Help with stove adapter for 30NC wood stove

  • Active since 1995, Hearth.com is THE place on the internet for free information and advice about wood stoves, pellet stoves and other energy saving equipment.

    We strive to provide opinions, articles, discussions and history related to Hearth Products and in a more general sense, energy issues.

    We promote the EFFICIENT, RESPONSIBLE, CLEAN and SAFE use of all fuels, whether renewable or fossil.
  • Hope everyone has a wonderful and warm Thanksgiving!
  • Super Cedar firestarters 30% discount Use code Hearth2024 Click here

Blaine Coon

New Member
Oct 21, 2019
10
Virginia
Just purchased an England 30NC wood stove and used Ventis Double Wall black pipe with a Ventis double wall stove adapter. The adapter will not fit flush on the stove. The interior pipe hits the weld inside the stove which prevents it from sitting flush. I called the company today they quit selling the AC-1677 adapter (mentioned in the manual). I need suggestions for a flush adapter. Thank you. Blaine Coon
 

Attachments

  • [Hearth.com] Help with stove adapter for 30NC wood stove
    3FBE1097-DCB2-4FF9-8A04-D68EE2BA9102.webp
    58.9 KB · Views: 178
Last edited:
The outer shell does NOT have to set down on the stove top. Be most concerned that the inner pipe fits tightly against the actual appliance collar.
 
The outer shell does NOT have to set down on the stove top. Be most concerned that the inner pipe fits tightly against the actual appliance collar.
It does fit snug. Here is a pic of how the inner pipe hits the weld on the collar.
 

Attachments

  • [Hearth.com] Help with stove adapter for 30NC wood stove
    FF1E9F4E-EB57-403E-80DC-123E53694DF0.webp
    47 KB · Views: 155
So the tapered part of the inner layer mates up with the stove collar before the inner pipe bottoms out in the weld?
 
Sounds perfect. The inner tapered pipe makes the seal. If it’s tight and you can get screws in to connect the appliance collar to the inner pipe then run them in.
 
I trim down the inner pipe to make the outer sit down better. Or just run with no adapter. That works well on some stoves. Other stoves the adapter sits down perfectly.
 
The outer shell does NOT have to set down on the stove top. Be most concerned that the inner pipe fits tightly against the actual appliance collar.
If you want the clearance reduction provided by doublewall pipe it does
 
If you want the clearance reduction provided by doublewall pipe it does

That’s absurd. Does that particular brand of double wall support this theory with its installation manual?

Definitely not a requirement for DVL. I was worried for a minute!

(broken link removed to http://www.duravent.com/docs/product/L114_W.pdf)
 
Last edited:
That’s absurd. Does that particular brand of double wall support this theory with its installation manual?
A drawband collar around the "exposed" part of the adapter would take care of any "issues" in my mind (but I'd probably run it as is as I said earlier) although I'm sure that would not satisfy some inspectors. The UL guys would have little geek heart attacks when they seen that clamp! ;lol
 
  • Like
Reactions: bholler
That’s absurd. Does that particular brand of double wall support this theory with its installation manual?

Definitely not a requirement for DVL. I was worried for a minute!

(broken link removed to http://www.duravent.com/docs/product/L114_W.pdf)
That information was direct from Bryan the CEO of Olympia that manufacturers ventis. I find it a bit absurd that you think an inch of single wall exposed at the hottest part of the pipe would not effect clearances
 
A drawband collar around the "exposed" part of the adapter would take care of any "issues" in my mind (but I'd probably run it as is as I said earlier) although I'm sure that would not satisfy some inspectors. The UL guys would have little geek heart attacks when they seen that clamp! ;lol
I agree completely.
 
That information was direct from Bryan the CEO of Olympia that manufacturers ventis. I find it a bit absurd that you think an inch of single wall exposed at the hottest part of the pipe would not effect clearances
Would that clearance be part of the stove clearance spec? The flue collar being part of the stove. The lab testing doesn't specify a particular type of double-wall required.
 
Would that clearance be part of the stove clearance spec? The flue collar being part of the stove. The lab testing doesn't specify a particular type of double-wall required.
That would be a question for Englander. All I know is what Olympia told me which was the double wall has to run from the stove top to the chimney with no gaps.
 
I do see that the 30 has a lip at the back of the stove which in theory would sheild the stove collar.
 
I do see that the 30 has a lip at the back of the stove which in theory would sheild the stove collar.
I was thinking about that too...
 
I do see that the 30 has a lip at the back of the stove which in theory would sheild the stove collar.

it’s not a very tall lip on that rear heat shield but it is welded on.

no single wall pipe is exposed, just a sliver of the stove’s collar which of course is single walled but does it count as “single wall connector pipe” requiring 18” clearance?

I don’t think it matters what Bryan allegedly said. This is a ul listed product and unless the installation instructions require that outer shield to rest on the stove top then I can’t see how anybody can require it.
 
Looks like the flue collar extends just slightly above the rear heat shield. Less than 1/4”.
 

Attachments

  • [Hearth.com] Help with stove adapter for 30NC wood stove
    image.webp
    40.5 KB · Views: 148
it’s not a very tall lip on that rear heat shield but it is welded on.

no single wall pipe is exposed, just a sliver of the stove’s collar which of course is single walled but does it count as “single wall connector pipe” requiring 18” clearance?

I don’t think it matters what Bryan allegedly said. This is a ul listed product and unless the installation instructions require that outer shield to rest on the stove top then I can’t see how anybody can require it.
I don't know if the collar counts as single wall or not. As I said that is a question for Englander. But I do know what I was told by Olympia. And I know making it fit all the way down is extremely easy so why not just do it and be on the safe side? I honestly don't know if it says it in their instructions or not. I took their training class on their ventis line when it was introduced and that is what I have gone by unless a new product is introduced.
 
And I know making it fit all the way down is extremely easy so why not just do it and be on the safe side?
It would be helpful to the OP to describe the options and recommend how to in this case.
 
It would be helpful to the OP to describe the options and recommend how to in this case.
I did above. I either trim down the inner wall so it fits down or run just the pipe with no adapter if that fits better. Every stove is different I have also had to hammer out the inner wall to make it fit tight in the collar.
 
Thanks, sorry, I missed that.
 
  • Like
Reactions: bholler