That's funny and probably true. The stove is heating up to around 600 degrees. Problem is, very little of that heat is coming inside the house.
 
BrotherBart said:
Roospike said:
BrotherBart said:
Just hanging out on the side listening in. Summit that won't heat. Can't be, can't happen.

Just keep hanging out BrotherB , its not that the Summit is not heating, its acosta2269 heating the state and not the house. ;-)

Gotta be brother.

We have a few Summit owners here on Hearth.com that are from NewYork , now you know why New York hasnt had much snow.
 
acosta2269 said:
Hogwildz, how are you?

Standing in front of the insert is not extremely HOT. It blows warm/hot air out, since day 1, which is why I started this mess.

The stones on the face of the chimney are not hot. They are slightly cooler than room temperature.

How do I know if I have a Heat-a-lator fire place? How can I find out what "type" of fireplace it is and how those vents are being used? Is that something that the building dept would have on file in the house plans?

First tell sign is the firebox is made of like 3/16" or 1/4" steel. the walls, back top, damper area, everything in the firebox is steel. Except the floor.
Heat-a-lator has been around for years. The original part of this plce, which was a 1 story 2 room cabin was buint in the 60's so I was told. And it was confirmed heat-a-lator fireplaces were pretty popular back then. The vents kind of give it away also. But if that firebox is all steel inside except for maybe the floor, its a heat-a-lator.
Not cheap thin steel like some cheapo pre-mades today. I bet you have one.

Elk: Mine is a brick over block wall. That whole wall is. No combustibles untill the second story. Sunken living room, so about 12'-15'' to the next story. And also 2'x2' block chimney lined with terracotta. No heat damage going to happen here. I don't know what acosta's construction is. But I would almost put money thats where his heat is going.

Edit: Ok I didn't see your last post till I posted this already. If its a heat-a-lator its steel, like I said all but floor. I have no clue what you have there. Whae is the wall the fireplace is in made out of? are there combustibles anywhere near the fireplace in the wall, in back, etc. I still think your losing the heat out those vents. Prolly an outside air vent, and like others said, your heating the neighborhood.
 
Roospike said:
BrotherBart said:
Roospike said:
BrotherBart said:
Just hanging out on the side listening in. Summit that won't heat. Can't be, can't happen.

Just keep hanging out BrotherB , its not that the Summit is not heating, its acosta2269 heating the state and not the house. ;-)

Gotta be brother.

We have a few Summit owners here on Hearth.com that are from NewYork , now you know why New York hasnt had much snow.
We had small snow showers here the last few days, problem is, it won't lay here. I think the Summit has a several square mile heating radius :)
No wonder my neighbors are so nice to me :).
Some days however, its ok here, but snowing over the nuke plant, thats no BS either. Weird stuff.
 
So I tried the incense into the outside vent this morning. The vent seems to be drawing in the smoke, but I don't smell anything inside the house. To be honest though, it may be tough to actually smell inside the house. Mixing with the cold outside air, I'm not sure how apparent the smell would be, but it was drawing the smoke into the vent.

I also spoke to the installer this morning. He was "shocked" that the unit wasn't throwing off more heat. He DID NOT install a block off plate. Rather, he stuffed the top "nice and tight" with insulation. He said that was "better" at avoiding drafts and keeps the pipe from moving.

He was going to call Pacific Energy to see if they had any thoughts.

Here are the pictures of the inside and outside air vents.
 

Attachments

  • 109-0911-b_IMG.jpg
    109-0911-b_IMG.jpg
    41.4 KB · Views: 415
  • 108-0900-b_IMG.jpg
    108-0900-b_IMG.jpg
    49 KB · Views: 429
He DID NOT install a block off plate. Rather, he stuffed the top “nice and tight” with insulation. He said that was “better” at avoiding drafts and keeps the pipe from moving.

Im making light of this statement so keep on smiling

He said that was “better” at avoiding drafts and keeps the pipe from moving.

Let me interpet this installers speak

I'm bs-ing you because I was too freaking lazy to do it the right way He might have had some creedence in the avoiding drafts
but the next statment was comming out the seat of his pants
keeps the pipe from moving

After that statement any else that came from his lips consider lip service.

Remember over the weekend I stated there are idiot installer still trying to use common fiberglass insulation as the block off Found in the post ,
where it was exploded out during the flashback explosion that blew the suround off and knocked the tea pot off the stove

When speaking to this installer again ask him this can he provide proof tha common insulation is listed for that application?
like the listing from ownes corning where it has been tested and listed for that application. did he take the paper backing offf?

