Thermostat for Quadra-Fire Classic Bay 1200i

  • Active since 1995, Hearth.com is THE place on the internet for free information and advice about wood stoves, pellet stoves and other energy saving equipment.

    We strive to provide opinions, articles, discussions and history related to Hearth Products and in a more general sense, energy issues.

    We promote the EFFICIENT, RESPONSIBLE, CLEAN and SAFE use of all fuels, whether renewable or fossil.
Status
Not open for further replies.
Morning guys,
The stove didn't kick back on last night,it was working fine for awhile and sometime after midnight just didn't cycle again; even with the thermostat showing 6 degrees below the one set in it.
So, I decided to press the "Up" arrow to 75 (set @ 68 for nights) degrees and the hold button to warm the place quick and nothing happened.
Not a noise from the fan to even try to start or anything, so I decided to press and hold the reset button next to the control box for a few seconds.
Stove it's doing its thing right now, not sure what else can be wrong at this point. :(

Thanks for all the help guys ,almost there......almost :'(
 
That's a bummer. Now I'm thinking it's not the thermostat. But you said the other one worked until the kids broke it...

I wonder if there is some sort of firmware update for the control box. Did a dealer install it ?

I'm not sure what to tell you, I'm still pretty new at this. :(
 
  • Like
Reactions: Gato13
Sounds like an issue with the thermocouple and not thermostat to me. Try taking the cover off and cleaning out the ash and be sure the wires are touching the end of the cover.
 
  • Like
Reactions: Gato13
Thanks Jonkman and rexrules,

Last season the control box was replaced by a local dealer.
I did replaced the thermocouple myself,since a pretty straight forward to wires connected; slice the cover till reaches the end and leave it about one inch showing into the fire pot (Being held by it's bracket). I connected the wires the same way as the old one.
The stove it's running now, once it finish a cycle will clean it up again and see f I can find something unusual there.

Thanks again fellas.
 
Hey guys,
Sorry for not updating on status for a few days,but Christmas got in the way :P
So,I decided to use my baseboard heating (oil) while we had family over for dinner,etc. Because of the pellet stove not working as I was expecting.
Yesterday, I decided to clean it up again, check all connections and everything seems to be correct.
Removed and blew air in the control box connection area.
My only question would be, do I have to "glue" the ceramic cover to the thermocouple with some sort of heat resistance product? Not to the very tip,but like on the outer end,so stays in place?
- Checked the thermostat, everything still set for swing of 2 degrees and still same issue. :(
Works for one cycle and doesn't kick back on again,last night it cycled twice and that was it.
I'm thinking about just getting the same old style thermostat, because this is driving me crazy. Not to mention We don't really need the programming feature.
We leave for work,set it @ 65,come home and set it to 70ish and so on.

After work I might stop and check the local dealer,maybe they got some answer,ideas or the old fashion thermostat.

Regards.
 
Of it cycled twice last night and worked I don't see how it can be the thermostat.

What exactly happens whem the thermostat clicks and starts calling for heat again? Does the stove feed pellets and not ignite or just nothing at all? On the initial startup do you have to press the reset button?
 
  • Like
Reactions: Gato13
Hey Gato,

You can try bypassing the thermostat entirely by connecting a jumper wire between the thermostat terminals at the back of the stove - where the two thermostat wires normally connect - UNPLUG of course before you do. Then plug the stove back in and see if it completes a normal start-up sequence. If it does, then the problem is with the thermostat or the stat wires. If it doesn't go through a normal start-up with the T-stat jumpered then it is something else, or in addition to the T-stat, causing the issue.

You shouldn't have to glue the ceramic TC (thermo-couple) cover on with anything - as long as it isn't angled down into the fie pot it should be able to maintain contact with the solder blob at the end of the TC wires. If the thermo-couple is bad you should see an amber colored light in your control box - less likely if you recently replaced the TC, unless maybe the connections to the wiring harness are bad.

Try the above and post back on what rex asked ie does it feed pellets on the failed start-up cycle.

DK
 
Last edited by a moderator:
  • Like
Reactions: Gato13
Thanks rexrules and DMKNLD :)
Nothing at all happens , no clicks to blower starts,no pellet dropping as a normal operation.
Sometimes I had to move the left lever down to off and then to Heat position again, this way starts a cycle for a bit,ends the cycle without even reaching the set temperature and doesn't kick back on.
So, I used to re-set it (press the button by the control box) and it did one cycle and again,doesn't kick back on again.
Before I replaced the thermocouple, it used to drop pellets and never got ignited sometimes. After I chance the piece, everything was back to normal..
Until the kids took care of the original thermostat <>
I just finished installing the old fashion thermostat on,I hope that works. :(

Otherwise I'll try what DMKNLD recommends.


