What gauge wire for 220v welder circuit?

  • Active since 1995, Hearth.com is THE place on the internet for free information and advice about wood stoves, pellet stoves and other energy saving equipment.

    We strive to provide opinions, articles, discussions and history related to Hearth Products and in a more general sense, energy issues.

    We promote the EFFICIENT, RESPONSIBLE, CLEAN and SAFE use of all fuels, whether renewable or fossil.
  • Hope everyone has a wonderful and warm Thanksgiving!
  • Super Cedar firestarters 30% discount Use code Hearth2024 Click here
Status
Not open for further replies.

Black Jaque Janaviac

Feeling the Heat
Hearth Supporter
Dec 17, 2009
451
Ouisconsin
I'd like to get a better welder, but I don't have 220v in my garage. I'm trying to see if it would be worth it to run wire into the garage or would it be better to get a used generator.

What gauge wire would I need to run one of those "tombstone" buzzboxes? It would be probably 50 feet of wire from the breaker box to the garage.
 
Check the welder label to see required amperage at 220/240VAC.
Use the chart here or elsewhere to look up the minimum sized wire required based on amperage. http://www.powerstream.com/Wire_Size.htm
Voltage drop can be an issue too and you use the chart with the calculator below to calculate voltage drop. At 50ft. though I don't think it will be a factor.
That said, if the amperage capacity of the size (gauge) wire you determine in the chart is very close to what the welder draws you may want to go to the next size larger wire.
 
Yep - its the amps that count. Some little 220 migs only draw 7 or 8 amps on 220v. My Lincoln Tombstone (super old bastage) is wired to a 50 amp 220v outlet.
 
Okay there's some funky monkey stuff and code when it comes to welder outlets. The outlet that the Lincoln AC225 stick welder, and just about all welders, use is a 50 amp outlet. 50 amps needs 6 gauge in romex and 8 gauge in THHN in conduit for regular circuits like ovens, boilers, and hot tubs. That's great and I use 6 gauge romex on a 50 amp breaker for my personal Lincoln tombstone.

The electrical code allows you to downsize the wire for welders because they are not continuous use. You have to label the outlet and remember. Note that the cord on the Lincoln welder is only like 12 gauge or maybe 10. Anyway, I think that this is silly and conservatively use the full size wire.

Ignore the voltage drop over distance crap. Not applicable in a residential setting.

Note also that a stick welder welds at about 26 volts. 225 amps at 26 volts is not very many watts. Like 6500. When fed with a 240 volt circuit it is only like 26 amps. Why do they use a 50 amp plug? It is standard for welders.
 
My Dialarc 250 needs a 90 amp breaker. The reason for large breakers is the amount of juice it needs to strike an arc. Also OCV (Open circuit volts) are around 80-90 volts. You need that voltage to start the arc. It is always safer to go bigger.
 
My question would be how far of run from the main panel to the garage ??

Attached or detached ??

What I would do is install a 100 amp sub panel and be done .

That way if you need to get a air compressor and Plasma unit you should be set.
 