Installing Antique Wood Stove in Denver

coltee Posted By coltee, Apr 8, 2018 at 3:09 PM

  1. coltee

    coltee
    Member 2.
    NULL
    

    Nov 29, 2015
    1
    0
    Loc:
    Denver
    36AC7380-1555-4CCA-9E1B-0A8DC492C5A9.jpeg 3827BE5B-62D9-418C-B36C-7140DB36AECB.png

    Apologies if this topic has been posted before. I have a Walker and Pratt “Good Cheer 2” antique cast iron fireplace. I want to install it in my home in Denver. Being as old as it is, I don’t think it’s UL approved. Does anyone know if this can still be installed in my home as long as I follow proper installation and venting?
     
  2. begreen

    begreen
    Mooderator 2.
    NULL
    
    Staff Member

    Nov 18, 2005
    72,926
    10,906
    Loc:
    South Puget Sound, WA
    The stove will not be UL listed and therefore must have 36" clearance to combustibles in all directions. This can be reduced to 12" with proper wall shielding. If it is going to sit in a masonry fireplace then the clearances, except perhaps to the mantel are not an issue. Check with your insurance company to find out their requirements too.

    I thought this might be a coal stove, but see it listed as an open grate wood stove in a 1926 parts catalog. Is it rear or top vented? Does it have an ember screen?
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
  3. coaly

    coaly
    Fisher Moderator 2.
    NULL
    
    Staff Member

    Dec 22, 2007
    3,242
    552
    Loc:
    NE PA
    Colorado has adopted the ICC Family of Codes which includes the 2015 Mechanical Code which requires all appliances to be UL Listed.
     