Edit: Since I leave for work early in the A.M., let's just say that DMKNLD suggestion works; is it OK to leave like that (The jumper connected)? or it will cause some damage to something? or just the thermostat "feature" won't work and will keep cycling over and over?

Thanks
 
Last edited:
Edit: Since I leave for work early in the A.M., let's just say that DMKNLD suggestion works; is it OK to leave like that (The jumper connected)? or it will cause some damage to something? or just the thermostat "feature" won't work and will keep cycling over and over?

Thanks

Yeh, that's OK to temporarily run your stove that way. Bypassing the thermostat with a jumper just keeps the 'call for heat' circuit on full time instead of cycling the stove on and off via the thermostat when the set temps are reached. That's essentially how pellet stoves work that don't have thermostats, and instead use an on / off switch.

The only hassle when the t-stat is jumpered is turning it off, given that a Quad that doesn't have an on / off switch. Unplugging it will stop your combustion blower and thus the ability to clear the firebox of smoke. The easiest way to let the stove shut down is to open the hopper lid if you have a newer model that has a hopper switch, and that will shut down the auger feed. If no hopper lid switch, you can remove one of the t-stat jumper wires. But if it's easier on your CB to access the vacuum switch than it is to remove one of the t-stat jumper wires, you could instead pull off the vacuum hose at the vac switch end, which will shut down the vacuum circuit, that will then shut down the auger feed and let the stove shut down / clear the firebox of smoke. Once the combustion fan shuts down you can unplug the stove and then hook back up the vacuum hose or the t-stat jumper. If you want to start it up again with the t-stat jumpered you'll need to hit the reset after plugging it in.

Good luck! You'll get it figured out ! :cool: Keep us posted how things play out. DK
 
Last edited by a moderator:
  • Like
Reactions: Gato13
Well, something it's definitely wrong and I'm guessing it's not the thermostat :(
After I tried the new "original " thermostat, I kept running into the same issue. So, I decided to go ahead and try DMKNLD trick.
- First I put the jumper connecting the two terminals from where the wires are connected, with the wires also in place, ran for a while and sometime in the middle of the night,just gave up.
- This morning left the jumper in place,but removed the wires. Same result. Just got back from work,so I reset it while still the jumper in this position.
ran for about 45mins and that was it.
It just looked like this:
[Hearth.com] Thermostat for Quadra-Fire Classic Bay 1200i

After a while,the green light went away. Red still on (after 15mins or so after the stove finished it's thing)

The jumper install:

[Hearth.com] Thermostat for Quadra-Fire Classic Bay 1200i
It's the little black wire.

I this point no idea what it might be causing the issue
 
Yep, sounds like it's not your t-stat. Sounds like you get the normal start-up with the green and then red lights - which indicates your thermo-couple is working OK, then it quits feeding pellets at some point after that, correct ?

The process of elimination in pellet stove troubleshooting starts with being sure the exhaust pathway is clear of fly ash from the fire pot holes to the termination vent. Then the next step is to make sure there's no air leaks causing a vacuum circuit issue, which can often cause 'mystery shut downs' like you're having.

Are your door seals good ? Do the 'dollar bill' test all around it to make sure there is some resistance to pulling out the bill or piece of paper. You're sure your fire pot clean out 'trap door' is closing fully and is not hanging down more than a dimes width on the non-hinge side ?

Sawdust build-up can cause a partial obstruction in the vacuum hose, that goes from vacuum switch on the lower back of the stove to a nipple on the upper back side the auger tube. The vacuum tubing and / or the nipple can get blocked at the top of the auger, particularly if you're burning especially dusty pellets. You can clear it by disconnecting the vac hose at the switch end and blowing through it with Dust Off type canned air, or just blowing it clear with your mouth will work too.

It's best to take the vac hose completely off and make sure the auger tube nipple is clear by poking a toothpick or straightened paper clip into it. You can also check for cracks in the vac hose, most commonly in the auger connection end where it gets exposed to more heat. If the tubing end is cracked or doesn't fit snugly on the nipple you can just trim the hose end off a bit.

Vibration and dust build-up over time can compromise the electrical circuit contacts between your control box and the junction box. With the stove UNPLUGGED (standard disclaimer), try removing then re-seating the control box. Is your control box the original one, or is it the upgraded clear one ?

Check the above stuff and then post back. If no change, the next thing to do is to temporarily bypass your vacuum switch to rule out a bad vac switch, which isn't too hard to do but takes a little more electrical awareness.

