Okay now I'm really confused, after reading the manual. You guys are saying that if I'm in room mode set the temp for 75 it should run all day looking for 75 degrees. When it hits 75 it should lower or raise temp, but not go out. And in control mode it should look for 75 (4) and do the same thing. When I first was testing it in room mode it shut off, it didn't lower the heat. Last night I started it in controlled heat it was on 50 or 1 and still is. I switched it over to ignitor off, room mode, still on 50 and it ran all night and is still running now at 80 ish. This is at the external sensor. It's been running at the same flame temperature since last night. According to the manual it should be somewhere around 50 and I image barely running which it hasn't done. Help me out. I'm posting a pic of my settings.
You are interpreting opposite of what we and the manual are saying.
If it is in Room Temp / Ingniter Auto, the stove will shut down when it hits just above the set point (1-1.5*F). So, the stove acted appropriately. It will restart itself if the temperature gets 1-1.5*F below the set temp.
If it is in Room Temp / Ingniter Manual, then it will go to idle when it hits just above the set point then increase the feed rate when it gets to just below the set point.