Grigg

Member
Jan 7, 2015
37
Lexington, VA
Trying to plan ahead as we need to dig the trench soon.

In a couple years we'd like to install a Garn at/in the house.
Now we have a 12'x24' outbuilding that looks a lot like a "guest house" located about 100' from the main house. In the next few weeks we'll be running electric, gas, water, and a spare conduit to the outbuilding.

Seems while we're digging, laying, and covering up lines that now would be the time to run some insulated PEX for future heating and hot water use in the outbuilding.

I've read on here a lot about foaming in the trench and that sounds attractive. However I wonder if considering the intermittent use of the building and likely smaller size pipe needed? if a pre-packaged solution may be comparable and or easier, perhaps cheaper in this case.

The building has 4" stress skin panels with white styrofoam in them. Again it is 12' x 24' and one story with about 12/12 pitch roof. Does have a large 9' wide double pane glass window/door/window on one wall. To heat we'll likely use a radiator or perhaps staple up PEX radiant. I wonder if the loop could also include a plate and plate heat exchanger to provide hot water for a shower?

Questions:
1- Can we heat and have hot water with only two insulated lines plus a cold water line in the ground
2- What size insulated lines might we need?
3- Considering the above what sort of insulated pipe would be suitable.

Options as I see them, in no order:
Spray foam in trench
ThermoPEX
(broken link removed to http://www.comfortprosystems.com/sites/comfortprosystems.com/files/cps_2015_product_guide2.pdf) (page 53)
(broken link removed to https://www.logstor.com/Brochures/PexFlextra/PexFlextra_EN_P_DH.pdf)
INSULPEX
 
Last edited:
Grigg, If either your HVAC contractor or someone here can give you an educated guess on the energy need for your <300sf building (10,000-15,000btu/hr??). I designed our water-to-air system around a 30*F deltaT. But worst case for you if radiant was only 30*F and it needed 20kbtu/hr that's only .7gpm at ~.4fps velocity, easily handled by 1". If it was my guest house and depending how often it was used, I'd consider electric or ?. Price 300ft of 1" thermopex and decide if the usage justifies the expense based in how much of the year it needs to be heated. Really rough guesses indicate 1" pex way more than enough. I've never looked to see if there is insulated pex under 1".

Thot I'd give you something since your post was quiet.
 
Thanks,
It doesn't look like any of the brands I was looking at offer anything less than 1". Haven't done any calculations yet but from reading here seems like folks are heating a lot more space and using 1", so likely that would also work for us.

You're probably right though... something like a vented gas wall heater (the original plan) will be a lot more economical up front and continue to be for a long time compared to the insulated PEX cost.
I do already have a gas water heater for the building but still need to make a small bump out on one wall to have a good place for it to live. Using hot water from a wood boiler for both heat and DHW seemed like a smaller and simpler setup in the little house. But you're right, more expensive, likely more than the use justifies.

Thanks for the thoughts,

[Hearth.com] Insulated PEX considerations for small outbuilding
 
Oh my... that's going to be stunning. I can't let my wife see this. It appears to be pinned together with wood dowels. Interesting the structure is different for the far versus the near end. Please PM me your progress. I've got a similar project upcoming in the next year converting a small milk barn. Need to keep it boiler focused here, but via PM I can learn about your cabin design/progress. Used to drive thru Lexington a bunch going home to PA from Newport News. Cheers and congrats on an exciting project.
 