Good luck ! DK
 
Last edited by a moderator:
  • Like
Reactions: Gato13
I decided to disconnect everything and start with everything clean and give me a chance to check behind the stove,etc. I did use the blower,door was open by the way,still the whole living room it's a mess :D
[Hearth.com] Thermostat for Quadra-Fire Classic Bay 1200i

[Hearth.com] Thermostat for Quadra-Fire Classic Bay 1200i

Used the vacuum ,blower,wire brush,etc to clean the inside nicely. Removed interior panels ,to vacuum exit to fan,etc.

I started stove again 2 mins ago......fingers crossed!
 
  • Like
Reactions: DMKNLD
DMKNLD, I was uploading the images and writing my post when you were also writing yours :p

I didn't do the dollar bill test,but doors close tight. I did a good clean up inside and out.
Now just need to clean the house :(
I'll report back.
 
Hello,
First of all,please apologies for triple posting; this post almost two days after the second one :)

So, I ran the stove with just jumper in place with the thermostat wires completely off.It was set in "Medium"

Just in case my stove is way different to others, there's a button called "Heat output switch" with threes settings : Low,medium and High.
I always had it in medium with a fairly low feed rate.
So, I plugged the stove and ran fine for maybe 1 hr and back to the same (this after cleaning it as above posts show). So I decided to go for the low setting,thinking it might run "longer".... About the same result. Gave up for a day, yesterday after work decided to go for the High option and see what it does...
It's been running for over 12hrs and still going :D

The switch and its location:
[Hearth.com] Thermostat for Quadra-Fire Classic Bay 1200i

I was worried about the flame being or getting too big,but it's a "perfect" flame I'd say.
The glass starts to get some ash,but you can see the flame size seems ok,the place its warm ==c

[Hearth.com] Thermostat for Quadra-Fire Classic Bay 1200i
[Hearth.com] Thermostat for Quadra-Fire Classic Bay 1200i

So, that bring more questions. Is something wrong with the switch? the feed rate ? or something else.......I'm planning on letting it run for at least till noon (6am right now) and shut it off,clean it off and try the medium rate again.....Double testing,just to make sure ;em

Thanks guys ;)
 
OK, that's a good breakthrough - yes, warm is good ! :) So that sounds like a feed rate related issue, where the high stove setting gives enough fuel feed to keep the flame burning consistently, but not on the medium or low stove settings. When the feed rate is set correctly on the high setting it should have a flame height that is 4-6" above the fire pot. From your pics it's a little hard to tell but it looks like your flame height is a good bit less than that. So you should open your feed gate up in small increments, wait about 10 mins or so to see how the flame corresponds, then open it up a bit more again as needed. The flame height will ebb and surge some, but should be generally in the 4 - 6" range on the high setting. Then that feed rate setting is right for the medium and low settings on the stove as well. The flame should be brisk and yellow to white in color.

The other feed related cause could be sawdust and fine pellet pieces built up at the bottom of the hopper, which can keep the regular sized pellets from getting picked up by the auger screw. Do you periodically vacuum out those pellet 'fines' that collect there ? If not, that can cause an insufficient amount of pellets to be fed to the fire pot. If the bottom of the auger tube is clear of fines, you could have a partial pellet 'bridge' at the top of the auger, particularly if the pellets you're burning are consistently longer than an inch and a quarter or so in length. If you have a small mirror you can hold it at the bottom of the pellet drop chute, above the fire pot, and shine a flashlight beam off the mirror to see if there are any pellets obstructing the top of the chute. Or you can take a straightened out coat hanger or long handled screw driver and poke around at the top of the drop chute to break up any 'bridged' pellets that might be partially blocking the pellet feed.

A couple other thoughts. Did you clean the stove glass before you ran the stove on high, or was it dirty like that before? The reason I'm asking is that your glass shouldn't get that dirty overnight, without some other air flow leak or a vent restriction issue that would cause allot of sooty ash to be deposited on the glass. Did you clean the vent all the way to its termination with a vent brush to make sure it is clear ? Lastly, what pellet brand are you burning? A stove and the venting can be perfectly clean, with the correct feed rate and no air leaks, and the stove can still burn crappy with poor quality pellets. After my 1st burn season, when I mistakenly bought 4 tons of 'dirt in a bag' pellets, I can speak to that personally. :(

Update back again after you've checked the above stuff. It must be cold for you guys in NY like it is here in ME, so having a warm house on New Year's eve is a good resolution to make ! Cheers, DK
 
Last edited by a moderator:
Status