Ask him the temperature range of common insulation then ask him if it is approved for direct contact with the liner

Ask him is he would direct you to where ASTME or sillimar agencies approves of this type of installation and substitution of approved block off material?

Did he pull a permit for the install was it inspected and approved?.. Human nature would now be wondering what other short cuts he made
 
Elk,

I got the same feeling that he was BS'ing me when I spoke to him. The insulation is probably cheaper and easier for him to install, which is why he used it.

I did file for a permit before the install. The building inspector came the other day and he really didn't look at the stove all that much. He asked me to get an affidavit from the installer on the specifics of the installation. I also mentioned my heat output problem to him and he said he would do a little research and get back to me. Meanwhile the installer called me back and said he spoke to Pacific Energy and the stove temps of 600 degrees are normal (actually a little high) and stove is operating normally. I should try burning different wood and keeping the blower fan a little lower (about 1/2 it's capacity). "Let's see if that works". I feel like I live is Bizzaro world and everyone keeps passing the buck! (The inspector back to the installer. The installer back to PE. PE back to me).

Could the insulation, instead of the block off plate, be causing this? Is the insulation there dangerous? Is that not code? Should I mention it to the building inspector?

He really didn't answer my questions about the outside air supply. He said they didn't notice one. If they noticed one during the installation they would have closed it off. Whatever that means. It's pretty clear that I have one, so I don't really know what that means. Could that be the problem?
 
Now I would really want to know how the installer connected the OAK and if any other corners have been cut here?

The outside vent at this point is a complete mystery. If it's venting the stack, that would lead me to wonder if the chimney is brick or just a brick veneered chase. Is there cool air coming from the interior hole on the upper side of the fireplace? Or if you hold an incense stick near it, does it draw air?
 
I would demand removal of that fiberglass insulation & installation of the block off plate. Block off plate is stated right in the manual! Either at damper area, or seal around surround (tightly), if its stone you'll never get it to seal tight. I'd demand a damper blockoff plate.
 
Hogwildz said:
I would demand removal of that fiberglass insulation & installation of the block off plate. Block off plate is stated right in the manual! Either at damper area, or seal around surround (tightly), if its stone you'll never get it to seal tight. I'd demand a damper blockoff plate.

Is that what the block off plate does?
 
BeGreen said:
Now I would really want to know how the installer connected the OAK and if any other corners have been cut here?

The outside vent at this point is a complete mystery. If it's venting the stack, that would lead me to wonder if the chimney is brick or just a brick veneered chase. Is there cool air coming from the interior hole on the upper side of the fireplace? Or if you hold an incense stick near it, does it draw air?

I held the incense stick there this morning. It drew the smoke in. Not terrible fast (like a vacuum), but it definitely drew it in. I didn't notice the smell of the incense in the house though. Maybe it was too diluted with the outside air
 
acosta I'm a pressed fot time but promise to adress some of this issues after bowling 9:00 EST
I agreee if you are reaching 600 degrees its not the stove or draft or moisture in the wood
 
You have inside vents on the hearth pulling inside air out and you have outside vents pulling air in and must be up the hearth.

I'm not a hearth / fireplace expert but as we know the fireplace is not very efficient and as to the design of the fireplace with an open fire the designs ( vents ) sound like they are made to keep the hearth and construction cool and keep from overheating.

To me it sounds like the design for the fireplace is a backfire design for a wood stove insert.

Obviously if a hearth / chimney was designed for max efficiency it would be on the inside of the home like they were many years ago.

The fine line is to figure out the best way to keep the hearth from venting the heat out of the house wile stil being within the design of the fireplace as to how it was built to keep its construction cool.

Does anybody know if these vents are more to the side of keeping construction cool or to keep fireplace smoke smell going up the chimney ?
 
So to prove to myself that I'm not going crazy, I went out and bought a thermometer to try to measure the temperature of the air coming out of the blower. It's been hanging there for a few hours now and it reads 73.8 degrees. It hasn't really gone much higher than that. I know the thermometer works because if I lower it closer to glass (which is boiling hot) the temperature starts to rise, quickly. The stove temp (on the face of the stove) is 500 degrees but the hanging thermometer reads 73.8 degrees. Odd!

Shouldn't the temperature of this air out of the blower be higher? The installer today said the air out of the blower should be around 200 degrees, but judging from the quality of his installation, I don't think he really knows what he's talking about. Has anyone ever measured this?
 

