jenny

New Member
Mar 19, 2010
4
canada
I bought an old Jotul, Classic DVNG D31719 that had never been used. When I turn the flame up, after a couple of minutes theres a click and the pilot light goes out.
Has anybody got a manual or installation guide? Wonder if it was installed right.
 
Sounds like the classic symptoms of an improper vent configuration.
It could be a mis-connected section of pipe allowing the combustion gases
to get into the intake air or it could be a blocked exhaust.
Open some windows & try to burn it with the glass off.
If it runs fine, it's the vent...
BUT DON'T JUST RUN IT WITH THE GLASS OFF! That's a BIG no-no.
If it STILL shuts down there may be a spill switch in the system...
I don't have a manual here, but I can look up your unit tomorrow at work
& see if anything jumps out at me...
 
You're right, its the venting. I tried what you said and it worked fine. I wonder if it was installed right. The vent goes straight out of the wall, direct, no snorkel. Not having a manual or installation instructions makes it difficult to know. The man who installed it obviously didnt get it right!
Thanks for your help
 