coil but I am not sure if its different design. Mine was not sitting exactly right on the wall when I put it back in but once I hooked the unions up it straightened out.
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
  18. brenndatomu

    brenndatomu
    Minister of Fire 2.
    NULL
    

    Aug 21, 2013
    3,980
    1,457
    Loc:
    NE Ohio
    They make stainless zip ties...
    https://www.harborfreight.com/12-in-stainless-steel-cable-ties-25-pk-69413.html
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
  19. Marshy

    Marshy
    Minister of Fire 2.
    NULL
    

    Dec 29, 2016
    812
    245
    Loc:
    NY
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
    huffdawg and brenndatomu like this.
  20. brenndatomu

    brenndatomu
    Minister of Fire 2.
    NULL
    

    Aug 21, 2013
    3,980
    1,457
    Loc:
    NE Ohio
    Only if it turns out those are galvan-ized fittings...;);););lol
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
    Marshy likes this.
  21. Marshy

    Marshy
    Minister of Fire 2.
    NULL
    

    Dec 29, 2016
    812
    245
    Loc:
    NY
    20171231_000624.jpg
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
  22. Marshy

    Marshy
    Minister of Fire 2.
    NULL
    

    Dec 29, 2016
    812
    245
    Loc:
    NY
    Is there a recommended minimum distance I should maintain between the pump suction and the mixing valve on the left? Is it going to cause any issues if it's about as close as pictured? I could move the pump to the right some if needed.
    20171231_005557.jpg
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
  23. maple1

    maple1
    Minister of Fire 2.
    NULL
    

    Sep 15, 2011
    9,851
    2,077
    Loc:
    Nova Scotia
    Should be OK. My loading unit has the pump built right into the thermo body.
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
    Chris Hoskin and Marshy like this.
  24. Marshy

    Marshy
    Minister of Fire 2.
    NULL
    

    Dec 29, 2016
    812
    245
    Loc:
    NY
    One joint at a time.
    20171231_185202.jpg
    20171231_184613.jpg
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
    brenndatomu likes this.
  25. maple1

    maple1
    Minister of Fire 2.
    NULL
    

    Sep 15, 2011
    9,851
    2,077
    Loc:
    Nova Scotia
    Get some extra slip couplings? I had a couple instances where I had to fix something and it was easier and faster to recip saw a section out and solder it back in quick with a couple of couplings.
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...