Attachments

  • 109-0914-b_IMG.jpg
    109-0914-b_IMG.jpg
    65.5 KB · Views: 311
  • 109-0916-b_IMG.jpg
    109-0916-b_IMG.jpg
    38.9 KB · Views: 323
  • 109-0920-b_IMG.jpg
    109-0920-b_IMG.jpg
    47.2 KB · Views: 292
Roo, you thought I was nuts, right?

It's ok..I thought I was nuts!
 
.......................TESTING...........................................................................




Not sure how the insert surrounds are put together but maybe something is not put together correct ? A panel , a shield not in place or installed right ?

500° temp on the stove and 73° heat out put from the blower , that has to be a magic trick.
 
Alright , freestanding Summit , front temp 490° , thermometer 12" away , blower on medium , temperature 178°

Not an insert test so it will differ but 105° difference ?!?! I think the insert blower temp should be warmer then a free stander.

Are you sure your Summit is not set on A/C mode ?
 
That was my thought from the begining, that something wasn't installed correctly. It's either not installed correctly, or the vents (inside or outside) are causing the problem.

I also got some additional information today from the installer...

(1) No block off plate was installed. He stuffed the top with insulation instead.
(2) He did not use a full flue liner. Instead he used a 6" - 5 foot liner.
(3) He's clueless!
 
Roospike said:
Alright , freestanding Summit , front temp 490° , thermometer 12" away , blower on medium , temperature 178°

Not an insert test so it will differ but 105° difference ?!?! I think the insert blower temp should be warmer then a free stander.

Are you sure your Summit is not set on A/C mode ?

LOL

And your thermometer was 12" away....mine is about 2" away.
 
Found Willhounds Summit install pics , looking at the insert it looks like the suround is 1 piece except for the top shield , couldnt find a pic of the top shield except for once its installed.
 

Attachments

  • Summit_5.jpg
    Summit_5.jpg
    40.4 KB · Views: 382
  • Summit_6.jpg
    Summit_6.jpg
    43.6 KB · Views: 356
  • Summit_9.jpg
    Summit_9.jpg
    37.1 KB · Views: 344
Every post more and more is disclosed your instalation was short changed de did a direct connect with out a block off plate? Lets review
what's happening can you scan in in a copy of the bill for the instalation block off persomnal information I want to see what you paid for and materials listed
what is your current flue size servicing that fireplace? this is a masonry fire place? was outside air connected to your summit? Is this fireplace a prefab with vents?
I want to narrow down the facts because at one time there were two posters with similar problems One picture I see a vent in a plastered wall. What function does it serve.

I want to know the relationship with the retailer that sold you the stove and the person who installed the stove does he work for the retailer or is he subcontracted?

Age of the home did you know in 1998 BOCA national mechanical codes required the installation of outside air feeds for all newly constructed fireplaces.

I know I an asking for repeat iinfo but weeding threw 7 pages takes time Humor all followers with my request. Also any communications with the retailer or the installer.

the last thing PE wants is for me to call them and tell them Roospike is pissed at them. PS PM ne your town and the dealers name

In the summer of 1996 I persented a mechanical seminar for the entire eastern states building inspector's convention all states east of the
Mississippi (hey did I spell that correct) River I have contacts at your state level to drop a dime on
 
Combustion Air
Consult local building codes regarding combustion air supply.
Intake or combustion air can be supplied to the Insert in one of
two ways:
1) Outside air supply: Remove cover from ash clean out in
existing fireplace. Place a rodent screen in place of the
cover. Install the Insert as described in the "Installation"
section, making sure not to cover the opening of the air
inlet. When installation is complete, seal surround to
fireplace and anywhere else air may enter. This will ensure
combustion air is drawn from outside the house and into
the 7" x 2" intake at the lower rear of the appliance.

2) Room air supply: Remove the 4" knock-out plug from
either casing side prior to installation (Fig. #11). Install the
Insert as described in the "Installation" section. The Insert
will now draw its air from the room through the front.

**************************************************************
This is what i have found ,
manual does not show picture of outside air supply (1)

Pictured below is the top panel of the surround of the insert , the other picture of the room supply air knock out of the surround.
 

Attachments

  • untitled.JPG
    untitled.JPG
    10.5 KB · Views: 291
  • knock out plug Summit.JPG
    knock out plug Summit.JPG
    10.8 KB · Views: 300
  • insert_diagram.jpg
    insert_diagram.jpg
    42.5 KB · Views: 298
Here's the invoice....
 